This panel is in a workshop next to house and is fed by 3 conductor feeder from a 40amp breaker in main panel. Is this a amateur electrician home owners attempt at a subpanel (obviously done totally wrong) or can this be a Remote distribution panel done by an electrician? This is my first picture upload so hopefully it works.
Attached Thumbnails
remote-distribution-panel-subpanel-conway-powell-038.jpg  
Reply With Quote
  #2  
Old 3/18/07, 11:49 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Remote distribution panel or subpanel?

Is the workshop detached?
Reply With Quote
  #3  
Old 3/18/07, 12:05 PM
rwilcox rwilcox is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Blairsville, GA
Posts: 9
Default Re: Remote distribution panel or subpanel?

Yes, the workshop is detached.
Reply With Quote
  #4  
Old 3/18/07, 12:54 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Remote distribution panel or subpanel?

It's a "panel" or "panelboard." Call it an electrical panel, load side panel, distribution panel, equipment panel, remote panel - whatever. The point is, it is not "service" equipment, and that's all that really matters.

I know subpanel is a fairly common term, but it is not recognized by the NEC, and if you read through the electrical forum, you'll see where it leads to a large amount of confusion, especially with newer inspectors.

There is "service" equipment and then there is "other" equipment.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 3/18/07, 12:56 PM
David P. Valley's Avatar
David P. Valley David P. Valley is online now
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,024
Default Re: Remote distribution panel or subpanel?

What's up with the grounds?
Reply With Quote
  #6  
Old 3/18/07, 1:02 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Remote distribution panel or subpanel?

Quote:
Originally Posted by dvalley
What's up with the grounds?
Are you referring to the fact that they're attached to the neutral bus?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #7  
Old 3/18/07, 1:13 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Remote distribution panel or subpanel?

If this is a deteched structure, and there are no other metallic paths between the house and the detached structure (phone lines, metal water lines, etc.), then it is permissible to feed that panel with 3-wire.
Reply With Quote
  #8  
Old 3/18/07, 1:33 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Remote distribution panel or subpanel?

Quote:
Originally Posted by Marc D. Shunk
If this is a deteched structure, and there are no other metallic paths between the house and the detached structure (phone lines, metal water lines, etc.), then it is permissible to feed that panel with 3-wire.
But the grounding bus would still be required to be bonded to the enclosure.

Also, with strict interpretation of the code, the disconnect for that panel would be required to disconnect all three conductors (H-H-N) in a 3-wire feed.

It's easier (acting as a home inspector) to simply defer a 3-wire feed to a load side panel, and let the sparky make the call.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #9  
Old 3/18/07, 1:38 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Remote distribution panel or subpanel?

Quote:
Originally Posted by jpope
But ...

Also, ....
I was only addressing one matter, which was the 3-wire feeder. In the past, when I've addressed the entire photograph, I get blasted for providing too much information. Now, I only address one portion, and I get "but... also...". I have no idea which set of rules to follow.
Reply With Quote
  #10  
Old 3/18/07, 1:39 PM
rwilcox rwilcox is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Blairsville, GA
Posts: 9
Default Re: Remote distribution panel or subpanel?

OK Jeff I think I understand. Let me try to ask this question another way. Is there anything wrong with this panel being supplied by a 3 wire conductor from another panel? I think the neutral ground conductors and the grounding conductors should be isolated in this workshop panel and a fourth conductor (a dedicated grounding conductor) should have been ran to this workshop panel from the main panel and I think this workshop panel should also have its on grounded electrode. Help me out me, am I correct? I hope I my terminology is correct.
Reply With Quote
  #11  
Old 3/18/07, 1:41 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Remote distribution panel or subpanel?

Quote:
Originally Posted by rwilcox
Is there anything wrong with this panel being supplied by a 3 wire conductor from another panel? .
I dont' care if you're addressing Jeff directly or not. If it's a detached structure with no other metallic paths, 3-wire is legal.
Reply With Quote
  #12  
Old 3/18/07, 1:49 PM
rwilcox rwilcox is offline
InterNACHI Member
 
Join Date: Jul 2005
Location: Blairsville, GA
Posts: 9
Default Re: Remote distribution panel or subpanel?

Take a chill pill Marc, This is an open discussion to all knowageble inspectors. Thank you for your opinion.
Reply With Quote
  #13  
Old 3/18/07, 1:51 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Remote distribution panel or subpanel?

Jeff, why would you need to open the neutral on a feeder disconnect?
Reply With Quote
  #14  
Old 3/18/07, 1:55 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Remote distribution panel or subpanel?

It can be difficult to verify "no other metallic path." That's why I say defer a 3-wire feed.

In your picture, it's wrong, no matter what. If it's a proper 3-wire feed, that G/N bus needs to be bonded to the enclosure. Also, it does not appear that there is a grounding electrode (rod/pipe) for that panel, which would be required in either case.

The disconnecting means for that panel (in a 3-wire feed) should disconnect all three conductors - essentially, a three-pole breaker or switch.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net

Last edited by jpope; 3/18/07 at 1:59 PM..
Reply With Quote
  #15  
Old 3/18/07, 1:57 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: Remote distribution panel or subpanel?

Quote:
Originally Posted by Greg Fretwell
Jeff, why would you need to open the neutral on a feeder disconnect?
That's how I interpret the code section that allows for a 3-wire feed. I don't have it in front of me (I'm getting ready to start an inspection), but I'll post it later if nobody else does.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Subpanel wired as main panel. jlybolt Electrical 15 5/23/07 5:10 PM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Distribution panel GEC bsmith Electrical 11 9/13/06 4:26 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 7:08 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts