The 50 year old riser on my 50 year old house is deteriorating. I am hiring a licensed electrician to replace it.
I am relatively new to the US and have noted a lack of fuses along transmission lines. My question is this. If my riser, which goes up the side of my house via the meter, were to deteriorate to the point that it would short, what would happen? A big flash, a fire? Both? Is the only safety device the transfomer (which would blow) a mile away? Why aren't houses with deteriorated risers burning down at the rate of dozens? Last edited by Ian Gills; 3/10/08 at 6:06 PM.. |
|
#2
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Service conductors are not fused. The primary protection should protect the transformer but as long as it is OK the service conductors will keep arcing and sparking. I saw one in the Keys boil all of the water out of a puddle it fell in and start melting the asphalt paving before FPL got there and pulled the primary fuse.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Commercial Electrical Inspections | jtedesco1 | Commercial Inspections | 29 | 1/12/08 5:03 AM |
| Am I right? The IRC has no minimum rise height for stairways??? | gromicko | Interior Inspections | 25 | 1/2/08 11:56 AM |
| Deck stair riser | Kevin Luce | Exterior Inspections | 1 | 10/1/07 8:32 PM |
| code for minimum floor space at top of stairs? | areid | Miscellaneous Discussion for Inspectors | 12 | 4/16/07 9:39 AM |