Default Quiz: Main breaker panel box mounting

Greetings to all you good folks!

I was walking through a new three story apartment constrution project today and was surprised to find that the 2x4 studs measured 3 3/8", but many measured 3 1/4" or less, by 1 7/16" and a bit less. Several stages of construction are in progress - the site when complete will have 16 buildings housing 24 apartments each.

Of course, many questionable things were seen but I wonder most about the breaker panels - one for each apartment. Before sheetrock is installed, I can see that the back of these panels with have no breathing space. The backside of the panel may be facing into a living room or another bedroom. The user side of the panel is in a bedroom, but not a closet.

Does the backside need to be a fire rated sheetrock? If the studs were 3 5/8 or 3 1/2" the panel back would not be touching the sheetrock. Is this anything to be concerned about? (I am not doing a for-pay inspection, just nosing around to see how things have been done.) What do you think? is it okay and should I stick my nose where it doesn't belong if it is not okay?

Thanks


</IMG></IMG>
Reply With Quote
  #2  
Old 10/8/06, 9:28 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Quiz: Main breaker panel box mounting

Dennis,

I would not be overly concerned on this. Sheetrock in itself is considered non-combustible in the installation case....and as for the space behind it....that usually applies to surface mounts on cinderblock and concrete to allow air space to reduce moisture build up and corrosion.

I would not be overly concerned here.....



Paul W. Abernathy
Reply With Quote
  #3  
Old 10/8/06, 9:55 PM
dthomas2 dthomas2 is offline
Active Poster
 
Join Date: Jun 2006
Location: Spokane, Wa
Posts: 262
Please Note: dthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Quiz: Main breaker panel box mounting

Paul,

Judging from you credentials, I have all the answer I need. Thanks a bunch - how nice it is to get a quick expert answer!
</IMG></IMG></IMG>
Reply With Quote
  #4  
Old 10/8/06, 10:06 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Quiz: Main breaker panel box mounting

Just for future sake...here is the airspace reference in regards to wet and damp locations....may come in handy for ya.


312.2 Damp, Wet, or Hazardous (Classified) Locations.
(A) Damp and Wet Locations.

In damp or wet locations,
surface-type enclosures within the scope of this article shall be
placed or equipped so as to prevent moisture or water from
entering and accumulating within the cabinet or cutout box,
and shall be mounted so there is at least 6-mm (
14-in.) airspace
between the enclosure and the wall or other supporting surface.
Enclosures installed in wet locations shall be weatherproof.
For enclosures in wet locations, raceways or cables
entering above the level of uninsulated live parts shall use
fittings listed for wet locations.





Paul W. Abernathy
Reply With Quote
  #5  
Old 10/9/06, 2:21 AM
dthomas2 dthomas2 is offline
Active Poster
 
Join Date: Jun 2006
Location: Spokane, Wa
Posts: 262
Please Note: dthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Quiz: Main breaker panel box mounting

good stuff, thanks! Does it matter that these are flush mount panels?
Reply With Quote
  #6  
Old 10/9/06, 5:41 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Quiz: Main breaker panel box mounting

Quote:
Originally Posted by dthomas2
good stuff, thanks! Does it matter that these are flush mount panels?
If you are refering to can they set back into the wall....well if the wall is sheetrock or gypsum which it is called sometimes then it can set back up to 1/4"....BUT if the covering is combustible like wood paneling and so on...or simular then it has to be flush with the outside wall.

Most of the time when someone sets it back into the wall and it does not end up flush.....or has a depth more than 1/4" at the finish...it also causes a problem with the breakers fitting into the cover right and leaving GAPS that have to be addressed...so out of a courtesy you may want to let them know about that.....but again if the walls are gypsum or sheetrock finishes walls then it can set back up to 1/4" without any problems.



Paul W. Abernathy
Reply With Quote
  #7  
Old 10/9/06, 11:40 PM
dthomas2 dthomas2 is offline
Active Poster
 
Join Date: Jun 2006
Location: Spokane, Wa
Posts: 262
Please Note: dthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Quiz: Main breaker panel box mounting

.....but again if the walls are gypsum or sheetrock finishes walls then it can set back up to 1/4" without any problems.
Paul Abernathy,CME,RMS,CMI

--

Thanks Paul.
Without pictures it is difficult to communicate some intricateness's so I have to ask what you mean "...it can set back ..." Does this mean that the back surface of the electrical panel must be 1/4" from the back face of the sheetrock of its shared stud wall?




</IMG>
Reply With Quote
  #8  
Old 10/10/06, 6:47 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Quiz: Main breaker panel box mounting

No. The back of the panel has no restrictions as to "breathing space".

What Paul means is the front leading edge of the panel (where the cover screws on) can be 1/4" set back from the finish sheetrock.
Reply With Quote
  #9  
Old 10/10/06, 8:29 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Quiz: Main breaker panel box mounting

AS Speedy nicely added.........talking about the front....not the back of the panel..........



Paul W. Abernathy
Reply With Quote
  #10  
Old 10/10/06, 2:29 PM
dthomas2 dthomas2 is offline
Active Poster
 
Join Date: Jun 2006
Location: Spokane, Wa
Posts: 262
Please Note: dthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Quiz: Main breaker panel box mounting

Thanks, I appreciate the advice.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Subpanel wired as main panel. jlybolt Electrical Inspections 15 5/23/07 4:10 PM
Panel main rating sfalvey Electrical Inspections 7 9/24/06 8:46 PM
Can you guess what goofy inspection trade association requires all this?! gromicko Canadian Inspectors 7 8/26/06 3:11 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 4:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts