Default Quick question on Service size

FPE panel at todays inspection. Panel was rated for 200 amp max. (according to sticker on inside) Service was 3/0 awg Aluminum. My sheet tells me this is 175 amp rated service entrance conductor. Now, FPE panel typically don't have a main service disconnect, so am I too assume that this is 175 amp service? Thanks ahead of time........



Rick Slocum
NACHI # 04072697
Elizabeth CO 80107
ABSOLUTE Home Inspection Service

Last edited by rslocum; 7/4/07 at 2:33 PM..
Reply With Quote
  #2  
Old 6/10/07, 12:40 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,037
Default Re: Quick question on Service size

The service capacity (important inclusion) would be the lesser of the rated components, in this case, 175 amps.

Quote:
Originally Posted by rslocum
Now, FPE panel typically don't have a main service disconnect
That's not actually true. I think you'll find a pretty equal portion of FPE's with and without a single (main) disconnect. I generally find 60 to 100 amp services with a single disconnect. The larger services tend to be these split-bus type (with no disconnect) and the smaller services will generally be 6 or less circuits.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 6/10/07, 2:10 AM
Richard D. Slocum's Avatar
Richard D. Slocum Richard D. Slocum is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Elizabeth, CO
Posts: 215
Default Re: Quick question on Service size

Thank you Jeff , I appreciate the info. I haven't run into anything but the split buss type. Your always a great source of info !



Rick Slocum
NACHI # 04072697
Elizabeth CO 80107
ABSOLUTE Home Inspection Service
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Quick and easy trap question Danny Castellano Plumbing 4 8/14/06 1:17 PM
HSPF - quick question rray HVAC 5 7/17/06 5:01 PM
Quick question about double-wide plumbing mmorgan Plumbing 1 6/11/06 7:52 PM


All times are GMT -4. The time now is 8:27 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts