Default Range receptacle box

This just looks wrong to me,any comments?
Attached Thumbnails
range-receptacle-box-dsc08427.jpg   range-receptacle-box-dsc08429.jpg  



Greg Allen,Certified Home Inspector
NC License# 2239
NACHI ID# 05082583
Buyers Protection Group
Apex, NC 27502
"Greater Raleigh-Durham Home Inspections and Radon Mitigation Services"

http://homeinspectorguy.com


"Paying attention to simple little things that most men neglect makes a few men rich" Henry Ford
Reply With Quote
Need a home inspection in New Hampshire? Check out InterNACHI's listing of New Hampshire certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 12/1/10, 11:15 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Range receptacle box

I'll let a sparky address, but I'm pretty sure that blue box is not listed for use with 220 VAC.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 12/1/10, 4:11 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range receptacle box

Not enough detail is shown to see if that box has the proper clamp for that size cable. I don't know why someone would think a two gang box could not be used on a 240 volt circuit, or maybe that blue is only for 120 volts.
Reply With Quote
  #4  
Old 12/1/10, 5:24 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range receptacle box

Unless the box is improperly sized or the cable is subject to physical damage I see nothing wrong with it. Maybe someone could say that the box is not installed as per it's listing but to me that's a stretch. The receptacle used as a disconnect for an electric range is required to be accessible after the range is installed. This is usually by removing the bottom drawer on the range.

Quote:
422.33 Disconnection of Cord-and-Plug-Connected Appliances.
(A) Separable Connector or an Attachment Plug and Receptacle. For cord-and-plug-connected appliances, an accessible separable connector or an accessible plug and receptacle shall be permitted to serve as the disconnecting means. Where the separable connector or plug and receptacle are not accessible, cord-and-plug-connected appliances shall be provided with disconnecting means in accordance with 422.31.
(B) Connection at the Rear Base of a Range. For cord-and-plug-connected household electric ranges, an attachment plug and receptacle connection at the rear base of a range, if it is accessible from the front by removal of a drawer, shall be considered as meeting the intent of 422.33(A).
Reply With Quote
  #5  
Old 12/1/10, 6:01 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Range receptacle box

It would have to be a 20 cuin box or bigger I believe. I don't think that type plastic boxes are usually allowed to be surface mounted and you also have unprotected non-metallic cable there. I would refer it out to a licensed Electrician. They could replace that with a surface mount receptacle and cover the wire with flexible conduit through the floor.
Reply With Quote
  #6  
Old 12/1/10, 6:20 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Range receptacle box

Quote:
Originally Posted by Jim Port View Post
I don't know why someone would think a two gang box could not be used on a 240 volt circuit, or maybe that blue is only for 120 volts.
Perhaps I misspoke about the listing being due to the voltage or amperage. But you can bet there's a reason why it's not acceptable or you'd see them all them time like that.

Because it's a floor mounted box, it would have to be specifically listed for such use. What you normally see is a much more rugged type of plastic. That blue box is very likely to be cracked if the range hits it the wrong way. If I were the AHJ, I'd make the electrician prove the box is listed as acceptable for a floor mount.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #7  
Old 12/1/10, 7:38 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range receptacle box

Just for the sake of argument, I would say the box is not mounted on the floor. It is nailed to the framing near the floor.

The box, regardless of style, is told where to be installed in the manufacturers instructions to avoid any conflict with hitting any part of the stove to avoid any damage.

I would have expected to see either a surface mount receptacle or a metal box with the correct coverplate, but don't see any reason to reject this install.

That box is probably a 34 cubic inch box. A 20 cubic inch box would still be a single gang box.
Reply With Quote
  #8  
Old 12/1/10, 8:11 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range receptacle box

Even if this were 6/3 NM cable the box would need to be 38 cu inches, not overly large for a two gang box. Here's the calculation:


3-#6 conductors * 5 cu in/ conductor= 15 cu in
1-#8 conductor * 3 cu in/conductor = 3 cu in
1-2 gang device * (2*5) cu in/gang= 20 cu in

Total: 38 cu inches minimum box size.
Reply With Quote
  #9  
Old 12/1/10, 10:27 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Range receptacle box

I came up with 20 cu in but this says the calculator states 23 cu in. They make extra deep plastic boxes that are allot thicker. The wires can fit into a deep box but I still don't like exposed plastic boxes unless they are meant to be connected to conduit. Here is a handy link.
http://www.constructionmonkey.com/ca...l/boxfill.aspx
Reply With Quote
  #10  
Old 12/2/10, 5:01 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range receptacle box

Quote:
Originally Posted by rernst1 View Post
I came up with 20 cu in but this says the calculator states 23 cu in. They make extra deep plastic boxes that are allot thicker. The wires can fit into a deep box but I still don't like exposed plastic boxes unless they are meant to be connected to conduit. Here is a handy link.
http://www.constructionmonkey.com/ca...l/boxfill.aspx
What size conductors/number of did you use to come up with 20 cu in?

I tried that calculator and algorithm for #6 conductors on a device is incorrect.

Last edited by Robert Meier; 12/2/10 at 5:38 AM.. Reason: Added note
Reply With Quote
  #11  
Old 12/2/10, 4:14 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Range receptacle box

I was using #6 and I do think the calculator is wrong. I used another program I have and it's different at 27.25.
3-#6=15 1-Divice (2x conductor)=10 and 1-#12 ground 2.25.
Reply With Quote
  #12  
Old 12/2/10, 11:55 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Range receptacle box

Quote:
Originally Posted by rernst1 View Post
I was using #6 and I do think the calculator is wrong. I used another program I have and it's different at 27.25.
3-#6=15 1-Divice (2x conductor)=10 and 1-#12 ground 2.25.
My apologies, I missed the fact that this was single gang box and a #10 EGC. Usually the EGC in a cable containing #6 conductors is a #10. Therefore my calculation should have been:

3-#6 conductors * 5 cu in/ conductor= 15 cu in
1-#10 conductor * 2.5 cu in/conductor = 2.5 cu in
1-1 gang device * (2*5) cu in/gang= 10 cu in

Total: 27.5 cu inches minimum box size.
Reply With Quote
  #13  
Old 12/3/10, 4:57 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Range receptacle box

Quote:
Originally Posted by gallen1 View Post
This just looks wrong to me,any comments?

Don't like the exposed cable.
Reply With Quote
Need a home inspection in New Hampshire? Check out InterNACHI's listing of New Hampshire certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 12/8/10, 10:29 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Range receptacle box

I guess if you really want a reason to give them a headache then you could write down the bold/underlined below.

334.15 Exposed Work.
In exposed work, except as provided
in 300.11(A), cable shall be installed as specified in
334.15(A) through (C).

(A) To Follow Surface.
Cable shall closely follow the surface
of the building finish or of running boards.

(B) Protection from Physical Damage.
Cable shall be
protected from physical damage where necessary by rigid
metal conduit, intermediate metal conduit, electrical metallic
tubing, Schedule 80 PVC conduit, Type RTRC marked
with the suffix -XW, or other approved means. Where passing
through a floor, the cable shall be enclosed in rigid
metal conduit, intermediate metal conduit, electrical metallic
tubing, Schedule 80 PVC conduit, Type RTRC marked
with the suffix -XW, or other approved means extending at
least 150 mm (6 in.) above the floor.

However, if installed properly I would call it a non-issue but since we are all doing the calculations and all that jazz...




Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Outlet behind cooktop srowe Electrical Inspections 12 5/17/08 2:02 PM
Electric Range Receptacle jtedesco1 Electrical Inspections 4 5/16/08 9:29 PM
Range hood Ian Gills Electrical Inspections 3 2/2/07 8:14 AM


All times are GMT -4. The time now is 9:23 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts