Are the red & black connection at the breaker an acceptable electrical connection? This would be the 4th one from the bottom.
And for the sake of me not remebering what is the problem when the nuetral & ground are attached at the same screw on the bar? Does it really make a difference seperating the nuetral & ground on seperte screws? Last edited by dmacy; 8/3/07 at 5:16 PM.. |
|
#2
|
||||
|
||||
|
From what I understand in your question, so I may be wrong.
(1)Red and/or black wire to a circuit breaker is ok. Double-pole breakers are connected with both a red and black wire; single-pole breakers (in most installations) are connected with just the black wire. Red and black both represent a hot leg. Usually you see them connected to a double 220v breaker meaning that the breaker actually connects to both bus bars in the panel. *Looks like you have a double tap breaker in the first picture also. (2) The doubling up of neutrals (white wires) on a terminal lug (buss) bar has been a violation going back to the Standard 67 of the UL and has been required by many panel manufacturers. Correction is recommended for electrical safety. Peter Doane Realty Check Inspection Service NACHI ID# 05120681
|
|
#3
|
||||
|
||||
|
If you're referring to the double-tap at the breaker terminal, no, it's not okay.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#4
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#5
|
|||
|
|||
|
Our AHJ will not pass that breaker with a double tap.
Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties. Abraham Lincoln www.qualityhomeinspectionsfl.com |
|
#6
|
||||
|
||||
|
I need to learn to spell.
Balck Thanks for the response |
|
#7
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#8
|
|||
|
|||
|
Please Note:
rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Up in Ontario double taps are not okay unless its a Square D breaker, last time I checked with our Electrical Safety Authority that was the rule, they are the only approved breaker for double taps. But having said that the Electrical Authority inspectors have routinely accepted double tapped Stab-loks where a door bell transformer and 14 ga circuit are used. Contrary to their own rules fwiw.
|
|
#9
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#10
|
|||
|
|||
|
Please Note:
rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Speedy
I am only going by what I have been told by our ESA inspector. I realize its possible to put two wires of the same guage under the terminal screw of other breakers but ESA has stated its the only approved breaker (Sq D) they will accept for double lugging fwiw. It is also uncommon at least in my area to see anything but Stab-lok and the occassional Square D panel in newer housing. |
|
#11
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#12
|
|||
|
|||
|
Please Note:
rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Marc,
I had it in writing from the ESA so I can only base my comments on what they wrote in an email. Aren't all breakers certified by CSA and CUL? Does it say in the Ontario code double taps are permitted or which breakers are certified for double tapping? |
|
#13
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Would you mind CC'ing that email here: |
|
#14
|
|||
|
|||
|
Please Note:
rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
http://www.nachi.org/forum/archive/i...hp/t-2527.html
3/29/06, 5:52 PM Quote:
|
|
#15
|
||||
|
||||
|
Quote:
The local AHJs enforce local codes (which are not always in accordance with the national codes (which, in themselves, have no force of law). Not to start an argument, but we have to remember (not being local code enforcers) that the local AHJ code requiremements are, usually, pretty crazy. They are not (usually) up to date, are more a political document that a technical one and are 'enforced' by guys who only spend about 10 - 15 minutes on site. (Not to slam them, they are only allowed that time, being overworked as they are). This is what home inspectors usually run into. Being in the middle of the local guys, the national codes and the local contractors and realtors. We are confused, but we have to try to explain this messed up system to the client. What a job. Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| AC Unit Maximum Breaker | jchamp | Inspecting HVAC Systems | 17 | 11/28/10 1:10 AM |
| Electrical Guru Question? Breaker lock outs | pdoane | Electrical Inspections | 4 | 9/7/07 2:05 PM |
| Double Tapped Breaker | tjohnson3 | Electrical Inspections | 8 | 4/20/07 9:04 AM |