I know that a 120 volt swimming pool light has to be on a GFCI, but what about a 12 volt light. Does the power to the transformer have to be GFCI protected? This is the pool panel I inspected yesterday. the transformer is located inside the panel but the light is only 12 volts.
Robert Sole, CMI 407-637-7288 Florida license numbers HI 169 and MRSA 92 Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties. RobertSole@REMinspections.com Check out my blog orlandohomeinspections.info/ REMinspections.com OrlandoHomeInspector.net |
| Find an InterNACHI certified Idaho Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
No need for GFCI if less than 15V.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net Last edited by jpope; 9/30/09 at 5:36 PM.. |
|
#3
|
||||
|
||||
|
That has been my opinion also. I didn't feel that it wa a problem with the low voltage. It kept bugging me though so I wanted some confirmation. Thanks for the response.
Robert Sole, CMI 407-637-7288 Florida license numbers HI 169 and MRSA 92 Serving the Orlando Florida area including Orange, Seminole, Northern Osceola and Southwestern Volusia Counties. RobertSole@REMinspections.com Check out my blog orlandohomeinspections.info/ REMinspections.com OrlandoHomeInspector.net |
|
#4
|
||||
|
||||
|
This may assist you :
(3) GFCI Protection, Relamping. A ground-fault circuit interrupter shall be installed in the branch circuit supplying luminaires operating at more than 15 volts such that there is no shock hazard during relamping. The installation of the ground-fault circuit interrupter shall be such that there is no shock hazard with any likely fault-condition combination that involves a person in a conductive path from any ungrounded part of the branch circuit or the luminaire to ground. When dealing with those types of luminaries the key is in the transformer: (2) Transformers. Transformers used for the supply of underwater luminaires, together with the transformer enclosure, shall be listed as a swimming pool and spa transformer. The transformer shall be an isolated winding type with an ungrounded secondary that has a grounded metal barrier between the primary and secondary windings. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
![]() |