Default Question for Mr. Decker

Actually, anyone can chime in if they feel. This was directed at Will just because it is in his home territory.
Just received an e-mail from a client stating that the seller/builder is arguing one of my findings. The EBJ from the A/C is not attached correctly, but by a self-tapping screw. The seller's attorney states that "the village approved it and they got a certificate of occupancy and this is the way they do it". Will, I was wondering if this is the common practice in the village of Skokie or if you would be able to tell me if Eric Johnson (elect inspec) would accept questions about this. Thanks, Jeff (Wick)
Attached Thumbnails
question-mr-decker-p1010018a.jpg  
Reply With Quote
  #2  
Old 4/3/08, 4:01 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question for Mr. Decker

Sheet metal screws are not permitted to be used as a ground screw. That screw pictured, commonly referred to as wafer-head TEK screw, is a self-drilling sheet metal screw. A different type of sheet metal screw, but a sheet metal screw just the same. Shouldn't be like that, but nothing I'd lose any sleep over if it's otherwise redundant. Looks like the circuit is in EMT, which qualifies as the ground in and of itself.
Reply With Quote
  #3  
Old 4/3/08, 4:10 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,923
Default Re: Question for Mr. Decker

Personally, I've seen nothing to "argue" about.

If the buyer wants it, the buyer should get it or go find another house.

If the seller doesn't want to fix it than the seller should put the house back on the market and take their chances.

Again however, is this a significant issue? Did you see something associated with this alleged deficiency that indicates that it is actually a deficiency or just a theoretical technical concern?

Due to the lack of other significant issues, I would be telling my client that if they don't like it they should pay to get it fixed. That way they can sleep at night.
Reply With Quote
  #4  
Old 4/3/08, 4:20 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Question for Mr. Decker

Quote:
Originally Posted by jwicklander
The EBJ from the A/C is not attached correctly, but by a self-tapping screw.
I always call out improper connections, if for no other reason than to document that I saw it, and it's improper.

In the instances where I'm confronted by an electrician, I simply suggest that they give a written statement that there is "no problem" with the connection. I've only had one electrician willing to do that, and as such, any liability was shifted to him.

FWIW- EBJ is not the proper term for this conductor. EGC or equipment-grounding-conductor is more accurate.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 4/3/08, 5:18 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Question for Mr. Decker

An NM cable clamp looks the same as that on one side, nothing there that proves to have EMT.

Here is a picture of one of the nachi training panels I built thats full of problems. You can see both sides of these clamps.
Attached Thumbnails
question-mr-decker-dsc03726a.jpg  



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937

Last edited by bking; 4/3/08 at 5:23 PM.. Reason: added picture
Reply With Quote
  #6  
Old 4/3/08, 5:48 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question for Mr. Decker

Quote:
Originally Posted by bking
An NM cable clamp looks the same as that on one side, nothing there that proves to have EMT.
Since it's all THHN leaving out of the connector, and the person posted this pic from the Chicago area, it's a pretty good bet it's leaving in EMT.
Reply With Quote
  #7  
Old 4/3/08, 5:50 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Question for Mr. Decker

thats right! I didn't notice the THHN.

Rat proof electrical like NY.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #8  
Old 4/3/08, 5:56 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Question for Mr. Decker

Quote:
Originally Posted by jpope
FWIW- EBJ is not the proper term for this conductor. EGC or equipment-grounding-conductor is more accurate.
While "EGC" is proper in verbiage terminology......the "EBJ" is more accurate in function.... ....kinda wish they would actually change it but alas it always fails adoption...lol



Paul W. Abernathy
Reply With Quote
  #9  
Old 4/3/08, 5:59 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Question for Mr. Decker

Quote:
Originally Posted by pabernathy
While "EGC" is proper in verbiage terminology......the "EBJ" is more accurate in function....
Agreed. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 4/3/08, 6:06 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question for Mr. Decker

Quote:
Originally Posted by pabernathy
....kinda wish they would actually change it but alas it always fails adoption...lol
I think they won't adopt it because they're all old fogies and the acronymn has "BJ" in it.
Reply With Quote
  #11  
Old 4/3/08, 6:20 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Question for Mr. Decker

. . . and it might eliminate some of the confusion between bonding and grounding. We couldn't have that. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 4/3/08, 6:39 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Question for Mr. Decker

J being for jumper?

A jumper is usually where you can view each end of it without moving your feet. But this view might be more electronics than electrical.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #13  
Old 4/3/08, 7:57 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Question for Mr. Decker

Quote:
Originally Posted by jwicklander
Actually, anyone can chime in if they feel. This was directed at Will just because it is in his home territory.
Just received an e-mail from a client stating that the seller/builder is arguing one of my findings. The EBJ from the A/C is not attached correctly, but by a self-tapping screw. The seller's attorney states that "the village approved it and they got a certificate of occupancy and this is the way they do it". Will, I was wondering if this is the common practice in the village of Skokie or if you would be able to tell me if Eric Johnson (elect inspec) would accept questions about this. Thanks, Jeff (Wick)
Sorry I was so late to the party. Thought you were asking my Dad (Mr. Decker). Best to just e-mail me (see below) directly.

That is a truely F'ed up installation, in this area.

1) Usually, grounding is through the contiguious metal conduit (EMT), but most AHJ's want to see a seperate green wire run and connected to the servive equipment at the ground / neutral bonding point (the neutral buss) for A/C units.

2) You have to remember (I assume that this was in Skokie, in which case why didn't you just call me and I would have come over and helped (no charge, buy me a coke if you feel guilty)) that in Illinois:
a) Electricians are NOT state licensed. Only city or, sometimes, the county, licenses electricians.
b) Many builder / sellers who have no clue, and hire similarly clueless subs.
c) What the builder eastern european? That would explain it (in this area).

3) When they say that it was OK with the village or town, DEMAND proof. You will not get it. The builder just says that it passed code inspection (which it usuallu did not). The local AHJs will NEVER provide documentation that they approved anything to the buyer or the buyer's lawyer. By court decision, they have no liability for not inspecting it or not calling it out if it is wrong. Go figure.

If you call me (see below), I can provide some help. There are a couple of builders in this area that "have an in", if you know what I mean. They have to be dealt with a certain way.

But, to answer your question, this is wrong, as far as an HI is concerned. It does not conform to "current national construction standards", which is this state's requirement for HIs.

Call me.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!

Last edited by wdecker; 4/3/08 at 8:01 PM..
Reply With Quote
  #14  
Old 4/3/08, 11:24 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question for Mr. Decker

Quote:
Originally Posted by pabernathy
While "EGC" is proper in verbiage terminology......the "EBJ" is more accurate in function.... ....kinda wish they would actually change it but alas it always fails adoption...lol
The revised definition includes a new FPN No. 1, and it gives us something to consider, seems appropriate and helps to settle the long standing issues that were proposed and rejected.

"Grounding Conductor, Equipment (EGC). The conductive path installed to connect normally non–current-carrying metal parts of equipment together and to the system grounded conductor or to the grounding electrode conductor, or both.

FPN No. 1: It is recognized that the equipment grounding conductor also performs bonding.

FPN No. 2: See 250.118 for a list of acceptable equipment grounding conductors."
Reply With Quote
  #15  
Old 4/4/08, 1:43 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Question for Mr. Decker

250.102 talks about EBJs.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Got a letter from ASHI's President today. gromicko General Inspection Discussion 55 12/12/10 11:51 PM