Default Re: Remote distribution panel or subpanel?

Ahh...I see what you are saying....you are taking the term Disconnecting Means as literally the OCPD itself.

Disconnecting Means.
A device, or group of devices, or
other means by which the conductors of a circuit can be
disconnected from their source of supply.

Ie: A location of the source of disconnection..........not the actual OCPD located within...

Circuit Breaker.
A device designed to open and close a
circuit by nonautomatic means and to open the circuit automatically
on a predetermined overcurrent without damage
to itself when properly applied within its rating.




Paul W. Abernathy
Reply With Quote
  #47  
Old 3/19/07, 12:21 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Remote distribution panel or subpanel?

That's how I read it. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #48  
Old 3/19/07, 12:23 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Remote distribution panel or subpanel?

Quote:
Originally Posted by Greg Fretwell
Someone better explain your view to NFPA. They get it "wrong" (by your interpretation) in the handbook. Basically you are saying it is illegal to use a panelboard main breaker as the disconnect in a second building since that will not interrupt the neutral.
In the 3-wire feed, yes. That's how I read it.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #49  
Old 3/19/07, 12:38 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Remote distribution panel or subpanel?

how exactly would this take place Jeff.....none of the enclosures sold today for this purpose ( other than lets say a transfer switch for a SDS system ) would be designed to actually SWITCH the neutral ( grounded ) conductor in any way.

easy to read it literally...like in this statement as well...


(5) Load-Side Grounding Connections.
A grounding
connection shall not be made to any grounded circuit conductor
on the load side of the service disconnecting means
except as otherwise permitted in this article.


Basically they are refering to the Disconnection means as the enclosure as a whole......so basically in the 250.32(B)(2)...when they say disconnection means...they are refering to the whole enclosure itself that makes up the disconnection means for that setup.....not JUST the OCPD itself.

Also this would limit that from happening as well....
240.22 Grounded Conductor.
No overcurrent device shall
be connected in series with any conductor that is intentionally
grounded, unless one of the following two conditions is
met:
(1) The overcurrent device opens all conductors of the circuit,
including the grounded conductor, and is designed
so that no pole can operate independently.
(2) Where required by 430.36 or 430.37 for motor overload
protection.

so in allowance (1) above....don't believe I have ever seen a 120/240 enclosure with a panelboard and OCPD that would do this.......so it boils down to what is the term disconnection means in that statement.....I believe it is the actual enclosure itself as a whole........does that clear it up any Jeff?





Paul W. Abernathy

Last edited by pabernathy; 3/19/07 at 12:49 PM..
Reply With Quote
  #50  
Old 3/19/07, 12:54 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Remote distribution panel or subpanel?

I won't let you (Paul) and Greg pound me into submission

I don't know "how" this would be done or "why" it's written as it is. That's why I will defer most 3-wire feeds I come across (uh-oh, I said most).

I'm off to the races again this morning. I'll be back this evening. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 3/19/07 at 12:59 PM..
Reply With Quote
  #51  
Old 3/19/07, 1:33 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Remote distribution panel or subpanel?

Quote:
Originally Posted by jpope
I won't let you (Paul) and Greg pound me into submission

I don't know "how" this would be done or "why" it's written as it is. That's why I will defer most 3-wire feeds I come across (uh-oh, I said most).

I'm off to the races again this morning. I'll be back this evening. . .
lol...I would never think of it my friend......but in light of your thinking that the "grounded" conductor should be switched on a 3-wire setup...lol...I would suggest you continue to defer... ....sorry I could not resist....



Paul W. Abernathy
Reply With Quote
  #52  
Old 3/19/07, 3:36 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Remote distribution panel or subpanel?

90.1(C) Intention. This Code is not intended as a design specification or an instruction manual for untrained persons.
Reply With Quote
  #53  
Old 3/19/07, 4:05 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Remote distribution panel or subpanel?

lol.......nice....



Paul W. Abernathy
Reply With Quote
  #54  
Old 3/19/07, 6:39 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Remote distribution panel or subpanel?

Way back in the olden days (circa 1988 or so) a group of electrical professionals were hanging out on the Prodigy BBs. The homeowners accused us of being a "secret society" with an arcane dogma (the NEC). The name stuck and a number familiar names here got their "T" shirts with the Secret Society logo. A few of them were me (AKA DP), Joe Tedesco (AKA NecMeister) and our mutual friend Ryan Jackson (AKA Roper) who wrote the proposal that will kill 250.32(B)(2).
Some of the others are regular contributors on alt.electrical.engineering and the ECN groups but they try to stay a bit more anonymous.
Reply With Quote
  #55  
Old 3/19/07, 6:58 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Remote distribution panel or subpanel?

Quote:
Originally Posted by Greg Fretwell
90.1(C) Intention. This Code is not intended as a design specification or an instruction manual for untrained persons.
Good point Greg. I ain't no sparky



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #56  
Old 3/19/07, 10:03 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Remote distribution panel or subpanel?

Maybe this will help Jeff. Bonding the grounded conductor to the disconnect enclosure serves a very important function, as we all know. What function could a switched or fused neutral possibly serve in the case of a remote building on the same system?

Please don't take this wrong, but many parts of the code are much easier to understand when a person has been in the trade for many years and understands electrical theory enough to understand the reasons behind a code requirement. Sadly there are still many "electricians" out there who do not understand basic theory.


I was not allowed to take my NEC classes until I had completed my theory classes. I was not happy with that, but now I see the reason for it. Of course I will be the first to admit that I don't know it all. But one thing I do know, you are wrong in your interpertation of 250-32(B)(2)

Last edited by brian winkle; 3/19/07 at 10:22 PM..
Reply With Quote
  #57  
Old 3/19/07, 10:12 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Remote distribution panel or subpanel?

Don't feel bad about it. The cryptic language of the NEC can get fistfights started in inspector meetings. 250 is always good for a fight and this is the new and improved, rewritten 250. In 99 they scrapped the whole article and started over.
If you really want to be confused look at 250.24 in the 96 code where this used to be covered. The intent never changed but the language is completely different.
Reply With Quote
  #58  
Old 1/11/08, 6:49 PM
Ryan C. Jackson Ryan C. Jackson is offline
New User
 
Join Date: Jan 2008
Posts: 9
Please Note: Ryan C. Jackson is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Remote distribution panel or subpanel?

Quote:
Originally Posted by Greg Fretwell
... A few of them were me (AKA DP), Joe Tedesco (AKA NecMeister) and our mutual friend Ryan Jackson (AKA Roper) who wrote the proposal that will kill 250.32(B)(2)...
Indeed, I did write and substantiate that proposal for Mike Holt, as I work for Mike on a part time consulting basis. I don't where "Roper" came from though...
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Subpanel wired as main panel. jlybolt Electrical Inspections 15 5/23/07 4:10 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Distribution panel GEC bsmith Electrical Inspections 11 9/13/06 3:26 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM