Angry Repairs made by a LICENCED electrician

Recommended that water logged panel be removed from "wet location" and new service run to "dry location" by a qualified, licensed electrician.

Well they moved it - living room dry location ok great, but sloppy work.

Checked the original location of the main panel and see it being used as a j box. propped by a 2x4 over a puddle, secured to the foundation ... yea by a water logged/rotting piece of OSB.


my report states: "Old main panel used as a junction box for the new service. this is a safety hazard as the "junction box is located in a wet location.
This installation is not recognized as a safe installation per national standards. A Qualified, licensed electrician should be consulted to properly relocate/rewire main panel/junction box/s"

Tom I may have to give you my next re-inspection fee so you can keep me from possibly causing injury to this hack if he is present when I do go back to re-inspect this work for a second time!

Techincal term for this brain dead hack installation - unfreakinbelievable!

PS- he charged the current homeowner over $2,000.00 for this cluster****.

Last edited by cduphily; 6/10/08 at 11:35 PM..
Reply With Quote
  #2  
Old 1/11/08, 6:23 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: Repairs made by a LICENCED electrician

Remember Chris, they think HI's are jokes!



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #3  
Old 1/11/08, 6:24 PM
Dale Duffy's Avatar
Dale Duffy Dale Duffy is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Scottsdale, AZ
Posts: 8,261
Default Re: Repairs made by a LICENCED electrician

Chris, that first picture is simply mind boggling what you guys have to put up with where it rains....or have basements.....

Oh, and the photos are incredible at best.....
Reply With Quote
  #4  
Old 1/11/08, 6:28 PM
cduphily's Avatar
cduphily cduphily is offline
Active Poster
 
Join Date: Sep 2006
Location: Dingmans Ferry, PA
Posts: 2,486
Please Note: cduphily is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Repairs made by a LICENCED electrician

Quote:
Originally Posted by bwiley
Remember Chris, they think HI's are jokes!
My client's REALTOR was present ... he looked at me after looking at my photos on site and said "thank you for coming out". Needless to say client and his RE agent are upset, current home owner is upset, and all their anger is squarely on the shoulders of the hack that completed the work.
unfreakinbelievable!

Hope someone fixes it over the weekend ... I have a CRM to pick up in the area on Monday .... perfect for my next re-inspection .... it would save me $10.00 in gas!
Reply With Quote
  #5  
Old 1/11/08, 6:31 PM
cduphily's Avatar
cduphily cduphily is offline
Active Poster
 
Join Date: Sep 2006
Location: Dingmans Ferry, PA
Posts: 2,486
Please Note: cduphily is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Repairs made by a LICENCED electrician

Quote:
Originally Posted by dduffy
Chris, that first picture is simply mind boggling what you guys have to put up with where it rains....or have basements.....

Oh, and the photos are incredible at best.....
You hiring? .... I hear it's all slabs out in sunny AZ!

I swear, I'm taking your advise .... market commercial inspections and not deal with this crap!

Last edited by cduphily; 6/10/08 at 11:35 PM..
Reply With Quote
  #6  
Old 1/11/08, 9:59 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,115
Default Re: Repairs made by a LICENCED electrician

Chris,

Foirward this to that Mike Whitt guy. Maybe he can explain it away.

After all, the NEC is designed to keep handymen like us out of the electrical panel.

Looks like a VERY professional installation.
Reply With Quote
  #7  
Old 1/11/08, 10:36 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Repairs made by a LICENCED electrician

Chris:

Just too much for words to adequately express, epecially in cases of gross stupidity or ignorance.

unfreakinbelievable!

They will be published in my articles soon! OK to use them?
Reply With Quote
  #8  
Old 1/12/08, 12:29 AM
Frank M. Carrio, CMI's Avatar
Frank M. Carrio, CMI Frank M. Carrio, CMI is offline
ESOP Committee Member
 
Join Date: Jan 2004
Posts: 4,364
Default Re: Repairs made by a LICENCED electrician

Quote:
Originally Posted by jfarsetta
Chris,

Foirward this to that Mike Whitt guy. Maybe he can explain it away.

After all, the NEC is designed to keep handymen like us out of the electrical panel.

Looks like a VERY professional installation.
Joe!
My thoughts EXACTLY! Mike Whitt thinks that he is G-ds gift to the Home Inspection industry and that everyone is stupid except him.

The guy is a joke!


One thing that I will give him credit for.....it must have been extremely dificult to get this Jack***** to hold still long enough to put a cowboy hat on it's head



Signed, Frank Carrio, CMI
Certified Master Inspector & Consultant
Certified Commercial Building Inspector
Certified, WDI Inspector
Founder & Current President, New Hampshire State Chapter NACHI
NACHI, State Representative for Legislative Affairs
Retired: ICC Certified Member
Retired: Code Compliance Inspector.
Retired: ASTM Committee Member
New Hampshire License #0096

Last edited by fcarrio; 1/12/08 at 1:46 AM..
Reply With Quote
  #9  
Old 1/12/08, 12:40 AM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Repairs made by a LICENCED electrician

Quote:
Originally Posted by jtedesco1
Chris:

Just too much for words to adequately express, epecially in cases of gross stupidity or ignorance.

unfreakinbelievable!

They will be published in my articles soon! OK to use them?
Me too, Chris.

I see many such "repairs" done by licensed and union electricians. I would love to put these into my courses.

Just shows that the repairs MUST be re-inspected.

Let's keep the liability in the right hands, and not in the Home Inspectors.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #10  
Old 1/12/08, 7:39 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: Repairs made by a LICENCED electrician

Repairs made by a...1/11/08 10:40 PM
I guess one of the tradesmen or tradesmen vendors didn't like my comment. Too bad he didn't have the balls to sign it, but then they don't want to put their comments in writing after we point out they screwed it up, either!



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #11  
Old 1/12/08, 7:43 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Repairs made by a LICENCED electrician

The guy who did that installation was neither an electrician nor was he qualified. At least this job did not show it.

BTW - Nice professionalism from some in this thread.
Frank, your post was especially out of line!
Reply With Quote
  #12  
Old 1/12/08, 7:54 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Repairs made by a LICENCED electrician

Quote:
Originally Posted by bwiley
Repairs made by a...1/11/08 10:40 PM
I guess one of the tradesmen or tradesmen vendors didn't like my comment. Too bad he didn't have the balls to sign it, but then they don't want to put their comments in writing after we point out they screwed it up, either!
Welcome to my world. I don't mind getting reds, just let me know why.

BTW- Us lowly non-members cannot give out reds or greens. One of your NACHI brothers gave you that red.
Reply With Quote
  #13  
Old 1/12/08, 8:04 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Repairs made by a LICENCED electrician

Oh I'm gunna be flamed.

There is a world where I think in. Peaceful, everyone is safe, and the streams flow with cold beer. I would have tried t completely move the home runs out into the new panel. One problem, I live in the real world.

If the guy changed out the old cabinet for a new corrosion resistant one, mounted it properly high enough (say 6" higher than any high water mark), this topic would be dead. So the problem is that he was lazy in the crawlspace. This is an simple, easy fix, nothing to scream about, except the home owner got the cheapest/fastest fix.

tom
Reply With Quote
  #14  
Old 1/12/08, 8:08 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: Repairs made by a LICENCED electrician

Quote:
Originally Posted by Speedy Petey
One of your NACHI brothers gave you that red.
Trust me Speedy, I'm well aware of that. I just think they should sign their name if they wish to leave a red. At least I know it wasn't Cookie, he leaves his initials on reds!



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #15  
Old 1/12/08, 2:48 PM
cduphily's Avatar
cduphily cduphily is offline
Active Poster
 
Join Date: Sep 2006
Location: Dingmans Ferry, PA
Posts: 2,486
Please Note: cduphily is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Repairs made by a LICENCED electrician

Quote:
Originally Posted by jtedesco1
Chris:

Just too much for words to adequately express, epecially in cases of gross stupidity or ignorance.

unfreakinbelievable!

They will be published in my articles soon! OK to use them?
any images I post are available to all members to use as they see fit.

I see too much of this crap on a daily basis from every trade here in PA.

I post the bad ones here when I really need to vent. .... It keeps me from sleeping on a piece of cold steel behind bars and other contractors from sleeping wit da fishes
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM