#46
|
|||
|
|||
|
Ahh...I see what you are saying....you are taking the term Disconnecting Means as literally the OCPD itself.
Disconnecting Means. A device, or group of devices, or other means by which the conductors of a circuit can be disconnected from their source of supply. Ie: A location of the source of disconnection..........not the actual OCPD located within... Circuit Breaker. A device designed to open and close a circuit by nonautomatic means and to open the circuit automatically on a predetermined overcurrent without damage to itself when properly applied within its rating. Paul W. Abernathy |
|
#47
|
||||
|
||||
|
That's how I read it. . .
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#48
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#49
|
|||
|
|||
|
how exactly would this take place Jeff.....none of the enclosures sold today for this purpose ( other than lets say a transfer switch for a SDS system ) would be designed to actually SWITCH the neutral ( grounded ) conductor in any way.
easy to read it literally...like in this statement as well... (5) Load-Side Grounding Connections. A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article. Basically they are refering to the Disconnection means as the enclosure as a whole......so basically in the 250.32(B)(2)...when they say disconnection means...they are refering to the whole enclosure itself that makes up the disconnection means for that setup.....not JUST the OCPD itself. Also this would limit that from happening as well.... 240.22 Grounded Conductor. No overcurrent device shall be connected in series with any conductor that is intentionally grounded, unless one of the following two conditions is met: (1) The overcurrent device opens all conductors of the circuit, including the grounded conductor, and is designed so that no pole can operate independently. (2) Where required by 430.36 or 430.37 for motor overload protection. so in allowance (1) above....don't believe I have ever seen a 120/240 enclosure with a panelboard and OCPD that would do this.......so it boils down to what is the term disconnection means in that statement.....I believe it is the actual enclosure itself as a whole........does that clear it up any Jeff? Paul W. Abernathy Last edited by pabernathy; 3/19/07 at 12:49 PM.. |
|
#50
|
||||
|
||||
|
I won't let you (Paul) and Greg pound me into submission
I don't know "how" this would be done or "why" it's written as it is. That's why I will defer most 3-wire feeds I come across (uh-oh, I said most). I'm off to the races again this morning. I'll be back this evening. . . IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net Last edited by jpope; 3/19/07 at 12:59 PM.. |
|
#51
|
|||
|
|||
|
Quote:
Paul W. Abernathy |
|
#52
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
90.1(C) Intention. This Code is not intended as a design specification or an instruction manual for untrained persons.
|
|
#53
|
|||
|
|||
|
lol.......nice....
Paul W. Abernathy |
|
#54
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Way back in the olden days (circa 1988 or so) a group of electrical professionals were hanging out on the Prodigy BBs. The homeowners accused us of being a "secret society" with an arcane dogma (the NEC). The name stuck and a number familiar names here got their "T" shirts with the Secret Society logo. A few of them were me (AKA DP), Joe Tedesco (AKA NecMeister) and our mutual friend Ryan Jackson (AKA Roper) who wrote the proposal that will kill 250.32(B)(2).
Some of the others are regular contributors on alt.electrical.engineering and the ECN groups but they try to stay a bit more anonymous. |
|
#55
|
||||
|
||||
|
Quote:
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#56
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Maybe this will help Jeff. Bonding the grounded conductor to the disconnect enclosure serves a very important function, as we all know. What function could a switched or fused neutral possibly serve in the case of a remote building on the same system?
Please don't take this wrong, but many parts of the code are much easier to understand when a person has been in the trade for many years and understands electrical theory enough to understand the reasons behind a code requirement. Sadly there are still many "electricians" out there who do not understand basic theory. I was not allowed to take my NEC classes until I had completed my theory classes. I was not happy with that, but now I see the reason for it. Of course I will be the first to admit that I don't know it all. But one thing I do know, you are wrong in your interpertation of 250-32(B)(2) Last edited by brian winkle; 3/19/07 at 10:22 PM.. |
|
#57
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Don't feel bad about it. The cryptic language of the NEC can get fistfights started in inspector meetings. 250 is always good for a fight and this is the new and improved, rewritten 250. In 99 they scrapped the whole article and started over.
If you really want to be confused look at 250.24 in the 96 code where this used to be covered. The intent never changed but the language is completely different. |
|
#58
|
|||
|
|||
|
Please Note:
Ryan C. Jackson is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Subpanel wired as main panel. | jlybolt | Electrical Inspections | 15 | 5/23/07 4:10 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 9:02 PM |
| Distribution panel GEC | bsmith | Electrical Inspections | 11 | 9/13/06 3:26 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |