Default Receptacle 16" above Electric Baseboard

I've seen plenty of situations (and pics on this forum) where the receptacle was either covered by the electric baseboard heater or immediately above it.

Here are pictures of a home built in 2004 with a finished basement. The receptacles are 16" above the baseboard heaters. This occurs above all 3 heaters in this bonus room and one more time in the basement "office". I say no good, but is there anything to back this up?

Thanks!!
Attached Thumbnails
receptacle-16-above-electric-baseboard-p1280033.jpg   receptacle-16-above-electric-baseboard-p1280034.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
Need a home inspection in Kansas? Check out InterNACHI's listing of Kansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 5/13/11, 6:43 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacle 16" above Electric Baseboard

You would need to check with the baseboard manufacturer to see if they prohibit receptacles above electric baseboard. Almost all manufacturers do prohibit this type of installation.
Reply With Quote
  #3  
Old 5/13/11, 7:00 PM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Receptacle 16" above Electric Baseboard

Interior: Electric Baseboard heaters/outlets
LOCATION(S): Interior rooms.
Outlets installed above electric baseboard heaters in one or more areas–not a recommended and a potentially unsafe practice.All manufacturers of electric baseboard heaters prohibit the installation of electrical outlets above the heaters. Electric baseboard heaters work by turning a heating element on and off; it's either hot or it's not, nothing in-between. Because they get so hot, an electric wire draped in front of a baseboard heater could potential melt or start a fire- recommend corrective action as necessary by relocating outlets or use caution when using outlets or don’t use at all.

Reply With Quote
  #4  
Old 5/13/11, 7:59 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacle 16" above Electric Baseboard

Note that no mention is made for hydronic baseboard, only electric baseboard.
Reply With Quote
  #5  
Old 5/13/11, 8:44 PM
Mark S. Tyson Mark S. Tyson is offline
InterNACHI Member
 
Join Date: Jun 2009
Location: Fort Pierce, Fl.
Posts: 359
Default Re: Receptacle 16" above Electric Baseboard

I'm curious as too how the cold areas of the Country deal with this issue and also meet the N.E.C. for required outlets no more than 12' apart and no further than 6' from a corner. While here in Florida, I have never seen base board heating I would think that the areas that use this method would have difficulty meeting the requirement for outlet spacing, clearance, and minimum temperature adjustment



Mark S. Tyson

M Tyson construction LLC
Tyson Home Inspections

Certified General Contractor #1516843
Florida Licensed Home Inspector #1824
Member N.A.C.H.I.
IAC2 certified
Member Florida Building Officials Association
http://www.TysonHomeInspections.com
Reply With Quote
  #6  
Old 5/13/11, 9:01 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacle 16" above Electric Baseboard

They make receptacles that replace the blank cover on the end of the heater section. Here's an example:
Reply With Quote
  #7  
Old 5/13/11, 10:42 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Receptacle 16" above Electric Baseboard

Quote:
Originally Posted by Robert Meier View Post
You would need to check with the baseboard manufacturer to see if they prohibit receptacles above electric baseboard. Almost all manufacturers do prohibit this type of installation.
The nameplate was not visible and I'm not going to act like Mr. Holmes and start tearing things apart. The property was vacant and I'm making an assumption that the basement was finished by a previous owner with without permits or without inspections... Just a normal day in the neighborhood even though I know what the meaning of "ASSuME" is. The report will be published tomorrow.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #8  
Old 5/13/11, 10:44 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Receptacle 16" above Electric Baseboard

Quote:
Originally Posted by Robert Meier View Post
They make receptacles that replace the blank cover on the end of the heater section. Here's an example:
I saw this picture in a previous post. This is why this post exists. It isn't relevant to the situation observed and this device would cause me to ask many more questions...Good picture, though.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In

Last edited by gliebig; 5/13/11 at 10:47 PM.. Reason: Removed Picture from Quote
Reply With Quote
  #9  
Old 5/13/11, 10:55 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Receptacle 16" above Electric Baseboard

Quote:
Originally Posted by mtyson View Post
I'm curious as too how the cold areas of the Country deal with this issue and also meet the N.E.C. for required outlets no more than 12' apart and no further than 6' from a corner. While here in Florida, I have never seen base board heating I would think that the areas that use this method would have difficulty meeting the requirement for outlet spacing, clearance, and minimum temperature adjustment
The baseboard heaters were approximately 5 to 6 feet long. I believe the requirements are to have a receptacle within 6 feet of each other on open wall space so it would work depending on the geometry of the room. Good question to spur more thought. What takes precedent? Heat or Power?



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #10  
Old 5/13/11, 11:00 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Receptacle 16" above Electric Baseboard

Quote:
Originally Posted by mtyson View Post
I'm curious as too how the cold areas of the Country deal with this issue and also meet the N.E.C. for required outlets no more than 12' apart and no further than 6' from a corner. While here in Florida, I have never seen base board heating I would think that the areas that use this method would have difficulty meeting the requirement for outlet spacing, clearance, and minimum temperature adjustment
In Minnesota, typically the only baseboard heaters we have here are hydronic. Very rarely do I find electric baseboards in any location. The homes with baseboards are older homes that originally had radiators and were converted to baseboards, or homes converted to apartments (very common). As for outlets, new construction is no issue, as most every home has HE HVAC. Older homes, do not need to meet the newer standards until reno'd. Usually, they get it right, but not always. I only need to write this up probably 2 or 3 times a year.
Reply With Quote
  #11  
Old 5/13/11, 11:02 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Receptacle 16" above Electric Baseboard

Quote:
Originally Posted by gliebig View Post
Good question to spur more thought. What takes precedent? Heat or Power?
As my neighbor to the East, you know that a person can live without power, but would never survive our winter's without heat.
Reply With Quote
  #12  
Old 5/13/11, 11:09 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Receptacle 16" above Electric Baseboard

Greg there are certain clearance requirements for anything attached to that outlet,Appliance cords,etc.

Go here for help......http://www.cadetco.com/support/ownersguides/1004.pdf
Reply With Quote
  #13  
Old 5/14/11, 5:21 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacle 16" above Electric Baseboard

Quote:
Originally Posted by gliebig View Post
The baseboard heaters were approximately 5 to 6 feet long. I believe the requirements are to have a receptacle within 6 feet of each other on open wall space so it would work depending on the geometry of the room. Good question to spur more thought. What takes precedent? Heat or Power?
The NEC requirement is within 6' of entering the room and no more than 12' foot between thereafter. Also any wall 2' of more get a receptacle, like behind a door or between cloosets.
Reply With Quote
Need a home inspection in Kansas? Check out InterNACHI's listing of Kansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 5/14/11, 8:15 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacle 16" above Electric Baseboard

Quote:
Originally Posted by gliebig View Post
I saw this picture in a previous post. This is why this post exists. It isn't relevant to the situation observed and this device would cause me to ask many more questions...Good picture, though.
Mark asked about receptacle compliance so I posted the photo. This is one way that you can comply with the NEC regarding having receptacles installed in a room and not have them above the electric baseboard. If you had a room with continuous or long runs of baseboard you could have the receptacles in the baseboard for NEC compliance.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 77 5/10/12 6:13 PM
Electrical Safety Media Center jtedesco1 Electrical Inspections 1 3/15/08 8:18 AM


All times are GMT -4. The time now is 9:24 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts