Default Re-Bar Ground Rod

For the second time in one week, I found standard re-bar placed for the main panel ground. Of course, the rods were very rusted, which I believe causes a potential bonding issue. To the best of my knowledge, all ground rods must a non-corrosive material, such as copper. In both cases. the rods were set in a concrete slab, one in a garage and the other in a basement. Looking for opinions, as I did call these out for correction.

John Evans
AIM Home Inspection, Inc.
Attached Thumbnails
re-bar-ground-rod-airdrie-018.jpg  
Reply With Quote
  #2  
Old 12/2/07, 2:01 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Re-Bar Ground Rod

trip/impalement hazard. Any thing else?

tom
Reply With Quote
  #3  
Old 12/2/07, 2:03 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Re-Bar Ground Rod

Hmmm...are you sure they are not UFER connections?..kinda looks like 4 AWG Solid going to it.......while I dont like the ACORN at the connections...many have no problem with it...so since we see a Concrete Floor, Re-bar and 4 AWG......could it not be a UFER connection....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #4  
Old 12/2/07, 2:06 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Re-Bar Ground Rod

Quote:
Originally Posted by pabernathy
Hmmm...are you sure they are not UFER connections?

Wrong clamp for ufer, right.

tom
Reply With Quote
  #5  
Old 12/2/07, 2:08 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Re-Bar Ground Rod

generally...but seen used all the time.....you know the ole saying...." Clamp does not define the connection...if clamped by someone not knowing what a proper clamp is "



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #6  
Old 12/2/07, 2:11 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Re-Bar Ground Rod

Either way.......sticking out like it is would indeed be dangerous...lord knows kids playing around it could be impaled....heck adults even...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #7  
Old 12/2/07, 2:33 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Re-Bar Ground Rod

Quote:
Originally Posted by jevans
For the second time in one week, I found standard re-bar placed for the main panel ground. Of course, the rods were very rusted, which I believe causes a potential bonding issue. To the best of my knowledge, all ground rods must a non-corrosive material, such as copper. In both cases. the rods were set in a concrete slab, one in a garage and the other in a basement. Looking for opinions, as I did call these out for correction.

John Evans
AIM Home Inspection, Inc.
You found a: Concrete-Encased Electrode............
consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive
coated steel reinforcing bars or rods of not less than 13 mm (
12 in.) in diameter, ....... this is an acceptable method.

Reply With Quote
  #8  
Old 12/2/07, 2:47 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Re-Bar Ground Rod

lol....better late than never JOE...LOL....Glad to see ya



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #9  
Old 12/2/07, 2:51 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Re-Bar Ground Rod

As stated in my first post....it is a CEE...but it appears many are still not sure what they are. I did a seminar yesterday and asked the guys...do they know what a UFER is and only (2) electricians in the class said they did.....I found that shocking actually.....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #10  
Old 12/2/07, 3:10 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Re-Bar Ground Rod

Do you find the same joe at your seminars....you speak about CEE or "UFER" and the majority act like they have no clue what it is......very strange as I have known about them since I started in the field....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #11  
Old 12/2/07, 3:19 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Re-Bar Ground Rod

Quote:
Originally Posted by pabernathy
lol....better late than never JOE...LOL....Glad to see ya
Paul:

Same here!

The "one or more" part was made clear to clarify up one of Mike's Proposals for the 1981/84 revision, when he sent in 125 proposals. This one asked to make it clear that the rebar had to be in one continuous length, and CMP-5 said they never expected them to be a full 20 ft. the 4 AWG is required to be the full 20 feet as so stated.

UFER was his name and was well known ....... PS: Expert needed to add information here ........
Reply With Quote
  #12  
Old 12/2/07, 3:27 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Re-Bar Ground Rod

no additional info needed...lol.......We have SPOKEN !



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #13  
Old 12/2/07, 3:33 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Re-Bar Ground Rod

This is what I was referring too in my like:

This article or section is in need of attention from an expert on the subject.

Please help recruit one or improve this article yourself. See the talk page for details.

Please consider using {{Expert-subject}} to associate this request with a WikiProject

I am never finished talking,
Reply With Quote
  #14  
Old 12/2/07, 3:38 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Re-Bar Ground Rod

Quote:
Originally Posted by pabernathy
Do you find the same joe at your seminars....you speak about CEE or "UFER" and the majority act like they have no clue what it is......very strange as I have known about them since I started in the field....
True, it probably depends on where they went to school, some in vocational where the teacher was an electrician, or others in the field, and some with no training at all.

The subject of the UFER is covered in many IAEI articles now and as far back as the 50's, I have the original magazine articles written by Herbert Ufer and Eustace Soares.

See Page 370

Last edited by jtedesco1; 12/2/07 at 3:49 PM..
Reply With Quote
  #15  
Old 12/2/07, 3:55 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Re-Bar Ground Rod

loll...I hear ya....sad thing is these seminars are CE Required ones and I would expect them to know what a UFER is.....but alas when they leave my class they know what one is...and how to install it properly...lol



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 4:56 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 12:39 PM
Two ground wires jlybolt Electrical Inspections 8 8/10/06 3:06 PM
Harmonized Ground Fault Circuit Interrupters jtedesco1 Electrical Inspections 5 3/21/06 9:48 AM


All times are GMT -4. The time now is 8:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts