Default question on wireing furnace, legal or not

We have experienced power outages lately. With the temperatures in the 20's, I am looking to remedy my heating problem. At this time my forced air furnace is hard wired to my breaker box. I have a generator that is big enough to handle the furnace, sump pump, refrigerator and a few lights. I am trying to do this as inexpensively as possible, but (most importantly) safely.
I want to have the romex from the furnace circuit (where breaker is) end in a box with a receptacle close to the furnace. Then the romex from the furnace end in a box, (about a foot away from the receptacle) joined to a cord (with wire nuts) with the male end which gets plugged into the receptacle. This setup would be permanent. When there's a power outage, switch off breaker then plug in extension cord from my generator to furnace. When power returns, unplug extension, plug cord back into the receptacle and switch breaker on. No grid involved. But is it legal, as in code?
Reply With Quote
  #2  
Old 1/17/07, 5:25 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: question on wireing furnace, legal or not

NO

A small transfer switch would be required for something to code -

I am sure someone from the electrical side can give you some wire by wire guidance

While I agree with you that setup would be no different than a garbage disposal with a plug, garage door openers with a plug, large 220 volt window HVAC units etc.

Main problem is that items that are permanently installed must be wired as same except for the items that are exceptions to the rule

Small transfer switches are not that expensive

rlb

Last edited by rbennett; 1/17/07 at 5:39 PM..
Reply With Quote
  #3  
Old 1/17/07, 7:35 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: question on wireing furnace, legal or not

Bill,

I am sure many of us ( electricians ) could talk you through this but you will have a better chance over at www.doityourself.com as this is not really a DIY forum here and I am sure NACHI does not want the liability from telling a DIYer how to do something like this.



Paul W. Abernathy
Reply With Quote
  #4  
Old 1/17/07, 7:38 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: question on wireing furnace, legal or not

My furnace disconnect switch is a double pole double throw type. It is mounted in a 4"X4" box on the furnace. One side is connected to the house romex and the other is a 12" cord and cap. Furnace runs normally until switch is flipped from normal side to the cord side. Plug in the generator cord and voila! It's legal because it transfers both the hot and the neutral wires from house power to generator power. This isolates any chance of back feeding generator voltage to the power company grid. That protects linemen from a potential shock hazard from your generator. The switch cost about $10. aregular manual transfer switch does the exact same thing. Make sure the generator is a good distance from the house. You don't want any CO to find its way in.
Reply With Quote
  #5  
Old 1/17/07, 7:41 PM
rromoser's Avatar
rromoser rromoser is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Fishers, IN
Posts: 187
Default Re: question on wireing furnace, legal or not

As per Paul's suggestion, I've been doing electrical work for 30yrs. I recommend this being done by a qualified person. A life may be on the line.
Reply With Quote
  #6  
Old 1/17/07, 7:55 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: question on wireing furnace, legal or not

P.S. You can't use Extention Cord as permanent wiring and you can't place a MALE attachment cap onto a romex wire and remain legal.

I can't condone a jumper CORD made out of extention cord or the like as a permenant fix...sorry......

While it may be something YOU are aware of...it is the person who will mess with it potentially at risk.......you are not ALWAYS potentially going to be the one to make this cheap fix.



Paul W. Abernathy
Reply With Quote
  #7  
Old 1/17/07, 8:41 PM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,950
Default Re: question on wireing furnace, legal or not

Would not the manufacturers installation instructions and requirements for the furnace include its wiring? As such, wouldn't deviations such as those suggested, be in violation?



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167

Last edited by jbushart; 1/17/07 at 9:12 PM..
Reply With Quote
  #8  
Old 1/17/07, 8:42 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: question on wireing furnace, legal or not

Quote:
Originally Posted by pabernathy
P.S. You can't use Extention Cord as permanent wiring and you can't place a MALE attachment cap onto a romex wire and remain legal.

.
Paul when you have 5k worth of meat in a freezer as I have been through numerous ice storms you do what you have to do. 14 degrees outside ambient. My furnace and my freezer most important.I will be running a generator no matter what. I could place my meat outside but the varmints would be into it country living you know. I feed my main panel with a home made # 8 from the 50 amp 220 volt outlet on the generator and just turn off the breakers I don't want on. (Temporary Temporary)
Reply With Quote
  #9  
Old 1/17/07, 8:47 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: question on wireing furnace, legal or not

Dude...I dont DEAL in WHAT IF's...I can only deal in what I consider SAFE and LEGAL.

No cutting corners for the sake of saving some MEAT is not the right choice.

however, legally you can tell the guy whom is a DIYer to do it and IF by chance the guys burns his house down or kills himself...tell it to his son or daughter....whom could SUE the board.

lol..Ok...not coming down on you Charle...BUt you have to understand legal responsibilities of telling a person (DIYer) how to do something....wrong or technically illegal.

Now...if he just goes and does it because he HAS to do what he has to do...then not post about it....then I may agree.

Sites like www.doityourself.com has liability insurance for those types of questions......my site has coverage from my professional licence and covered....but I dont think NACHI has this insurance.

Please dont think i am coming down on ya....just explaining I can't use the " do what ever is needed" approach to this type of question...sorry



Paul W. Abernathy
Reply With Quote
  #10  
Old 1/17/07, 8:49 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: question on wireing furnace, legal or not

or...Charley you could send ME about 2 K of that meat.......ask Stephen in Seattle...I EAT alot.....



Paul W. Abernathy
Reply With Quote
  #11  
Old 1/17/07, 9:11 PM
Charley L. Bottger's Avatar
Charley L. Bottger Charley L. Bottger is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Marland, OK
Posts: 4,187
Default Re: question on wireing furnace, legal or not

[quote=pabernathy]Dude...I don't DEAL in WHAT IF's...I can only deal in what I consider SAFE and LEGAL

quote]
Paul;
I can understand your point of view but the gentleman was not asking how to wire it. He was just asking if it was code and its not. He had already made up his mind as to what he was going to do regardless of what you stated.
Reply With Quote
  #12  
Old 1/17/07, 9:28 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: question on wireing furnace, legal or not

Paul

Just for information -- how the heck can a 2 hp garbage grinder be wired on a plug under the sink and a furnace with equal or less current demand be required to be permanent??

Do not understand the code -- Both are perm. at about the same current and if the furnace were to be on a plug one could just plug it into the generator with no problem and have heat safe an legal??

Just a question -- not a debate

rlb
Reply With Quote
  #13  
Old 1/17/07, 9:49 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: question on wireing furnace, legal or not

[quote=cbottger]
Quote:
Originally Posted by pabernathy
Dude...I don't DEAL in WHAT IF's...I can only deal in what I consider SAFE and LEGAL

quote]
Paul;
I can understand your point of view but the gentleman was not asking how to wire it. He was just asking if it was code and its not. He had already made up his mind as to what he was going to do regardless of what you stated.
hmmm...just giving my opinion........I did direct him/her to a forum that possibly could explain to him how to legally do it.....

Ah...i thought I made a statement about it not being to code....at least I thought I did......



Paul W. Abernathy
Reply With Quote
  #14  
Old 1/17/07, 9:53 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: question on wireing furnace, legal or not

Quote:
Originally Posted by rbennett
Paul

Just for information -- how the heck can a 2 hp garbage grinder be wired on a plug under the sink and a furnace with equal or less current demand be required to be permanent??

Do not understand the code -- Both are perm. at about the same current and if the furnace were to be on a plug one could just plug it into the generator with no problem and have heat safe an legal??

Just a question -- not a debate

rlb
You basically answered your question....the Disposal is designed to be wired this way and and approved for such......if the furnace is wired in this manner then not a problem.....

Careful I dont like generators running in the house..but thats a different thing I wont go into.

I was only making a statement to ensure the person does not put a male plug on Romex......and not to use any extention cords or FLEX as perm. wiring....thats all......



Paul W. Abernathy
Reply With Quote
  #15  
Old 1/17/07, 10:04 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: question on wireing furnace, legal or not

Sorry Charley...just figured he would want an opinion from an electrician and an electrical educator on why he should not do it that way.....hell I get PAID for that advice......sorry if it was misguided.

Consider it some FREE consultation poster.....feel free to do as you wish

Hope that makes all my HATERS happy..... ( I am teasing guys...honestly )

Come on OTHER electricians...here's your chance to JUMP in and BERATE the GURU.......i am sure they are lurking under many screen names....



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Furnace Problem Comments Welcome rfrost Inspecting HVAC Systems 28 10/21/07 6:26 PM
Condemned Furnaces Spark Safety Issues Gary Reecher Inspecting HVAC Systems 7 3/8/07 8:17 PM
Lenox G40DF Furnace Albert Detorre Inspecting HVAC Systems 5 2/19/07 4:20 PM


All times are GMT -4. The time now is 4:08 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts