#1
|
||||
|
||||
|
I have run into this situation a couple of times recently and not being an electrician or of an electrical backround I need some education. While checking the switched recpticles in a home recently, the middle light on my tester was dimmly lit with the switch in the off position. I put the meter on it and you can see the result, it was showing 54v. Other switched recepts in the home were the same, anywhere from 40 to 54v. Whats going on here? I did write it up as a concern that needed evaluation by a licensed electrician. Thanks for your input.
Rick Slocum NACHI # 04072697 Elizabeth CO 80107 ABSOLUTE Home Inspection Service Last edited by rslocum; 7/4/07 at 1:33 PM.. |
|
#2
|
|||
|
|||
|
This Bulletin is intended to address the occurrence of so-called “phantom” voltages, a phenomenon detected during the testing of electrical conductors in the field. Due to the high impedance of measuring instruments, a voltage reading may be detected on open conductors where there is no hard electrical connection to a voltage source. Conductors that are installed in close proximity to one another, and are capacitively coupled to each other, can cause this a.c. voltage reading. Such a reading could be 2 or 3 volts, or it may be as high as the voltage on the adjacent conductors. This is what is referred to as a “phantom” voltage. According to Underwriters Laboratories Inc., this can be a harmless reading and can be caused by the high input impedance of the measuring instrument, which places very little loading on the circuit under test. The capacitance is increased as the length of the run is increased. A 50-foot run may produce a pronounced capacitance effect whereas a one-foot sample may not produce any. Since the “phantom” voltage is a physical phenomenon involving very small values of capacitance, it cannot energize a load or cause physiological damage to a person. Care must be taken to be sure that the voltage reading is a phantom voltage, which is caused by improper use of high impedance multimeters, and not as a result of a cable defect or improper installation, which may result in a shock hazard. In order to help minimize the likelihood of reaching a wrong conclusion from this phenomenon, NEMA recommends the use of a Listed low impedance multimeter in place of a high impedance multimeter or other high impedance measuring device for testing on open conductors where there is no hard electrical connection. Without a low impedance measuring device, a high voltage reading is an inconclusive indication of possible faults in the cable. This was provided by NEMA.........digital meters are prone to reading this " Phantom Voltage "....however it can also mean a hot wire is loose and voltage is being conducted on the netural...rather rare........try using an analog meter and you should get nothing......so be very careful on how you regard this. Chances are with an analog meter you will get nothing.......... Paul W. Abernathy Last edited by pabernathy; 12/12/06 at 6:44 PM.. |
|
#3
|
||||
|
||||
|
Paul, Thank you for your explaination, makes sense now. Always a great learning experiance on here. What threw me was the light lit up even with the wall switch off.
Rick Slocum NACHI # 04072697 Elizabeth CO 80107 ABSOLUTE Home Inspection Service |
|
#4
|
|||
|
|||
|
Magentics.....all voltage is created by magnetics in one way or the other...I always suggest an HI have a low cost low impedence tester like a "Wiggy" when simply detecting voltage...
Keep in mind....some conditions can use this type of effect....like an open conductor and so on...but it is best to leave that exporation to the electricians....because we will test it in all different ways... But to settle your mind......get a cheap low impe. meter...you can get them radio shack for like $8.00 - $10.00 bucks Paul W. Abernathy |
|
#5
|
||||
|
||||
|
Good advice. I'll pick one up tomorrow. Thanks again Paul!
Rick Rick Slocum NACHI # 04072697 Elizabeth CO 80107 ABSOLUTE Home Inspection Service |
|
#6
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Paul, I am having trouble seeing phantom voltage lighting the lamp on his 3 light tester. I suggest the possibility that the switches controlling these outlets are illuminated switches. The kind that illuminate when the switch is off. The light in these switches requires an incandecent lamp to be in series in order to glow. Ever notice when the fixture bulb burns out, the illuminated switch goes dark? Also ever notice when you change out a fixture with an illuminated switch controlling it, you can get knocked on your butt even with the switch off? I suspect his neon tester is glowing as it is in series with the neon in the switch. What do you think?
|
|
#7
|
|||
|
|||
|
hmmm.....never given that much thought Brian......let me JELL-O on it.....and see what I can find.
But....we will need richard to enlighten us on IF these were illuminated switches.....how goes it Richard... Also.....could be an issue of a transformer on the circuit say to a cordless phone...but I question it being the garbage disposal..I think it was... Are you saying brian that in order for the switch to work....voltage will have to be present at the receptacle in order for the little light in the switch to function...does it not need a neutral...or are you saying it takes place within the switch....can't say I agree on that one....but again......never thought about it...lol We have to understand however that if the receptacle is switched...it should have NO voltage at it ( usable that is ) when it is in the off position......and properly wired.... Dang Brian.......you are going to make me looking this up FUN....man I love this stuff... <------NERD !!!!! Paul W. Abernathy |
|
#8
|
|||
|
|||
|
But....the digital high impedance issue and phantom voltage holds true.....if anyone has been in the business long enough using a digital meter they will experience the phantom voltage........
Paul W. Abernathy |
|
#9
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Even if they were illuminated switches, with no load plugged into them they would not illuminate. And with the neon load plugged in, they would only glow dimly from the series circuit, probably not enough to see especially in daylight.
|
|
#10
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
As soon as I have the time I am going to try this in my shop with an illuminated switch and a 3 light tester. Maybe tomorrow after work.
|
|
#11
|
|||
|
|||
|
Do it....do it.......I love experiments
Paul W. Abernathy |
|
#12
|
|||
|
|||
|
You know Brian...it is a sickness.....thats what they tell me......we have a sickness.......
Paul W. Abernathy |
|
#13
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#14
|
|||
|
|||
|
OMG...yes when I was in electrical school years and years ago....all we had was Simpsons......love them old big black boxes....
Paul W. Abernathy |
|
#15
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Yes, it's a sickness all right. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Sump Pit/Pump Question | Joey D'Adamo | Plumbing Inspections | 4 | 11/26/08 1:04 PM |
| WA State Legislative update | hmiller | Legislation, Licensing & Legal Issues for Inspectors | 153 | 5/4/07 11:55 PM |
| Plumbing vent Routing Question | kweiss | Plumbing Inspections | 7 | 11/1/06 9:57 PM |