Default Receptacle tester malfunction????

Hey All,

anyone ever had all three lamps light up when testing an outlet? Any idea what it means?
Tested several receptacles and only one in particular in this house caused all three lamps to light up. This happened last week, after several inspections since then no other readings like that.
As always, thanks and keep safe.

Mark Ellison
Toronto
Reply With Quote
Find an InterNACHI certified Hawaii Home Inspector (and anywhere else in North America)
  #2  
Old 4/6/09, 9:30 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Receptacle tester malfunction????

Every time I have had this occur, the receptacle was improperly wired with 240 volts. You should attempt to verify this with another instrument.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 4/6/09, 9:49 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Receptacle tester malfunction????

Never had all 3 light up. But I have had the small 'Lowes' testers fail when testing GFCI function. I always keep a spare and sometimes use a SureTest for confirmation.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 4/7/09, 4:53 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Receptacle tester malfunction????

Quote:
Originally Posted by jpope View Post
Every time I have had this occur, the receptacle was improperly wired with 240 volts. You should attempt to verify this with another instrument.
Ditto down south of Jeff.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #5  
Old 4/13/09, 7:46 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 574
Default Re: Receptacle tester malfunction????

Quote:
Originally Posted by jpope View Post
Every time I have had this occur, the receptacle was improperly wired with 240 volts. You should attempt to verify this with another instrument.
Yes, this schematic shows that all 3 lights would come on with 240 volts.
Attached Thumbnails
receptacle-tester-malfunction-three-prong-tester-schematic.jpg  
Reply With Quote
  #6  
Old 4/13/09, 11:10 PM
mellison's Avatar
mellison mellison is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: GTA, ON
Posts: 190
Default Re: Receptacle tester malfunction????

Many thanks Gents!
Reply With Quote
  #7  
Old 4/19/09, 3:07 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Receptacle tester malfunction????

Ever had one show very DIM center light when using....had an electrician do this on a MUNI-Inspection and plugged the tester in and one of the lights were dimmer than the other....ended up being a poor on the neutral at the device connection...



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Would you use a floor system tester? dthomas2 Structural Inspections 24 12/23/06 12:20 PM
Online Code Check- Reference pabernathy Electrical Inspections 31 11/9/06 3:39 PM
Your old electrical wiring rray Electrical Inspections 16 8/1/06 9:51 AM
Do you trust your receptacle tester? Greg Fretwell Electrical Inspections 3 2/2/06 6:14 PM


All times are GMT -4. The time now is 9:24 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts