Default Question on swimming pool lights

I know that a 120 volt swimming pool light has to be on a GFCI, but what about a 12 volt light. Does the power to the transformer have to be GFCI protected? This is the pool panel I inspected yesterday. the transformer is located inside the panel but the light is only 12 volts.
Attached Thumbnails
question-swimming-pool-lights-img_3608.jpg  



Robert Sole



407-637-7288


Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
Find an InterNACHI certified West Virginia Home Inspector (and anywhere else in North America)
  #2  
Old 9/30/09, 5:31 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Question on swimming pool lights

No need for GFCI if less than 15V.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 9/30/09 at 5:36 PM..
Reply With Quote
  #3  
Old 9/30/09, 5:56 PM
Robert Sole's Avatar
Robert Sole Robert Sole is online now
InterNACHI Member
 
Join Date: Jun 2007
Location: Winter Park, Fl
Posts: 157
Default Re: Question on swimming pool lights

That has been my opinion also. I didn't feel that it wa a problem with the low voltage. It kept bugging me though so I wanted some confirmation. Thanks for the response.



Robert Sole



407-637-7288


Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties.

RobertSole@REMinspections.com

REMinspections.com
OrlandoHomeInspector.net
Reply With Quote
  #4  
Old 10/3/09, 10:00 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Question on swimming pool lights

This may assist you :

(3) GFCI Protection, Relamping.
A ground-fault circuit
interrupter shall be installed in the branch circuit supplying
luminaires operating at more than 15 volts such that there is
no shock hazard during relamping. The installation of the
ground-fault circuit interrupter shall be such that there is no
shock hazard with any likely fault-condition combination
that involves a person in a conductive path from any ungrounded
part of the branch circuit or the luminaire to
ground.

When dealing with those types of luminaries the key is in the transformer:

(2) Transformers.
Transformers used for the supply of underwater
luminaires, together with the transformer enclosure,
shall be listed as a swimming pool and spa transformer.
The transformer shall be an isolated winding type
with an ungrounded secondary that has a grounded metal
barrier between the primary and secondary windings.




Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Let's talk ESOP rcooke General Inspection Discussion 231 2/22/08 9:55 PM
It's time for Professional Pool Inspections Revel L. Thom Ancillary Services & Additional Topics 13 7/26/07 11:50 AM
Swimming pool Plaster phughes General Inspection Discussion 6 2/26/06 2:47 PM


All times are GMT -4. The time now is 3:08 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts