The electric wiring is up against the box of a recessed light for an insulated ceiling. I don't like it but is it wrong?
|
|
#2
|
|||
|
|||
|
Please Note:
ccbrands1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
depends on whether it's rated for zero clearance to combustibles.
most fixtures that are will say so. |
|
#3
|
||||
|
||||
|
Check for a "IC" stamp or sticker.
tom |
|
#4
|
||||
|
||||
|
It looks okay to me.
|
|
#5
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
As long as it is an IC rated fixture, which is looks like to me, it is perfectly fine.
Why don't you "like it"? |
|
#6
|
||||
|
||||
|
I don't see an issue with the wiring.
|
|
#7
|
||||
|
||||
|
The wiring has to enter the box at some point, at at that point it would be touching the box, whether it's IC rated or not. No other way around it, as I see it. Right?
The IC rating has to do with insulation. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#8
|
||||
|
||||
|
IC is for Insulation only, has nothing to do with wiring.. You are correct
Did you pull back insulation on other fixtures? Timothy Hejnicki All-Specs Property Inspections (707) 428-3544 |
|
#9
|
|||
|
|||
|
I see not issues really with the wire running beside it. heck when you replace the insulation, tuck some between the wires and the can if overly concerned otherwise it seems fine from the image.
Paul W. Abernathy |
|
#10
|
||||
|
||||
|
Quote:
So if it's non-IC and covered, the internal wires and wires touching the metal components are at risk. IC protects to like 90C, and fiberglass melts at a much higher temp. tom Last edited by tdietrich1; 2/5/07 at 9:49 AM.. |
|
#11
|
||||
|
||||
|
OK maybe I didnt word that correctly.. As a home inspector id there is no IC sticker and it is covered, you have a problem.. Still has nothing to do with the wiring.
Timothy Hejnicki All-Specs Property Inspections (707) 428-3544 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Lights Flickering while appliances start-up and while running. | Jeff Nunz | Electrical Inspections | 15 | 11/27/07 4:04 PM |
| Fan type and recessed can lights | dmacy | Interior Inspections | 7 | 7/23/07 10:39 PM |
| Recessed Lighting in Garage Ceiling | jhagarty | Electrical Inspections | 18 | 6/18/07 1:24 PM |
| Lights & GFCI Outlets | thejnicki | Electrical Inspections | 14 | 2/28/07 3:48 PM |