Question Receptacle location, Code In "FLORIDA"

Florida Electrical Code
Yesterday I inspected a 6.9 M house in Rosemary Beach FLORIDA. However, I noticed that the majority of the receptacles are within one inch from the floor. In fact inside the wine cellar they are touching the floor. Do you know what the CODE requires in "FLORIDA" for receptacle location??


info@HOMEINSPECTORUSA.biz

Thanks/John
Reply With Quote
  #2  
Old 11/8/08, 10:11 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Receptacle location, Code In "FLORIDA"

Hi John,

No there is no code minimum for most receptacles


Quote:
Q3. Is there a code requirement as to the height of a receptacle outlet?

A3. No, unless the receptacle is specifically required by the NEC. For example, the required wall receptacle outlets for a dwelling unit shall not be located above 5.5 ft [210.52]. Required dwelling unit kitchen counter top receptacles shall not be located more than 20 in. above the countertop [210.52(C)(5)], and required outdoor receptacles for one and two family dwellings shall not be located more than 6.5 ft above grade [210.52(E)].
The above from MikeHolt.com

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 11/8/08, 10:31 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacle location, Code In "FLORIDA"

Heck, they can be IN the floor and still meet code.
Reply With Quote
  #4  
Old 11/8/08, 11:48 AM
John M. Acaron's Avatar
John M. Acaron John M. Acaron is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Panama City Beach, FL
Posts: 587
Question Re: Receptacle location, Code In "FLORIDA"

I understand they can be on the floor provided they have a water proof cover. These receptacles are on the wall flush with the floor. Infact there are several in the kistchen, wine cellar, hallways and bedrooms. Just want to make sure????

Do they need to be protected (water, liquids, etc)??
Reply With Quote
  #5  
Old 11/8/08, 12:00 PM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 123
Default Re: Receptacle location, Code In "FLORIDA"

Quote:
Originally Posted by jacaron View Post
Do they need to be protected (water, liquids, etc)??
No protection from wate is required by the state or federal codes.



Mike Whitt
Contractor/Instructor
Reply With Quote
  #6  
Old 11/8/08, 1:10 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacle location, Code In "FLORIDA"

Quote:
Originally Posted by jacaron View Post
I understand they can be on the floor provided they have a water proof cover.
That's not necessarily true. Short story, no matter how low a receptacle is mounted on the wall, no special protection is required. Offices often feature tombstone receptacles mounted ON the floor.

Reply With Quote
  #7  
Old 11/8/08, 1:15 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacle location, Code In "FLORIDA"

When I take the dirt nap that's what I want.
Reply With Quote
  #8  
Old 11/8/08, 1:48 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacle location, Code In "FLORIDA"

Quote:
Originally Posted by Speedy Petey View Post
When I take the dirt nap that's what I want.
You want a tombstone for your tombstone? I wonder if any dead electrician has that yet?
Reply With Quote
  #9  
Old 11/8/08, 5:23 PM
Russell J. Hensel's Avatar
Russell J. Hensel Russell J. Hensel is offline
InterNACHI Member
 
Join Date: Jul 2008
Location: Fort Myers, FL
Posts: 5,576
Default Re: Receptacle location, Code In "FLORIDA"

John - there is no Florida specific electrical code. They refer everything to the NEC. Now there maybe some local codes that affect the area.

Where I live is a barrier island and all house are now built on stilts/pilings. There is no outlet nor switch allowed to be within 5 feet of the slab grade. So all switched in the garage and for exterior lighting are 5 feet above the grade. That is a LOCAL code and not an NEC code.

If this is the case there maybe something in your area. When in doubt call the local building code officials. They usually take calls from like 8-9 and 2-3 and are most helpful and many times can tell you where you can find it in writing.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Garage/house fire door Steven C. Meyer General Inspection Discussion 15 2/5/08 7:06 AM