Default Recessed Lighting in Garage Ceiling

Recessed Lighting in Garage Ceiling



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member

Last edited by jhagarty; 2/18/08 at 5:34 PM..
Reply With Quote
  #2  
Old 6/14/07, 8:29 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recessed Lighting in Garage Ceiling

There are fire rated recessed cans on the market (they look like a big drywall box), but I'd sorta doubt that's what you're dealing with. Might want to look into that a bit if those cans are a penetration in a rated assembly.
Reply With Quote
  #3  
Old 6/15/07, 12:44 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recessed Lighting in Garage Ceiling

Is there dwelling space above the garage? That would require a fire rated ceiling
Reply With Quote
  #4  
Old 6/15/07, 6:33 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recessed Lighting in Garage Ceiling

I agree.
From what I know, with no living space above, the fire rated ceiling needs only to be 8 feet(?) out from the dewlling partition.
Reply With Quote
  #5  
Old 6/15/07, 7:53 PM
Shawn Rowe's Avatar
Shawn Rowe Shawn Rowe is offline
Active Poster
 
Join Date: Aug 2003
Location: St. Augustine, FL
Posts: 260
Default Re: Recessed Lighting in Garage Ceiling

Here is a pic from today's inspection
Attached Thumbnails
recessed-lighting-garage-ceiling-picture-096-small-.jpg.jpg
Views:	145
Size:	73.3 KB
ID:	12353  



**************************************
Shawn Rowe, CMI
HomeFirst Inspection Services, LLC
- InfraRed Specialist (Level 1 & Building Science certified)
- Code Certified Residential Building Inspector
- Certified Master Inspector
-- Serving NE Florida, St. Johns, Duval, Flagler, Putnam counties --
Reply With Quote
  #6  
Old 6/15/07, 9:23 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recessed Lighting in Garage Ceiling

Interesting that those lighting penetrations are fire rated, but the hvac transition ducts are not. Either the electrician is wasting money, or the hvac people dropped the ball.

I also see the phone and cable running right next to the 120. Not a violation, but certainly poor practice. Current BICSI standards would require the phone and cable to be 12" away from line voltage conductors when running parallel, and 3" away when crossing at a perpendicular.

Last edited by Marc D. Shunk; 6/15/07 at 9:47 PM..
Reply With Quote
  #7  
Old 6/15/07, 9:58 PM
Shawn Rowe's Avatar
Shawn Rowe Shawn Rowe is offline
Active Poster
 
Join Date: Aug 2003
Location: St. Augustine, FL
Posts: 260
Default Re: Recessed Lighting in Garage Ceiling

I am actually surprised too but not for the same reasons you are. The photos are at the second floor attic (not above the garage) but there is a third story "tower" which now classifies the home as a 3-story. Ok, here is the surprise, the current local codes states that there needs to be a fire suppression system on anything over two floors (excluding a 2.5 floor mezzanine). Unless I have been misinformed, some how this home got through the requirements. Here is the catch, the builder is also the developer of this and other high priced communities. hhhmmmmmmmmm



**************************************
Shawn Rowe, CMI
HomeFirst Inspection Services, LLC
- InfraRed Specialist (Level 1 & Building Science certified)
- Code Certified Residential Building Inspector
- Certified Master Inspector
-- Serving NE Florida, St. Johns, Duval, Flagler, Putnam counties --
Reply With Quote
  #8  
Old 6/15/07, 10:32 PM
Joseph Hagarty's Avatar
Joseph Hagarty Joseph Hagarty is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 3,434
Default Re: Recessed Lighting in Garage Ceiling

Quote:
Originally Posted by Greg Fretwell
Is there dwelling space above the garage? That would require a fire rated ceiling
Master Bedroom Suite is located above this space.



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #9  
Old 6/17/07, 1:17 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Recessed Lighting in Garage Ceiling

ahhh.......didn't a previous QOD bring attention to those type of light bulbs being used in recess cans as being.....well....not a good thing.. as well.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 6/17/07, 1:28 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recessed Lighting in Garage Ceiling

Quote:
Originally Posted by pabernathy
ahhh.......didn't a previous QOD bring attention to those type of light bulbs being used in recess cans as being.....well....not a good thing.. as well.
I don't know, Paul. Most of the cans I've put in the last several years have some wattage of A-19 lamp as being permitted in the lamp list. They look dumb, but often they are permissible.
Reply With Quote
  #11  
Old 6/17/07, 1:33 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Recessed Lighting in Garage Ceiling

I have seen potential fires start from a 100 W lightbulb in a recess can, the design of most reflector bulbs for recess cans divert the heat enough to not be a problem....the can's I install clearly say the type of bulb that goes in them and normal incand. bulbs I don't believe are listed.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 6/17/07, 1:40 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recessed Lighting in Garage Ceiling

Quote:
Originally Posted by pabernathy
I have seen potential fires start from a 100 W lightbulb in a recess can, the design of most reflector bulbs for recess cans divert the heat enough to not be a problem....the can's I install clearly say the type of bulb that goes in them and normal incand. bulbs I don't believe are listed.
I'll have to get some pictures up then, maybe. Most every list I look at inside of the cans has an A19 lamp of some wattage or another listed. None of them I've ever seen will take a 100, naturally.

I know you prefer the SunStar cans, and they are only for R or BR lamps. They're an oddity.
Reply With Quote
  #13  
Old 6/17/07, 2:02 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recessed Lighting in Garage Ceiling

The most popular Halo cans are the H7 series, and they can take a regular lamp: http://www.cooperlighting.com/specfi...opdf/H7ICT.pdf

The most popular Progress cans are the P87 series, and they can take a regular lamp up to and including 100 watt. Just noticed that: http://www.progresslighting.com/pdfs/P87.pdf
http://www.progresslighting.com/pdfs/P8075.pdf

Just some stuff for starters.
Reply With Quote
  #14  
Old 6/17/07, 2:24 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Recessed Lighting in Garage Ceiling

Marc..as much a wattage issue as I have seen standard Incand. bulbs heat up so much around the edge of the can it discolors the ceiling from the heat...not enough to blow the thermal in some cases but enough to heat up the trim and edge sides.....causing discoloration on the sheetrock.

I dont always use Sunstar...just like the speedycans they have....installed about 130 on a large job just recently and all worked like a charm.



Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 6/17/07 at 2:40 AM..
Reply With Quote
  #15  
Old 6/17/07, 2:32 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Recessed Lighting in Garage Ceiling


• Socket can be used as a temporary work light
with ‘A’ lamp

I do notice the Halo do allow A-19 but in limited use on some models only.....as well as they restrict it to 60W bulbs...probably a wise thing.

My problem is when I see them with "A" type bulbs they are usually over 75 Watts.....and that bothers me as I notice progressive is not so OPEN about the use of an " A " type as Halo is....but again notice some models do not allow "A" type from the PDF you posted....so it really depends on the model......but overlamping is a huge concern with those bulbs which is why the higher wattage ones are R or BR style bulbs.









Paul W. Abernathy,CMI,CEI,CEPE
NEC® Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 6/17/07 at 2:39 AM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Garage ceiling & door header Al Barb Interior 7 3/27/07 1:07 PM
Vaulted Ceiling Insulation rcooke Canadian Inspectors 3 1/22/07 11:24 AM
Recessed lighting jfunderburk Electrical 4 11/24/06 10:47 PM
Attic fan in garage ceiling cowen Exterior 3 3/4/06 4:21 PM
Recessed lighting jfunderburk Electrical 5 2/2/06 9:27 AM


All times are GMT -4. The time now is 4:59 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts