Fellow Inspectors,

I wrote up neutrals and grounds sharing terminations and Cutler-Hammer breakers installed in a GE panel. Home is 68 years old. Electrician says "Cutler-Hammer breakers are interchangeable with GE breakers" & " Panel installed prior to 2003 NEC code requirement for separating grounds and neutrals."
Any idea when 408.21 was introduced? The claim that the breakers are interchangeable is wrong, but he has the license...

Anatol
Reply With Quote
Find an InterNACHI certified New Jersey Home Inspector (and anywhere else in North America)
  #2  
Old 11/8/09, 1:31 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 7,489
Send a message via Yahoo to bboerner
Default Re: Re-Inspection

Code is a minimum and code is updated due to safety concerns 9 times out of ten. Who cares if it wasn't code before hand. Its code now and if you ask me good call.

As for breakers...

Breakers...What's the Difference?
From time to time there may be a need to change a breaker or add one to your electrical panel. Most electrical devices, like switches, outlets and such, can be switched out with another brand without any problems. Breakers, however, are brand specific and require the exact replacement type to function properly in the electrical panel. Because of different mounting techniques, thickness of buss bars, and whether the breakers are press in or bolt on, it is necessary to use the appropriate breaker for the specific panel.

What's Wrong With Using Another Brand?
Although a breaker from another manufacturer may fit in the panel you have, the differences that you don't see may cause a electrical nightmare. Some breakers clamp over the buss bar, while other bolt onto the buss. Some breaker bases clamp onto a mounting bar, while others slide into a groove to secure the breaker. The tension that the breaker contacts are set for is brand-specific.

Will Another Brand Fit?
Yes, another brand, say Bryant breakers, will fit into a GE breaker slot. The manufacturer will tell you that they are not responsible for damage to the panel if you use a different manufacturers breaker.

Snap-in or Bolt-in?
Electrical panels come in different styles for residential, commercial, and industrial installations. While snap-in type breaker panels are used for residential and commercial installations, normally, bolt-in breakers are used for industrial installations where vibration may be a concern and a continuously tight contact is needed.

Same Manufacturer, Different Breakers
Square D has a Q0 series panel that has a different type breaker than their Homeline panel does. They both accomplish the same thing, but the construction is quite different. Notice in the photo how the Homeline breaker(left) physically mounts and how there is no way it could replace the Q0 breaker in the center of the photo. These breakers are even made by the same company, making the breaker selection even more critical. Also notice how the Cutler Hammer breaker mounts. It too is much different. That means, only replace a breaker with an exact match.

How Do I Know What Type Breaker I Have?
The breaker is maker on the side with type and amperage. If you open the panel door and look on the inside cover of the door, there is a label that should also tell you what type breaker that you need.

Q: What does the label say?



Bill Boerner
STL Home Inspection Services LLC
Serving St. Louis/Surrounding
(314) 805-2137
office@stlhomeinspector.com
http://www.stlhomeinspector.com
Residential, Commercial, Radon, Termite, Lateral Sewer Scopes

Last edited by bboerner; 11/8/09 at 1:35 PM..
Reply With Quote
  #3  
Old 11/8/09, 1:40 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Re-Inspection

It never has been permitted technically by UL67 and under NEC 110.3(B).

It was clarified in NEC 408.21 In 2005, this reference was moved to 408.41 (I lack that copy.)


110.14(A) and 110.3(B)..."Terminals for more than one conductor and terminals used to connect aluminum shall be so identified."
408.21 Grounded Conductor Terminations. Each grounded conductor shall terminate within the panel board in an individual terminal that is not also used for another conductor.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 11/8/09, 4:28 PM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Re-Inspection

Thanks, That is what I thought..
Reply With Quote
  #5  
Old 11/8/09, 4:30 PM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Re-Inspection

The label says only GE Breakers, It is on the electrician as he put it in writing.
Reply With Quote
  #6  
Old 11/13/09, 5:02 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: Re-Inspection

Quote:
Originally Posted by apolillo View Post
Fellow Inspectors,

I wrote up neutrals and grounds sharing terminations and Cutler-Hammer breakers installed in a GE panel. Home is 68 years old. Electrician says "Cutler-Hammer breakers are interchangeable with GE breakers" & " Panel installed prior to 2003 NEC code requirement for separating grounds and neutrals."
Any idea when 408.21 was introduced? The claim that the breakers are interchangeable is wrong, but he has the license...

Anatol
I cannot tell you exactly when the practice regarding landing grounding and grounded conductors under the same terminal came in to being but I can tell you that it was long before 2003. That was one of the first things I learned as an apprentice electrician in the mid 1970s. If I can find one of my old code books from then, I'll look it up.

The oldest NEC that I have in my office is the 1987. 110-14(a) covering two conductors under a single terminal has been rewritten but the provision has remained essentially the same since then.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
  #7  
Old 11/13/09, 5:14 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Re-Inspection

I would call the manufacturer of the panel. they will be able to tell you. I do it quite often, and they have people to answer the questions. I would check local codes about the shared wires. Here the code did not change until 03. Anything prior, doubling up is kosher.




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #8  
Old 11/14/09, 7:01 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Re-Inspection

Quote:
Originally Posted by sfogarty View Post
I would call the manufacturer of the panel. they will be able to tell you. I do it quite often, and they have people to answer the questions. I would check local codes about the shared wires. Here the code did not change until 03. Anything prior, doubling up is kosher.
Doubling up the neutrals was NOT kosher prior to 03. It was in the manufacturers instructions and would need to be followed under 110.3(B). It was added to the NEC as a specific requirement around 03.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 4:09 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts