Default Range hood

I recently fitted a range hood above my electric range. There wasn't one and I believe that code says there should be. It is not vented but has carbon filters, which I believe to be acceptable.

Here is my question (unless you wish to make a point about the range hood not being vented). Just above and behind my range there is a receptacle. The range hood is being powered from that receptacle by a power cord and plug (supplied with it). The wire runs six inches up the wall to the range hood. Are there any issues with this? I know the best solutioin is to power a range hood from a receptacle installed in a cupboard above the range but I do not have this.

My potential concern is that a cable is essentially rising flush with the wall from behind the top of the range, then up the wall to the range hood.

Last edited by Ian Gills; 2/1/07 at 3:57 PM..
Reply With Quote
  #2  
Old 2/1/07, 10:10 PM
ccbrands1 ccbrands1 is offline
Active Poster
 
Join Date: Jan 2006
Posts: 220
Please Note: ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range hood

no idea what koads might say.

cord could possibly be subject to mechanical and/or heat damage.

i'de consult with an electrician to see if moving the outlet is possible.
Reply With Quote
  #3  
Old 2/2/07, 6:48 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Range hood

I don't know of any codes that state that a ventilation hood is required over every stove. As far as venting this hood to the exterior, 90% of the hoods in homes today do not vent to the exterior. They are self-ventilated. It's a simple fan that sucks the air from below, runs through a filter, then discharges this air from the vent above.

If the supplied wiring to this ventilator is exposed and runs up the wall behind the stove, I see this as a safety issue. I would recommend an Electrician correct this issue.
Reply With Quote
  #4  
Old 2/2/07, 8:14 AM
Emmanuel J. Scanlan Emmanuel J. Scanlan is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Josephine, TX
Posts: 1,036
Default Re: Range hood

2006 IRC for appliance connections:

Quote:

E4001.3 Flexible cords.
Cord-and-plug-connected appliances
shall use cords suitable for the environment and physical conditions
likely to be encountered. Flexible cords shall be used
only where the appliance is listed to be connected with a flexible
cord. The cord shall be identified as suitable for the purpose
in the installation instructions of the appliance manufacturer.
Receptacles for cord-and-plug-connected appliances shall be
accessible and shall be located to avoid physical damage to the
flexible cord. Except for a listed appliance marked to indicate
that it is protected by a system of double-insulation, the flexible
cord supplying an appliance shall terminate in a grounding-
type attachment plug. A receptacle for a cord-and-plugconnected
range hood shall be supplied by an individual
branch circuit. Specific appliances have additional requirements
as specified in Table E4001.3 (see Section E3809).
2005 NEC proposals:
Quote:

422.16 Flexible Cords.
Quote:

(5) Range Hoods.
Range hoods shall be permitted to be
cord-and-plug connected with a
flexible cord identified as
suitable for the use on range hoods in the installation instructions
of the appliance manufacturer, where all of the
following conditions are met.
(1) The
flexible cord shall be terminated with a grounding
type attachment plug.

Exception: A listed range hood distinctly marked to identify
it as protected by a system of double insulation, or its
equivalent, shall not be required to be terminated with a
grounding-type attachment plug.

(2) The length of the cord shall not be less than 450 mm
(18 in.) and not over 900 mm (36 in.).
(3) Receptacles shall be located to avoid physical damage
to the
flexible cord.
(4) The receptacle shall be accessible.
(5) The receptacle shall be supplied by an individual
branch circuit.
[ROP 1721]


Check your manufacturers installation instructions. In the absence of specific directions for this situation then I would consult with a licensed electrician. There is the potential for damage if close enough to the heat source.




Knowledge is power, but sharing knowledge brings peace!

http://www.psinspection.com

TREC License# 7593

Professional Real Estate Inspections for the counties of Collin, Rockwall, Hunt, Dallas, Tarrant, Kaufman and all surrounding areas. If you want the the best you will find it with PS Inspection & Property Services LLC!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wood Cabinets over Range Top Skip Erwin Interior Inspections 2 4/15/07 8:14 PM
Range Hood Duct Length DSuelflow Inspecting HVAC Systems 3 1/24/07 6:41 AM
Range Clearance dsmith6 Interior Inspections 18 1/7/07 9:55 PM
Range exhaust hood question mmorgan Interior Inspections 24 4/20/06 9:50 PM


All times are GMT -4. The time now is 4:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts