Default Receptacles in dwelling unit bathrooms

Question: When checking for the presence of GFCI protection for the receptacles in a bathroom, do you also verify that the receptacle in the lighting fixture, if there is one, is also protected?

In dwelling units ALL 125-volt, single-phase, 15- and 20-ampere receptacles installed in a bathroom are required to have ground-fault circuit-interrupter protection for personnel.
Reply With Quote
  #2  
Old 1/18/08, 9:07 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,471
Default Re: Receptacles in dwelling unit bathrooms

Quote:
Originally Posted by jtedesco1
Question: When checking for the presence of GFCI protection for the receptacles in a bathroom, do you also verify that the receptacle in the lighting fixture, if there is one, is also protected?

In dwelling units ALL 125-volt, single-phase, 15- and 20-ampere receptacles installed in a bathroom are required to have ground-fault circuit-interrupter protection for personnel.
Good point, Joe. Sometimes they are not real obvious.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 1/18/08, 9:14 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,161
Send a message via MSN to bwiley
Default Re: Receptacles in dwelling unit bathrooms

I can't even remember the last time I saw a receptacle on a light fixture in a bathroom!

I do note them in the report as not being GFCI protected.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #4  
Old 1/18/08, 9:26 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,471
Default Re: Receptacles in dwelling unit bathrooms

The older mirror/medicine cabinet/light combinations are typically where I've seen and occasionally on individual wall mounted light fixtures.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #5  
Old 1/18/08, 9:28 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacles in dwelling unit bathrooms

Before we get to carried away here a receptacle that is part of a light fixture does not count as one of the required receptacles and might get shot down by someone else.

Just a note of warning in case it happens but by all means write it up.
Reply With Quote
  #6  
Old 1/18/08, 9:35 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,471
Default Re: Receptacles in dwelling unit bathrooms

Quote:
Originally Posted by Mike Whitt
Before we get to carried away here a receptacle that is part of a light fixture does not count as one of the required receptacles and might get shot down by someone else.

Just a note of warning in case it happens but by all means write it up.
Are you saying that receptacles which are part of a light fixture in the bathroom, often within 3 feet of the sink, are not required to be GFCI protected? And, if so, are the mirror/medicine cabinet/light combinations the excluded as well from the requirement?

Interesting...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #7  
Old 1/18/08, 10:12 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacles in dwelling unit bathrooms

Quote:
Originally Posted by lkage
Are you saying that receptacles which are part of a light fixture in the bathroom, often within 3 feet of the sink, are not required to be GFCI protected? And, if so, are the mirror/medicine cabinet/light combinations the excluded as well from the requirement?

Interesting...
210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. Receptacle outlets required by this section shall be in addition to any receptacle that is part of a luminaire (lighting fixture) or appliance, located within cabinets or cupboards, or located more than 1.7 m (5½ ft) above the floor.

Yes please call them out as I would call them out if i was doing the inspection.

In my opinion they should be protected. What I am saying it might be called due to the above section. I have seen this debated in the past.
Reply With Quote
  #8  
Old 1/18/08, 10:24 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,471
Default Re: Receptacles in dwelling unit bathrooms

Quote:
Originally Posted by Mike Whitt
210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. Receptacle outlets required by this section shall be in addition to any receptacle that is part of a luminaire (lighting fixture) or appliance, located within cabinets or cupboards, or located more than 1.7 m (5½ ft) above the floor.

Yes please call them out as I would call them out if i was doing the inspection.

In my opinion they should be protected. What I am saying it might be called due to the above section. I have seen this debated in the past.
Thanks, calling them out and recommending GFCI's for enhanced safety often has nothing to do with code interpretation.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #9  
Old 1/18/08, 12:03 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacles in dwelling unit bathrooms

I got called away while making my last post which sometimes happens.

The NEC mandates that any receptacle installed in a bathroom be GFCI protected and I would say that a light fixture that has a receptacle installed in the bathroom would also be required to be protected.

I have always protected the complete fixture when running across these items and will continue to do so.

I was in a debate a couple years back about a medicine cabinet that had a single receptacle installed on both sides inside the cabinet by two screws. The enclosure for these receptacles didn’t have enough room to make joints and came from the factory with conductors that reached up to the junction box for the cabinet light. These conductors were #16 gauge conductors.

Now the question of how to wire these built in receptacles. The electrical contractor had installed a 15 amp circuit to the opening for the medicine cabinet not knowing or caring that it came with these receptacles.

The code enforcement officer wanted them wired to the load side to the 20 amp circuit supplying the required receptacle.

The electrical contractor said they were an integral part of the equipment and outside the scope of the NEC and that protecting the #16 conductors with a 20 amp overcurrent device was against code.

In the end the receptacles were GFCI protected from a receptacle installed in the bedroom and on the same circuit that supplied the cabinet and also Arc Fault protected by the circuit supplying the bedroom. Everybody was happy. See sometimes I do come up with a pretty good idea.
Reply With Quote
  #10  
Old 1/18/08, 12:26 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacles in dwelling unit bathrooms

A bathroom is required to be supplied by at
least one 20 amp branch circuit for the supply to the bathroom receptacle outlet(s). Such circuits cannot have any other outlets, unless the 20-ampere circuit supplies a single bathroom.



Reply With Quote
  #11  
Old 1/18/08, 1:11 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacles in dwelling unit bathrooms

Quote:
Originally Posted by jtedesco1
A bathroom is required to be supplied by at
least one 20 amp branch circuit for the supply to the bathroom receptacle outlet(s). Such circuits cannot have any other outlets, unless the 20-ampere circuit supplies a single bathroom.


Joe

Are you saying that if a circuit supplies two bathrooms then it can’t supply the receptacle that is part of the light?
Or are you saying that if the light has a receptacle that the circuit can not leave that bathroom and must protect the light and receptacle.

Help me to understand just what you mean by your post please.
Reply With Quote
  #12  
Old 1/18/08, 1:34 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacles in dwelling unit bathrooms

You said that the circuit in the bedroom was used, that's not acceptable, the 20 amp circuit to the bathroom must be installed to protect ALL ..... bathroom receptacle outlet(s) and they are to be protected by a GFCI DEVICE
Reply With Quote
  #13  
Old 1/18/08, 2:21 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacles in dwelling unit bathrooms

So what you are saying is that the receptacles that are an integral part of a UL listed piece of equipment must be protected by the same 20 amp receptacle required by 210.52(D) even if the conductors that are internal to the piece of equipment is smaller than #12 and to connect to them would violate the listing of the equipment.
Reply With Quote
  #14  
Old 1/18/08, 2:39 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacles in dwelling unit bathrooms

I believe he is saying that if you serve 2 (or more) bathrooms with the required 20a dedicated receptacle circuit that circuit can't serve any lights or fans.
If your customer insists on keeping his light/receptacle assembly you will probably be looking for a 90-4 accomedation from the AHJ to find a way to make it legal.
Reply With Quote
  #15  
Old 1/18/08, 2:47 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Receptacles in dwelling unit bathrooms

Quote:
Originally Posted by Mike Whitt
So what you are saying is that the receptacles that are an integral part of a UL listed piece of equipment must be protected by the same 20 amp receptacle required by 210.52(D) even if the conductors that are internal to the piece of equipment is smaller than #12 and to connect to them would violate the listing of the equipment.
I am insisting that the receptacle in the bathroom fixture be properly protected by a GFCI device, or it can be removed and blanked off!



Home Inspectors don't do code, STOP, please STOP quoting the Code!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What do you think? Can this work for you? jtedesco1 Electrical Inspections 21 2/26/11 3:00 PM
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
2 questions staylor5 Electrical Inspections 14 12/18/09 3:32 AM
Where is it written.... bgromicko General Inspection Discussion 18 1/19/08 10:02 PM
Illinois: Carbon Monoxide Alarm Detector Act rcramer Legislation, Licensing & Legal Issues for Inspectors 2 2/9/07 8:52 AM


All times are GMT -4. The time now is 5:53 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts