This panel is in a workshop next to house and is fed by 3 conductor feeder from a 40amp breaker in main panel. Is this a amateur electrician home owners attempt at a subpanel (obviously done totally wrong) or can this be a Remote distribution panel done by an electrician? This is my first picture upload so hopefully it works.
|
|
#2
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Is the workshop detached?
|
|
#3
|
|||
|
|||
|
Yes, the workshop is detached.
|
|
#4
|
||||
|
||||
|
It's a "panel" or "panelboard." Call it an electrical panel, load side panel, distribution panel, equipment panel, remote panel - whatever. The point is, it is not "service" equipment, and that's all that really matters.
I know subpanel is a fairly common term, but it is not recognized by the NEC, and if you read through the electrical forum, you'll see where it leads to a large amount of confusion, especially with newer inspectors. There is "service" equipment and then there is "other" equipment. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#5
|
||||
|
||||
|
What's up with the grounds?
|
|
#6
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#7
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
If this is a deteched structure, and there are no other metallic paths between the house and the detached structure (phone lines, metal water lines, etc.), then it is permissible to feed that panel with 3-wire.
|
|
#8
|
||||
|
||||
|
Quote:
Also, with strict interpretation of the code, the disconnect for that panel would be required to disconnect all three conductors (H-H-N) in a 3-wire feed. It's easier (acting as a home inspector) to simply defer a 3-wire feed to a load side panel, and let the sparky make the call. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#9
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#10
|
|||
|
|||
|
OK Jeff I think I understand. Let me try to ask this question another way. Is there anything wrong with this panel being supplied by a 3 wire conductor from another panel? I think the neutral ground conductors and the grounding conductors should be isolated in this workshop panel and a fourth conductor (a dedicated grounding conductor) should have been ran to this workshop panel from the main panel and I think this workshop panel should also have its on grounded electrode. Help me out me, am I correct? I hope I my terminology is correct.
|
|
#11
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#12
|
|||
|
|||
|
Take a chill pill Marc, This is an open discussion to all knowageble inspectors. Thank you for your opinion.
|
|
#13
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Jeff, why would you need to open the neutral on a feeder disconnect?
|
|
#14
|
||||
|
||||
|
It can be difficult to verify "no other metallic path." That's why I say defer a 3-wire feed.
In your picture, it's wrong, no matter what. If it's a proper 3-wire feed, that G/N bus needs to be bonded to the enclosure. Also, it does not appear that there is a grounding electrode (rod/pipe) for that panel, which would be required in either case. The disconnecting means for that panel (in a 3-wire feed) should disconnect all three conductors - essentially, a three-pole breaker or switch. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net Last edited by jpope; 3/18/07 at 1:59 PM.. |
|
#15
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ℠ Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical | 44 | 4/18/08 12:43 AM |
| Subpanel wired as main panel. | jlybolt | Electrical | 15 | 5/23/07 5:10 PM |
| Panel Inspection Safety | roconnor | Electrical | 10 | 9/24/06 10:02 PM |
| Distribution panel GEC | bsmith | Electrical | 11 | 9/13/06 4:26 PM |
| Bad electrical problem | Pest Guy | Electrical | 4 | 1/20/06 10:26 PM |