This just looks wrong to me,any comments?
Greg Allen,Certified Home Inspector NC License# 2239 NACHI ID# 05082583 Buyers Protection Group Apex, NC 27502 "Greater Raleigh-Durham Home Inspections and Radon Mitigation Services" http://homeinspectorguy.com "Paying attention to simple little things that most men neglect makes a few men rich" Henry Ford |
| Need a home inspection in New Hampshire? Check out InterNACHI's listing of New Hampshire certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
I'll let a sparky address, but I'm pretty sure that blue box is not listed for use with 220 VAC.
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#3
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Not enough detail is shown to see if that box has the proper clamp for that size cable. I don't know why someone would think a two gang box could not be used on a 240 volt circuit, or maybe that blue is only for 120 volts.
|
|
#4
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Unless the box is improperly sized or the cable is subject to physical damage I see nothing wrong with it. Maybe someone could say that the box is not installed as per it's listing but to me that's a stretch. The receptacle used as a disconnect for an electric range is required to be accessible after the range is installed. This is usually by removing the bottom drawer on the range.
Quote:
|
|
#5
|
|||
|
|||
|
It would have to be a 20 cuin box or bigger I believe. I don't think that type plastic boxes are usually allowed to be surface mounted and you also have unprotected non-metallic cable there. I would refer it out to a licensed Electrician. They could replace that with a surface mount receptacle and cover the wire with flexible conduit through the floor.
|
|
#6
|
||||
|
||||
|
Quote:
Because it's a floor mounted box, it would have to be specifically listed for such use. What you normally see is a much more rugged type of plastic. That blue box is very likely to be cracked if the range hits it the wrong way. If I were the AHJ, I'd make the electrician prove the box is listed as acceptable for a floor mount. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#7
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Just for the sake of argument, I would say the box is not mounted on the floor. It is nailed to the framing near the floor.
The box, regardless of style, is told where to be installed in the manufacturers instructions to avoid any conflict with hitting any part of the stove to avoid any damage. I would have expected to see either a surface mount receptacle or a metal box with the correct coverplate, but don't see any reason to reject this install. That box is probably a 34 cubic inch box. A 20 cubic inch box would still be a single gang box. |
|
#8
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Even if this were 6/3 NM cable the box would need to be 38 cu inches, not overly large for a two gang box. Here's the calculation:
3-#6 conductors * 5 cu in/ conductor= 15 cu in 1-#8 conductor * 3 cu in/conductor = 3 cu in 1-2 gang device * (2*5) cu in/gang= 20 cu in Total: 38 cu inches minimum box size. |
|
#9
|
|||
|
|||
|
I came up with 20 cu in but this says the calculator states 23 cu in. They make extra deep plastic boxes that are allot thicker. The wires can fit into a deep box but I still don't like exposed plastic boxes unless they are meant to be connected to conduit. Here is a handy link.
http://www.constructionmonkey.com/ca...l/boxfill.aspx |
|
#10
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I tried that calculator and algorithm for #6 conductors on a device is incorrect. Last edited by Robert Meier; 12/2/10 at 5:38 AM.. Reason: Added note |
|
#11
|
|||
|
|||
|
I was using #6 and I do think the calculator is wrong. I used another program I have and it's different at 27.25.
3-#6=15 1-Divice (2x conductor)=10 and 1-#12 ground 2.25. |
|
#12
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
3-#6 conductors * 5 cu in/ conductor= 15 cu in 1-#10 conductor * 2.5 cu in/conductor = 2.5 cu in 1-1 gang device * (2*5) cu in/gang= 10 cu in Total: 27.5 cu inches minimum box size. |
|
#13
|
||||
|
||||
|
Don't like the exposed cable. |
| Need a home inspection in New Hampshire? Check out InterNACHI's listing of New Hampshire certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
|||
|
|||
|
I guess if you really want a reason to give them a headache then you could write down the bold/underlined below. 334.15 Exposed Work. In exposed work, except as provided in 300.11(A), cable shall be installed as specified in 334.15(A) through (C). (A) To Follow Surface. Cable shall closely follow the surface of the building finish or of running boards. (B) Protection from Physical Damage. Cable shall be protected from physical damage where necessary by rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, Type RTRC marked with the suffix -XW, or other approved means. Where passing through a floor, the cable shall be enclosed in rigid metal conduit, intermediate metal conduit, electrical metallic tubing, Schedule 80 PVC conduit, Type RTRC marked with the suffix -XW, or other approved means extending at least 150 mm (6 in.) above the floor. However, if installed properly I would call it a non-issue but since we are all doing the calculations and all that jazz... Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Outlet behind cooktop | srowe | Electrical Inspections | 12 | 5/17/08 2:02 PM |
| Electric Range Receptacle | jtedesco1 | Electrical Inspections | 4 | 5/16/08 9:29 PM |
| Range hood | Ian Gills | Electrical Inspections | 3 | 2/2/07 8:14 AM |