Default Reverse Polarity in Two Hole Outlet

How do you guys test for reverse polarity in a house with two hole outlets?
Cut the ground pin off your tester?
Reply With Quote
  #2  
Old 8/5/08, 8:18 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Reverse Polarity in Two Hole Outlet

With a non-contact voltage probe. Some people call it a "tic tracer". The wider slot is neutral, and the narrower slot should be the hot. The ticker should only light up in the shorter slot. I know some guys simply use one of those 3-prong to 2-prong adaptors on their regular receptacle tester.

If you run across any old receptacles where both slots are the same height, or where both slots are "T" shaped, I would recommend you call them out as recognized hazards. Put no special effort into determining the polarity of receptacles of this type.
Reply With Quote
  #3  
Old 8/5/08, 8:42 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,465
Default Re: Reverse Polarity in Two Hole Outlet

Quote:
Originally Posted by Marc D. Shunk

If you run across any old receptacles where both slots are the same height, or where both slots are "T" shaped, I would recommend you call them out as recognized hazards. Put no special effort into determining the polarity of receptacles of this type.
Could you please enlighten me on these type of receptacles as to why and if you have a photo would be nice.
Reply With Quote
  #4  
Old 8/5/08, 9:05 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 788
Default Re: Reverse Polarity in Two Hole Outlet

Quote:
Originally Posted by jallingham
How do you guys test for reverse polarity in a house with two hole outlets?
I have a Sure test tester with a retractable ground pin...



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
  #5  
Old 8/5/08, 9:45 PM
Justin D. Schlueter Justin D. Schlueter is offline
New User
 
Join Date: Jul 2008
Location: Minnesota
Posts: 10
Please Note: Justin D. Schlueter is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Reverse Polarity in Two Hole Outlet

Quote:
Originally Posted by dmacy
if you have a photo would be nice.
He's talking about a receptacle like this:



One of the reasons that I think that they are scary is that they could be wired for 120 or 240 volts. In other words, you could have one of these receptacles wired to 240 volt circuit. (and be able to plug in 120 volt appliances)
Reply With Quote
  #6  
Old 8/5/08, 10:55 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Reverse Polarity in Two Hole Outlet

good point
Reply With Quote
  #7  
Old 8/5/08, 11:13 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Reverse Polarity in Two Hole Outlet

Quote:
Originally Posted by Justin D. Schlueter
He's talking about a receptacle like this:

At least the one in your pic is polarized. They often aren't.
Reply With Quote
  #8  
Old 8/5/08, 11:45 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 696
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Reverse Polarity in Two Hole Outlet

With a 2-prong adaptor, these little testers tell you if there is power, but don't tell you polarity if there's no ground. OK for testing old razor outlets, there is no polarity concern with those, isolation transformer. The old outlets like the one in the middle are not polarized and ought to be replaced.

John Kogel
www.allsafehome.ca
Attached Thumbnails
reverse-polarity-two-hole-outlet-testfurnc.jpg   reverse-polarity-two-hole-outlet-two-prong-x3.jpg   reverse-polarity-two-hole-outlet-razorplug.jpg  

Last edited by jkogel; 8/6/08 at 12:53 AM..
Reply With Quote
  #9  
Old 8/6/08, 12:40 AM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 788
Default Re: Reverse Polarity in Two Hole Outlet

Attached is a few pics of receptacles/plugs.
Attached Files
File Type: pdf NEMA Plug.pdf (123.9 KB, 69 views)



Marcel Gratton, CMI
On The Level Inspection
Gatineau, QC
http://onthelevelinspection.com/
Reply With Quote
  #10  
Old 8/6/08, 12:40 PM
John Allingham John Allingham is offline
InterNACHI Member
 
Join Date: Jun 2004
Location: Milton, ON
Posts: 377
Default Re: Reverse Polarity in Two Hole Outlet

Thanks gents.
Reply With Quote
  #11  
Old 8/6/08, 12:47 PM
Ralph Brady's Avatar
Ralph Brady Ralph Brady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 610
Default Re: Reverse Polarity in Two Hole Outlet

As was stated already, the 3 prong testers do not work without a ground connection. You need to use one of these (or equivalent) to test for reverse polarity on all open ground 3-prong receptacles and all 2-prong receptacles. I like the fluke model, however I have not tried the new/current version that fluke is selling.

reverse-polarity-two-hole-outlet-p8060010.jpg



"An expert is a person who has made all the mistakes that can be made in a very narrow field"
Niels Bohr

"Learn all you can from the mistakes of others. You won't have time to make them all yourself"
Alfred Sheinwold


Eureka, Fortuna & Arcata, CA
Reply With Quote
  #12  
Old 8/7/08, 11:59 PM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Royal Oak, MI
Posts: 126
Default Re: Reverse Polarity in Two Hole Outlet

I just use my hand as the electrode by holding a probe tester with one probe on my hand and sticking the other probe in the slot. The hot slot will cause it to light up just a little bit -- barely noticably, but visibly.

Sometimes I shake my hand as if shocked as a practical joke ... sometimes making a "home inspector jackass" joke.
Reply With Quote
  #13  
Old 8/8/08, 12:51 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Reverse Polarity in Two Hole Outlet

Quote:
Originally Posted by fbartlo
I just use my hand as the electrode by holding a probe tester with one probe on my hand and sticking the other probe in the slot. The hot slot will cause it to light up just a little bit -- barely noticably, but visibly.

Sometimes I shake my hand as if shocked as a practical joke ... sometimes making a "home inspector jackass" joke.
You're an idiot.
Reply With Quote
  #14  
Old 8/8/08, 1:09 AM
Frank L. Bartlo Frank L. Bartlo is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: Royal Oak, MI
Posts: 126
Default Re: Reverse Polarity in Two Hole Outlet

Probe tester. I don't even so much as get a shock, but it is sometimes difficult to see the indicator light up.

But I'll test that 2-prong adaper idea. Never occurred to me that would work.

As I thought, it doesn't work: just shows as an open ground either correctly or incorrectly polarized.

Last edited by fbartlo; 8/8/08 at 1:17 AM..
Reply With Quote
  #15  
Old 6/2/09, 11:48 PM
Chuck Evans's Avatar
Chuck Evans Chuck Evans is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Stagecoach, TX
Posts: 690
Default Re: Reverse Polarity in Two Hole Outlet

double post

Last edited by cevans; 6/2/09 at 11:59 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Reverse polarity ddunning Electrical 9 5/9/08 11:08 PM
reverse polarity?? Scott Schultz Electrical 33 10/24/07 2:50 PM
Reverse Polarity dscott2 Electrical 12 6/26/07 1:22 AM


All times are GMT -4. The time now is 1:48 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts