Default Romex connected to male plug... OK?

Today, I came upon a ceiling fan installed in an apartment with a concrete ceiling and cement block walls. The wiring was run on the ceiling and walls and covered with wood molding down to the vicinity of the receptacle. At the end of this molding run the Romex ran outside the molding about a foot or so and was connected to a male 3-prong plug that was plugged into that receptacle.

I didn't tag it because I couldn't really determine if it was a problem. Wood moldings are OK to use in our area, so that was not a problem. The male plug was connected properly, so that was not a problem. It was just weird to see Romex with a 3-prong plug.

I searched the NEC reference books that I have and found nothing that prohibits Romex from having a plug attached or from being used as an "extension" cord for that matter. Am I missing something?

Thanks for any responses.
Reply With Quote
  #2  
Old 2/28/07, 8:12 AM
away away is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Aledo, TX
Posts: 229
Default Re: Romex connected to male plug... OK?

Gary,
I remember reading somewhere (I looked but can't find the source right now) where you can't use solid conductors as an extension cord. They are more prone to breaking than stranded conductors. But that would assume that one would be coiling and uncoiling the cord.

The only reference I could find was in my Code Check chart which referred back to IRC 3303.3 which is Listing and Labeling of electrical system components being used in such a manner that is consistent with manufacturers installation instructions. My gut feeling is that NM is not listed to be used in a cord and plug manner.

There is also a reference in IRC 3809.1 where is discussed flexible cords being used in leiu of permanent wiring. Given that a ceiling fan is intended to be a "permanent" fixture it should therefore be supplied by permanent wiring.
Reply With Quote
  #3  
Old 2/28/07, 8:15 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Romex connected to male plug... OK?

Hi to all,

Gary, am I understanding you correctly? from what you are saying the outlet was fed by a male plug attached to romex, is that correct? If so then the plug prongs would be energized all the time, and would present a clear shock hazard should someone remove the plug.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #4  
Old 2/28/07, 10:36 AM
Jason A. Sieg, CMI's Avatar
Jason A. Sieg, CMI Jason A. Sieg, CMI is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Davison, MI
Posts: 839
Default Re: Romex connected to male plug... OK?

Gerry,

I think he is saying just the opposite. When you insert the plug (connected to Romex) into the receptacle, it energizes the Romex run to the ceiling fan.

In other words the Romex has been converted into an extension core with a ceiling fan on one end and a plug on the other end.



Jason Sieg, CMI
Davison, MI
NACHI05091399


Knowing the current condition,
to make a wise decision.

President, Great Lakes-East Chapter
Join NACHI Great Lakes - East Chapter

http://mi.nachi.org/greatlakes-east/about.html
ssieg@gfn.org
Reply With Quote
  #5  
Old 2/28/07, 11:48 AM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 5,686
Default Re: Romex connected to male plug... OK?

Romex wire is not approved as a flexible cord. [IRC 4001.3]

Romex wire is not authorized for use outside of the finished wall system Unless it is protected within an approved conduit.
Reply With Quote
  #6  
Old 2/28/07, 11:51 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: Romex connected to male plug... OK?

Quote:
Originally Posted by dandersen
Romex wire is not approved as a flexible cord. [IRC 4001.3]

Romex wire is not authorized for use outside of the finished wall system Unless it is protected within an approved conduit.
Thanks for the reference



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #7  
Old 2/28/07, 1:10 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex connected to male plug... OK?

The rule actually says "protected from physical damage" not "conduit". A wood chase might be OK but the cord cap (plug) is still troubling.
Reply With Quote
  #8  
Old 2/28/07, 1:28 PM
lcapaul's Avatar
lcapaul lcapaul is offline
Active Poster
 
Join Date: Jun 2005
Location: Rathdrum, ID
Posts: 1,581
Please Note: lcapaul is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex connected to male plug... OK?

Quote:
Originally Posted by gbeaumont
Hi to all,

Gary, am I understanding you correctly? from what you are saying the outlet was fed by a male plug attached to romex, is that correct? If so then the plug prongs would be energized all the time, and would present a clear shock hazard should someone remove the plug.

Regards

Gerry
You would have liked the one I found the other day, the people had romex run to a old falling down garage about 60 feet away and only 7 foot off the ground, the neat part was the end of the romex inside the house, the copper wires had been flattened and stuck directly into a recepticle which, for some "unknown" reason the owners couldn't figure out, was all scorched and burned around one of the connectors in the recepticle. A plug would have been High Tech.
Reply With Quote
  #9  
Old 2/28/07, 1:52 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex connected to male plug... OK?

Ah the good old "Mexican service drop". That is not as uncommon as one would think. OTOH if this "drop" was a messenger supported UF cable, properly terminated and high enough it might be legal.
Reply With Quote
  #10  
Old 2/28/07, 2:07 PM
ghawley ghawley is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Honolulu, HI
Posts: 12
Please Note: ghawley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex connected to male plug... OK?

Thank you everybody for the responses. My gut feel is that is wasn't right, but I just wasn't certain of the exact reference. I am completing the report this morning with everyone's comments in mind.
Reply With Quote
  #11  
Old 2/28/07, 3:06 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex connected to male plug... OK?

The suggestion to bring this into compliance woiuld be a surface extension box with the splice in there. They would still be able to have the receptacle on the extension. A plastic wiremold box would work.
Reply With Quote
  #12  
Old 2/28/07, 10:07 PM
whandley's Avatar
whandley whandley is offline
Active Poster
 
Join Date: Sep 2004
Location: Laguna Niguel, CA
Posts: 2,093
Please Note: whandley is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex connected to male plug... OK?

Quote:
Originally Posted by dandersen
Romex wire is not approved as a flexible cord. [IRC 4001.3]

Romex wire is not authorized for use outside of the finished wall system Unless it is protected within an approved conduit.

That's not always the case David. In several counties here in california romex maybe left exposed when installed inside the open wall studs or above the plate line. I agree however in most areas romex subject to physical damage must be protected.
Reply With Quote
  #13  
Old 2/28/07, 10:14 PM
wward wward is offline
New User
 
Join Date: Nov 2004
Location: Tampa, FL
Posts: 81
Please Note: wward is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex connected to male plug... OK?

If the fan has the plug with romex it's ok
you can unplug the romex and all is well.
I find this on lanis with fans pluged into the receptracle.
If you can un plug it than it's no more than an extention cord.
Reply With Quote
  #14  
Old 2/28/07, 11:14 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Romex connected to male plug... OK?

Did a draw inspection, today. Went down in the basement and there was a radio going (with Polish music). I wasn't looking closely and I tripped over am electrical cord (to the radio) and the radio died.

I appologized and looked down.

The radio power wire had no plug. Just the bear wires stuck in a multiple recepacle extension cord.

The worker came over and pushed the wires back in. No harm, no foul.

Guess what kind of workers they were?







Yep. Licensed and insured, union electricians.

Go figure.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #15  
Old 2/28/07, 11:25 PM
ggreene ggreene is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Springhill, Fl
Posts: 162
Default Re: Romex connected to male plug... OK?

Whitley,romex is an indoor jacketed wire, that is not to be run outdoors on lanais. Aside from that the last thing i would want to unplug here in florida is an extension cord run by a homeowner !!



GREG GREENE
RANGER HOME INSPECTIONS,INC.
www.rangerhomeinspections.com
gregatranger@aol.com
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Help. What is the correct way to report a breaker that is too big. gromicko Electrical Inspections 72 3/12/08 12:19 AM
Romex question jcahill Electrical Inspections 22 7/11/07 9:26 AM
Romex Wire Through Stucco Wall Tab M. Wilcox Electrical Inspections 12 5/11/06 2:33 AM
Romex wire connected to standard male plug. ghawley Electrical Inspections 2 3/2/06 2:35 PM
Romex on a Boiler? mgifford Electrical Inspections 7 1/10/06 5:27 PM