What do you typically recommend when you come across this type of installation?

Receptacle above baseboard heating. This one is a little different in that it's actually blocked as well.
Attached Thumbnails
receptacle-outletabovebaseboardheater.jpg  



Vince Santos
Owner / Certified Home Inspector
StepByStep Home Services LC
(734) 748-9584
http://www.stepbystepinspections.com
Providing Home Inspection Services to Southeast Michigan

Active Rain blog
http://activerain.com/sbsinspections

ITA Trained and Certified
Reg104669Cc

Reply With Quote
  #2  
Old 12/16/08, 10:22 AM
James F. McKee's Avatar
James F. McKee James F. McKee is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Amherst, Oh
Posts: 4,403
Default Re: receptacle

Quote:
Originally Posted by vsantos View Post
What do you typically recommend when you come across this type of installation?

Receptacle above baseboard heating. This one is a little different in that it's actually blocked as well.
Repair by a qualified electrician....nice picture Vince



Classic Home inspections

Jim Mckee
Amherst, Ohio

www.amhersthomeinspector.com
Reply With Quote
  #3  
Old 12/16/08, 10:23 AM
bdoles2's Avatar
bdoles2 bdoles2 is offline
Active Poster
 
Join Date: Aug 2006
Location: Atlanta, GA
Posts: 2,927
Please Note: bdoles2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: receptacle

As a minimum I'd recommend removal of the outlets, to be replaced with a blank double gang cover. This will eliminate even the thought of plugging in something.

And as James states, to be done by a licensed electrician.
Reply With Quote
  #4  
Old 12/16/08, 10:26 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: receptacle

Quote:
Originally Posted by vsantos View Post
What do you typically recommend when you come across this type of installation?

Receptacle above baseboard heating. This one is a little different in that it's actually blocked as well.
Depends on whether the baseboard is electric or hot water.

Of course the half covered receptacles are a problem worth noting.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #5  
Old 12/16/08, 10:29 AM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,442
Default Re: receptacle

There should be no outlet above a heater
Reply With Quote
  #6  
Old 12/16/08, 10:31 AM
Vince Santos's Avatar
Vince Santos Vince Santos is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Canton, MI - Serving Souteast Michigan
Posts: 1,039
Default Re: receptacle

Quote:
Originally Posted by mlarson View Post
Depends on whether the baseboard is electric or hot water.

Of course the half covered receptacles are a problem worth noting.
The baseboard heat in this area was electric.



Vince Santos
Owner / Certified Home Inspector
StepByStep Home Services LC
(734) 748-9584
http://www.stepbystepinspections.com
Providing Home Inspection Services to Southeast Michigan

Active Rain blog
http://activerain.com/sbsinspections

ITA Trained and Certified
Reg104669Cc

Reply With Quote
  #7  
Old 12/16/08, 10:45 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: receptacle

Quote:
Originally Posted by vsantos View Post
The baseboard heat in this area was electric.
Then removal is the only option.

This does not apply to baseboard hot water systems.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #8  
Old 12/16/08, 7:29 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: receptacle

Quote:
Originally Posted by mlarson View Post
Then removal is the only option.
You could actually enhance the nature of the hazard if you step into recommending how the hazard is to be remediated. If this receptacle is installed to satisfy spacing rules, summary elimination of the receptacle is not the fix for the hazard. Removing the receptacle and installing two more, each at the outboard ends of the heater, is more likely the fix the electrician will have to do.
Reply With Quote
  #9  
Old 12/16/08, 7:43 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: receptacle

Quote:
Originally Posted by Marc D. Shunk View Post
You could actually enhance the nature of the hazard if you step into recommending how the hazard is to be remediated. If this receptacle is installed to satisfy spacing rules, summary elimination of the receptacle is not the fix for the hazard. Removing the receptacle and installing two more, each at the outboard ends of the heater, is more likely the fix the electrician will have to do.
I'm not sure what you are saying Marc.

Has is ever been code to have electrical outlets above electric baseboard?



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #10  
Old 12/16/08, 7:45 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: receptacle

Quote:
Originally Posted by mlarson View Post
Has is ever been code to have electrical outlets above electric baseboard?
No, it's never been in the code, per se - save for 110.3(B) which is a general rule that manufacturer's rules be followed. All electric baseboard heaters have instructions that forbid a receptacle over them. Even if they didn't, it's at least a stupid place for a receptacle. You're allowed to call out stupid things.
Reply With Quote
  #11  
Old 12/16/08, 7:46 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: receptacle

Quote:
Originally Posted by mlarson View Post
I'm not sure what you are saying Marc.
Was it the spacing rules that have you mixed up, maybe?
Reply With Quote
  #12  
Old 12/16/08, 7:54 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: receptacle

Quote:
Originally Posted by Marc D. Shunk View Post
Was it the spacing rules that have you mixed up, maybe?
I am very familiar with the spacing rules.

The heater was likely installed after construction in an unacceptable manner.

I'd rather have no receptacle there and violate the spacing rule than have the fire hazard of a cord draped over the heater.

Either way it needs to be called out. Remove one or the other.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #13  
Old 12/16/08, 8:00 PM
ccurrins's Avatar
ccurrins ccurrins is offline
Active Poster
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 3,233
Please Note: ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: receptacle

Quote:
Originally Posted by mlarson View Post
I am very familiar with the spacing rules.

The heater was likely installed after construction in an unacceptable manner.

I'd rather have no receptacle there and violate the spacing rule than have the fire hazard of a cord draped over the heater.

Either way it needs to be called out. Remove one or the other.
So you don't agree with Mark on replacing instead of removing? That is what I would recommend. You even said the rec. was most likely there before the heater.
Reply With Quote
  #14  
Old 12/16/08, 8:02 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: receptacle

Quote:
Originally Posted by ccurrins View Post
So you don't agree with Mark on replacing instead of removing? That is what I would recommend. You even said the rec. was most likely there before the heater.
I'm puzzled why you'd recommend any particular repair at all. Wouldn't the more prudent approach be to simply point out that it's being there is a hazard, and recommend an electrician correct it? Whether the electrician simply blanks it off or whether he blanks it off and installs another 1 or 2 outside of the heater's length should be up to someone besides the home inspector. Sorry, but I get a little cranked up when a home inspector attempts to tell the homeowner or buyer how I ought to effect the repair.
Reply With Quote
  #15  
Old 12/16/08, 8:21 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: receptacle

Quote:
Originally Posted by Marc D. Shunk View Post
I'm puzzled why you'd recommend any particular repair at all. Wouldn't the more prudent approach be to simply point out that it's being there is a hazard, and recommend an electrician correct it? Whether the electrician simply blanks it off or whether he blanks it off and installs another 1 or 2 outside of the heater's length should be up to someone besides the home inspector. Sorry, but I get a little cranked up when a home inspector attempts to tell the homeowner or buyer how I ought to effect the repair.
Hey Marc, remove the outlet or remove the heater. I don't care.


And please get off your high horse.



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Join Cu to Al at the receptacle screws? jkogel Electrical 11 9/19/08 4:22 AM
Microwave receptacle jwardenski Electrical 17 9/9/07 8:18 PM
What's This Receptacle For? cmettel Electrical 7 5/25/07 8:35 AM
Bedroom receptacle dnasser Electrical 9 4/16/07 11:33 AM
Online Code Check- Reference pabernathy Electrical 31 11/9/06 4:39 PM


All times are GMT -4. The time now is 4:23 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts