Default Recommend changes, or call as deficient?

The home was built in 1997 within a small city.

The service comes into a 200 Amp Cutler H panel on exterior, and a 100 Amp breaker feeds the sub distribution panel in the storage area.

In the storage area sub, the conductors come into a 100-Amp breaker at the top of the panel with a 3-wire feed. The rest of the breakers are below, all 20 Amp.

Are there different requirements because the conductors feed the breaker, not the panel itself ?
Should I comment that 'by today's standards a 4-wire,' etc,,,,, would be needed' -- or call it as deficient and defer to electrician.

By my understanding, the sub should have a 4-wire feed, but what year did this start?
Not sure which year of the NEC was in effect when home was built, mid 80's by guess

Harry HomeOwner is the Seller and did all the original wiring when the home was built,,,, I need to be able to explain what I state.

sheeeesh
Attached Thumbnails
recommend-changes-call-deficient-101_7253.jpg   recommend-changes-call-deficient-101_7234.jpg   recommend-changes-call-deficient-101_7229.jpg  
Reply With Quote
Find an InterNACHI certified New York Home Inspector (and anywhere else in North America)
  #2  
Old 8/9/09, 5:12 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Recommend changes, or call as deficient?

Ground and neutral should be separate at the sub-panel.
I recommend a Licensed Electrician examine and evaluate if correction should be made.
Reply With Quote
  #3  
Old 8/9/09, 8:12 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 2,037
Default Re: Recommend changes, or call as deficient?

Improper sub-panel. Should have 4 conductors with a floating neutral (grounded conductor) and should be separate from the EGCs.

In TX that would be a defect.



Chuck Evans (TREC #7657)
Level III Infraspection Institute Certified Infrared Thermographer (#8402)
HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook
Houston Thermal Inspections & Infrared Imaging Find us on Facebook
Houston Home Inspector

Houston, TX
Reply With Quote
  #4  
Old 8/9/09, 9:18 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Recommend changes, or call as deficient?

Even by earlier standards, it's wrong Linda. A neutral has to be run with the feeders, regardless of the code cycle being followed.

Earlier installations would have three conductors (H+H+N) and use the conduit as the ground.

What I see in your pictures is H+H+G, so all 120V circuits must use the ground as the return path.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 8/9/09, 9:35 PM
lfoster's Avatar
lfoster lfoster is offline
Active Poster
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 489
Please Note: lfoster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recommend changes, or call as deficient?

Thank you, guys. I appreciate it. !!
Have a great 'what's left of Sunday !'
Reply With Quote
  #6  
Old 8/9/09, 10:59 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Recommend changes, or call as deficient?

Maybe Paul A. can join in and confirm that all that is needed is a neutral cable (insulated) added in there also with necessary neut/gnd bus configuration done. Lots cheaper than running a new 4-wire cable.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #7  
Old 8/9/09, 11:07 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Recommend changes, or call as deficient?

Depending on the distance, it's usually easier to pull all new conductors, rather than trying to pull a single through a filled conduit. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 8/9/09, 11:21 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Recommend changes, or call as deficient?

We have very little conduit here in residential.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #9  
Old 8/10/09, 8:18 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Recommend changes, or call as deficient?

Quote:
Originally Posted by bking View Post
Maybe Paul A. can join in and confirm that all that is needed is a neutral cable (insulated) added in there also with necessary neut/gnd bus configuration done. Lots cheaper than running a new 4-wire cable.
Lol....I just saw this. What am I joining in about...Give me the short version and i will reply to it...lol



Paul W. Abernathy
Reply With Quote
  #10  
Old 8/10/09, 8:25 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Recommend changes, or call as deficient?

Quote:
Originally Posted by lfoster View Post
The home was built in 1997 within a small city.

The service comes into a 200 Amp Cutler H panel on exterior, and a 100 Amp breaker feeds the sub distribution panel in the storage area.

In the storage area sub, the conductors come into a 100-Amp breaker at the top of the panel with a 3-wire feed. The rest of the breakers are below, all 20 Amp.

Are there different requirements because the conductors feed the breaker, not the panel itself ?
Should I comment that 'by today's standards a 4-wire,' etc,,,,, would be needed' -- or call it as deficient and defer to electrician.

By my understanding, the sub should have a 4-wire feed, but what year did this start?
Not sure which year of the NEC was in effect when home was built, mid 80's by guess

Harry HomeOwner is the Seller and did all the original wiring when the home was built,,,, I need to be able to explain what I state.

sheeeesh
Hello Linda,

Basically if the service panel with the service disconnect is outside in this example and the panel which is a remote distribution panel 'sub-panel" is located in the same structure then indeed a 4 conductor cable would be required. This dates back well before 1980 with regards to remote panels within the same structure . Yes, I would instruct them to wire it properly as you many case to neutral connections where they should not be which creates objectionable currents and poor circuit circulation...hey I like that...Circuit Circulation...lol...

Don't get the allowance in the pre-2008 NEC where you can have a 3 wire feeder to a detached structure with this example. So yes, it needs to be a 4 wire setup.

Also dont be afraid to call out the non-reidentified white conductors on breakers and non-identified grounded conductor in the main panel as well. Also appears to be quite a few 408.41 violations....could be problematic if any multiwire circuits are present as well. Also is that panel listed for the tandom breaker within the enclosure......those kinda things.



Paul W. Abernathy

Last edited by pabernathy; 8/10/09 at 8:30 PM..
Reply With Quote
  #11  
Old 8/10/09, 9:04 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Recommend changes, or call as deficient?

Quote:
Originally Posted by pabernathy View Post
Lol....I just saw this. What am I joining in about...Give me the short version and i will reply to it...lol

ok, lol.... you want the short version from us lol... but we get long versions from you lol......


Here it is short and simple:

Is it ok to run a new insulated neutral conductor (properly sized) to a sub panel to in effect "upgrade an old 3-wire cable".

Has H-H-G
and will be upgraded to H-H-N-G with the N being a new seperate run.

This is assuming that the necessary configurations are also done for the neutral and ground circuits on the busses.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #12  
Old 8/11/09, 2:35 PM
Tom Horne Tom Horne is offline
New User
 
Join Date: Aug 2009
Posts: 12
Please Note: Tom Horne is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recommend changes, or call as deficient?

Linda
I am an electrician by craft for over forty years now and I can assure you that running that neutral as a bare conductor has never been allowed on the load side of the Service Disconnecting Means except for certain specific circuits and a feeder was never one of those circuits. So the bare neutral should come out and an insulated neutral with an appropriately sized Equipment Grounding Conductor (EGC) should be pulled in if the conduit is large enough to have 2.5 times the total internal cross sectional area of the four conductors. That would keep the conduit fill to the allowed forty percent fill for three or more conductors.
--
Tom Horne
Reply With Quote
  #13  
Old 8/11/09, 11:20 PM
lfoster's Avatar
lfoster lfoster is offline
Active Poster
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 489
Please Note: lfoster is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Recommend changes, or call as deficient?

I had called for the panel:
- to have a 4-wire feed, not 3
- multiple grounded neutrals under one screw terminal
- remove the bonding strap
- rework the bus bars for grounds only, grounded neut only

and, that is a CTL panel and should not have the tandem/wafer breaker.

Also, at the main panel we didn't find a ground wire to a ground rod. No ground rod found, in fact. There was underground service to the meter, but nothing found to the soil level for the SE panel.

It had several issues

Gives me headaches late at night !!

Appreciate all the help !

And,,,, if a new wire is added to the others, it should be in the original conduit / bundle - correct? Can't just stretch between the two panels however it's handy to install ?

Reply With Quote
Find an InterNACHI certified New York Home Inspector (and anywhere else in North America)
  #14  
Old 8/11/09, 11:38 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Recommend changes, or call as deficient?

Quote:
Originally Posted by lfoster View Post

And,,,, if a new wire is added to the others, it should be in the original conduit / bundle - correct? Can't just stretch between the two panels however it's handy to install ?
That is correct. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #15  
Old 8/15/09, 12:34 AM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: Recommend changes, or call as deficient?

Linda -

Probably the MOST important issue here is: YOU are the CURSORY screening process (the school nurse) that determined the football player is having a heart attack AND sent him to the ER at the hospital to see the CARDIOLOGIST for service and repair.

You point out some of the SYMPTOMS, but you DON'T tell the Heart Specialist what to do OR how to do it, OR you can be in DEEP **** if it ain't right OR your REPAIR screws something up.

You've got several issues in NEED of REPAIR. Therefore;

"There were electrical conditions present in the panel(s) that in my opinion indicate there has been a liberal approach to proper installation practices, SUCH AS: xxxxxxxxxxxx; yyyyyyyyyyyyy; zzzzzzzz.

This type of installation has the potential to become problematic in the future. I recommend having a licensed and competent electrician read ALL of the inspection report; evaluate the buildings FULL electrical system and its conditions; then service, repair or modify any unreliable conditions or deficiency's in a safe and proper manner prior to closing".


Too many of our guys try to BE the FINAL WORD, and they're not.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cell Phone Do not call #'s bjones5 Canadian Inspectors 10 1/31/09 12:17 PM


All times are GMT -4. The time now is 9:24 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts