Default Recepticles on Ceiling??

Hi Electrical Experts ,

I have a question here. The pictures may be a little hard to see but this house (built in 1994) has electrical recepticles on the ceiling. They "tested" fine, but is this OK to have these on the ceiling like this? Or do you think this was a bad homeowner job to have done this?? Help.

Thanks all,
Attached Thumbnails
recepticles-ceiling-100_4557-small-.jpg.JPG
Views:	82
Size:	15.8 KB
ID:	9974   recepticles-ceiling-100_4558-small-.jpg.JPG
Views:	87
Size:	20.2 KB
ID:	9975  
Reply With Quote
  #2  
Old 3/13/07, 6:53 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recepticles on Ceiling??

Popular in craft rooms and workshops. Drill press in middle of floor, ironing board in middle of room, etc.
Reply With Quote
  #3  
Old 3/13/07, 6:53 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recepticles on Ceiling??

They're fine. Nothing wrong with them.
Reply With Quote
  #4  
Old 3/14/07, 9:26 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Recepticles on Ceiling??

Yeppers.....Just put one in yesterday....

Just remembers they do not meet the " Spacing " requirement needed for a normal room layout...but they are perfectly fine and used many times as Marc said for dedicated needs.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #5  
Old 3/14/07, 10:18 AM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: Recepticles on Ceiling??

Not that it applies here....but remembering back to my commercial/industrial days isn't a ceiling mounted plug required to be a twist-lock type and isn't there a restriction on the type and length of the whip (extension cord) to the object being powered and that it cannot have any intermediate connections?
Reply With Quote
  #6  
Old 3/14/07, 10:29 AM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Location: Florida panhandle
Posts: 4,759
Default Re: Recepticles on Ceiling??

One that immediately comes to mind is the receptacle for a garage door opener. Ive installed and also find ceiling mounted 230v receptacles in garages, workshops, etc.
Reply With Quote
  #7  
Old 3/14/07, 10:57 AM
Steven C. Waskewicz's Avatar
Steven C. Waskewicz Steven C. Waskewicz is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Colorado Springs, CO
Posts: 1,829
Default Re: Recepticles on Ceiling??

Doug beat me to my comment.
I have one just like that in my garage also, its for the door opener.



Steven Waskewicz
Rest Assured Inspection Services, LLC.
719-510-7703 mobile all the time
719-495-7166 Fax.
s_waskewicz@msn.com
HVAC Lic. #10722
EPA cert.544143239730

www.restassuredinspection.com
NACHIiid=NACHI06032370





Reply With Quote
  #8  
Old 3/14/07, 12:41 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 13,927
Default Re: Recepticles on Ceiling??

Greatest invention since sliced Bread love them.
Have them all over my Garage and work shop So handy.
No cord to trip over and if you do get caught they just pull out .
Roy Cooke



If I can answer any questions please send me email Roycooke@hotmail.com

On an inspection and need immediate help call my cell 613-827-2011
Reply With Quote
  #9  
Old 3/14/07, 4:28 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recepticles on Ceiling??

Switched ceiling and "high wall" mounted receptacles are common for "rope light" prewires. I have several in my house, a couple in 1900 boxes with an occupancy sensor in it. It makes good "walking around light" at night. There really aren't many places in the living areas or outside (other than bedrooms) that the light doesn't come on when you approach. In the long run that saves money because the light goes out when you leave.
Reply With Quote
  #10  
Old 3/14/07, 5:24 PM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,067
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recepticles on Ceiling??

Rope lights w/ motion sensors?

Hmm...genius.
Reply With Quote
  #11  
Old 3/14/07, 5:58 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,722
Default Re: Recepticles on Ceiling??

Ahh yes... and blue neon under the bed .
Reply With Quote
  #12  
Old 3/14/07, 10:11 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recepticles on Ceiling??

Tony, rope under the toe kicks and over the uppers makes a very good soft light for walking around at night. That is certainly all you need for nature's call or rehydrating afterwards.
Rope is only listed for cord and plug connerct so receptacles are required
Reply With Quote
  #13  
Old 3/14/07, 11:09 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Recepticles on Ceiling??

I have done a few over the cabinets for atmosphere lighting.....we do just that switch a receptacle above the cabinet and looks rather nice.

I like the Sensor deal Greg...I might try that for the kitchen since at night we are only in their for a glass of water or something...and I like techie things.

I did install them on a large 12,000 sq ft house with all glass front...because their was no place to put the switch to the foyer so I oc.sensored it and worked rather nice.

Amazing how we do so much for other people but then forget to use it on our own houses.....atleast I do anyway.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #14  
Old 3/15/07, 9:11 AM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,067
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recepticles on Ceiling??

So does the sensor plug into the receptacle and the rope plugs into the sensor? I like it.
Reply With Quote
  #15  
Old 3/15/07, 9:15 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Recepticles on Ceiling??

Tony,

They do have the sensors like that...most certainly. The ones I have used actually go on the switch box and act just like a switch.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Asbestos ceiling tiles scoslett Interior Inspections 30 10/20/07 3:30 PM
"Darkness" at joist in ceiling mlong Interior Inspections 5 8/21/07 12:19 PM
Garage ceiling & door header Al Barb Interior Inspections 7 3/27/07 1:07 PM
Vaulted Ceiling Insulation rcooke Canadian Inspectors 3 1/22/07 11:24 AM
Ceiling discoloration from joists? dtaylor General Inspection Discussion 4 8/3/06 1:27 AM


All times are GMT -4. The time now is 9:31 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts