#31
|
||||
|
||||
|
Quote:
I'm about to start my final inspection for the day. I'll check back in later. . . IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net Last edited by jpope; 3/18/07 at 7:47 PM.. |
|
#32
|
||||
|
||||
|
Quote:
As for Marc, I think the dude is on the Marc! (pun intended). tom |
|
#33
|
||||
|
||||
|
250.6 Objectionable Current over Grounding Conductors. (A) Arrangement to Prevent Objectionable Current. The grounding of electrical systems, circuit conductors, surge arresters, and conductive non –current-carrying materials and equipment shall be installed and arranged in a manner that will prevent objectionable current over the grounding conductors or grounding paths. This would make it a compelling argument to NOT tie the Grounded and Grounding conductors together in a 4 wire setup to a detached garage so to speak....the 250.32(B)(2) section has been debated for many years.....some think it will disappear in future cycles.... Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#34
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
I wouldn't connect the feeder ECG to the bar either, and havn't said that's proper. It's okay that they ran 4-wire and only have the panel connected as 3-wire, but the ECG should remain unconnected. It is a parallel path for the neutral. The panel has plenty of issues, but being connected as a 3-wire panel is not among them.
|
|
#35
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Jeff that is telling you to bond the 3 wire feeder grounded conductor to the disconnect enclosure, where you also connect the ground electrode conductor. This is simply treating the second building like the first where you had a 3 wire service drop.
If there is a 4th wire in the feeder you WILL NOT reground the neutral in the second building. I doubt an inspector would simply let you tiee it back if he saw it was avaiable. It is true 250.32(B)(2) is going to be deleted in the 2008 assuming there is no last minute stay of execution. This is the same logic that made 250.50 go away (3 wire to dryers/ranges). The war is over, there is no reason to save copper anymore. Cost is no object if you can squeeze out another .0001% of safety ... or so it seems. |
|
#36
|
||||
|
||||
|
I understand the practical application of a 3-wire feed, and I know that installers/technicians say that it's proper, but you will have a difficult time convincing me that the code implies anything other than what it says.
Quote:
I am not going to try and convince anyone that my interpretation is absolute, and I'm not going to try and verify "no other metallic pathway." I'm going to state that the three wire feed should be verified as compliant by a qualified electrician (or something to that affect). IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#37
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
You still have 225.38 that says this can be (dis)connected via a busbar.
This is the example in the handbook, see a disconnect on the neutral? Last edited by Greg Fretwell; 3/19/07 at 2:18 AM.. |
|
#38
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
250.32 (B)(2) Grounded Conductor. Where (1) an equipment grounding conductor is not run with the supply to the building or structure, (2) there are no continuous metallic paths bonded to the grounding system in both buildings or structures involved, and (3) ground-fault protection of equipment has not been installed on the common ac service, the grounded circuit conductor run with the supply to the building or structure shall be connected to the building or structure disconnecting means and to the grounding electrode(s) and shall be used for grounding or bonding of equipment, structures, or frames required to be grounded or bonded.
The intent is to connect the grounded conductor to the disconnect for grounding and bonding of the equipment, just like it is required at other equipment. The last part of the section makes this clear. |
|
#39
|
||||
|
||||
|
Brian,
Yep...as long as all the FACTORS in that article are met. Just want guys to be clear that IF you have a 4 wire setup to a detached garage....you MUST have the Grounded and Grounding separated as you would normally see in a typical "remote" distirbution setup in a dwelling......lets not confuse the two as 250.32(B)(2) is very specifiic in nature. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#40
|
||||
|
||||
|
It will certainly be easier when/if this section of the code "goes away." I like the thought that the 4-wire feed will be the new mandate, but until then, I still see this as a switched or fused neutral. Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#41
|
||||
|
||||
|
Jeff,
I agree 100% with the premise.....I would prefer to see them as a 4 wire setup all the time.....IN fact MANY agree with that as well as their are simply too many " What If's " involved with 250.32(B)(2) but alas the NEC panel does not agree......so it will still be done and technically safe if done correctly. I am confused however in your use of the term Switched or Fused Neutral in either setup. The neutral ( grounded ) conductor is solidly connected in either system setup......the only time we get into switching a neutral would be in a SDS setup....in which it defines THAT type of setup....so I am confused ( not argueing my friend....I think you know me now )...just trying to learn myself why you would consider it such. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#42
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Someone better explain your view to NFPA. They get it "wrong" (by your interpretation) in the handbook. Basically you are saying it is illegal to use a panelboard main breaker as the disconnect in a second building since that will not interrupt the neutral.
|
|
#43
|
||||
|
||||
|
I read "disconnecting means" as a switch or OCPD, not a lug or bus terminal that is screwed down.
The section clearly (ok, maybe not so clearly IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net Last edited by jpope; 3/19/07 at 1:39 PM.. |
|
#44
|
||||
|
||||
|
As greg stated......it is simply not a case where you want to even think about the "grounded" conductor being switched or fused...simply not the case when it comes to a detached building as in this question.
Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#45
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
BTW if the hot rumor is true you will not get any help from 2008 code in Florida. There is a buzz that the 2008 will be skipped and they are going to stay with 2005 until the 11 code comes out. They plan to pick up anything they like with the "glitch" amendments to the FBC (as they did with the required bonding of steel framing)
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 8:28 PM |
| Subpanel wired as main panel. | jlybolt | Electrical Inspections | 15 | 5/23/07 5:10 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 10:02 PM |
| Distribution panel GEC | bsmith | Electrical Inspections | 11 | 9/13/06 4:26 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 10:26 PM |