Default Is Romex in a crawl space a problem?

Question:

Is there any problem with romex installed in a crawl space, or are we supposed to install EMT, "Thinwall" as they do in Chicago?

What about "BX" any problems with that wiring method in a crawl space?

My personal opinion:

If its a damp location, both BX and Romex would not be permitted, and using EMT is OK but not the best way out. One could install Type UF Cable instead.
Reply With Quote
  #2  
Old 2/5/06, 5:38 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: Is Romex in a crawl space a problem?

I think the question you posed deserves an official answer. Simply because a crawlspace exists, does not automatically qualify it as a damp location.

Further, if the romex simply passes through the space, even it it is damp, should not necessarily cause a problem. As to damp locations, I believe the restriction is more specific, as to the amount of moisture present. And, the truth of the matter is that there are thousands of homes where this cable is installed in damp crawlspaces. The question is whether the crawlspace is simply damp, or actually wet. I also question the question, in its entirety, as the NEC specifies a normally dry location. I do not believe crawlspaces are constructed, nor acceptable, in a normally wet condition.

I agree that damp locations may be problematic for metallic sheathed cabling, from the standpoint of the long-term affect of the moisture on the sheathing. As we know, some metallic sheathed cables have a separate conductor embedded inside the sheathing for grounding, while others have aluminum tracer wound around the sheathing, which is not affected by rust, and is installed to specifically allow a continuous grounding path via the metallic sheathing. Either scenario is no more affected than EMT will be. EMT will rust in time. For some applications, sealed fittings are required on EMT.

I believe the correct answer is that it depends. It depends on whether the crawlspace is truly considered as a damp location. Was it designed to be normally dry or normally wet, because the latter brings in an entire new set of rules for the inspector. The conditions are determined on-site.

Then, the question as to why the crawlspace is damp or wet raises other questions, like are site drainage issues causing the problem. Is there adequate ventilation in the crawlspace? Why is it wet? Then, are there open j-boxes present, which may prevent the inspector from venturing into the crawlspace? Dirt floor or rat slab? Entry from inside the dwelling or outside?Are the runs in question original, or part of a retrofit? Is there metallic sheathed cabling present, which is rusting or broken?

IMO, barring any applicable, non-obscure ruling, open to interpretation, then the situation needs to be evaluated on a case by case basis.

Indeed, the crawlspace in my home is vented to the inside basement. It is 3' high, has a concrete rat slab, and is dry. By the way, its loaded with romex, inspected and approved by the Board of Fire Underwriters.

So, in my case, the answer is yes, it is fine. Either romes or bx, or EMT

Last edited by jfarsetta; 2/5/06 at 6:18 PM..
Reply With Quote
  #3  
Old 2/5/06, 5:49 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is Romex in a crawl space a problem?

Joe:

This question was asked here at the Convention and the Instructor said that EMT was required, I said UF cable here in my personal opinion, only because it is designed for underground.

I was not addressing sunlight. Naturally, the location is not always damp, but in some areas it is damp and may even be wet.

PS: Quite a bit of discussion concerning New Construction Inspection of Electrical Wiring, and many questions could use more detailed replies.

I believe that the NEC Forum should be re opened again for this type of discussion. I know of a new kid who has taught the 1999 and 2002 NEC that will be helpful there.
Reply With Quote
  #4  
Old 2/5/06, 6:21 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: Is Romex in a crawl space a problem?

I believe the instructor was incorrect, but he is entitled to his opinion. We are supposed to be generalists, and each inspector should be familiar with applicable codes in his or her own area, IMO. I limit that comment to those GENERAL rules one may encounter on an inspection, like what is acceptable for wiring in a crawlspace. However, I still go back to the assumption that crawlspaces are not normally considered as wet locations. If so, I believe there would be construction rules and further observations which could also be applicable.

On wet days, an electrician may encounter a river running in the crawlspace. That doesnt mean he will alter the materials he is allowed to use because the crawlspace may be wet on a particular day. He will wait until conditions change, as this is not the normal condition encountered in that crawlspace.

Going to the NEC (both 1999 and 2002) it speaks to locations which are normally dry. I dont see damp. I believe the assumption is that crawlspaces are designed to be normally dry. I think that says it all. Wet locations may bring a whole new set of rules to the table. I believe EMT does not necessarily perform well in wet conditions, either, and is subject to breakage and physical damage to the conductors contained therein.

Chicago has some whack rules, IMO. BTW, who was the instructor. I'd like to see his reference to the NEC verbiage. I conferred with several licensed electricians when answering this question, and their answers were identical.

Last edited by jfarsetta; 2/5/06 at 6:29 PM..
Reply With Quote
  #5  
Old 2/5/06, 6:55 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is Romex in a crawl space a problem?

Joe, there was no reference given to any rules, and the entire presentation for Advanced Electrical was not available for use because of a software problem, so Gerry took the discussion toward a checklist from a local city and pointed out the New Construction items.

That list can be found here:


http://www.tcfl-libinfo.com/

Perry, Florida

Taylor County Building Department
William D. Griner
Building Inspector
Taylor County Administrative Complex
201 E. Green St.
Perry Fl. 32347
(850)838-3500 Ext. 8 | 850-838-3501 fax
Reply With Quote
  #6  
Old 2/5/06, 7:03 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is Romex in a crawl space a problem?

If an inspector was to call out romex that was attached to the joist under the crawl space he would be questioned to death by the electrician that was called to perform repairs. As well as the state or city inspector. At least in this area. I would not suggest calling this out at all, anytime. Unless the romex in in connection with the ground.
I would say the instructor is off base, if he is speaking nationally as a suggestion.

If discussions like this continue they will want you to run rigid in crawl spaces. not gonna happen.
Reply With Quote
  #7  
Old 2/5/06, 7:21 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: Is Romex in a crawl space a problem?

I take exception to the comments listed in one of the links Joe T provided (I know that its not your link, Joe.. so no foul!).

In the first one, under "aluminum wiring" (that's all) the "rule" is that aluminum and copper splices are only permitted in split-bolt connectors, which discounts other approved splicing methodologies. This is totally false. The second comment states that all aluminum wire terminations reqire anti-oxidizing compounds, which is also false. It depends on the instructions of the equipment manufacturer.

I see no where that EMT as required, and no reference to romex or bx being prohibited in crawlspace areas. The other problem I see is that the referenced material is specific to a municipality, which is not necessarily applicable in all jurisdictions...

And Ben is dead-on. I think the premise is absurd

Last edited by jfarsetta; 2/6/06 at 1:21 AM..
Reply With Quote
  #8  
Old 2/5/06, 11:34 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Is Romex in a crawl space a problem?

lol..who is this NEW kid...lol.......do we know him Joe...?

I do have some opinions on the romax in crawl spaces if anyone wants MY opinion on it from a everyday practicle use opinion...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #9  
Old 2/6/06, 12:42 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: Is Romex in a crawl space a problem?

Paul,

Which new kid are you speaking of. There are two Joe's here. And, yes, we'd like to hear your opinion onthe matter, then a reference in the NEC where it is prohibited, which is where this started from.
Reply With Quote
  #10  
Old 2/6/06, 12:50 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is Romex in a crawl space a problem?

If this is really Perry Florida I have two things you should know.
First there is only one electric code in Florida, the NEC, with no local addendums.
The second thing is, them good old boys in Perry Florida do whatever they damn well please. A whole lot of laws haven't caught up with them.
Reply With Quote
  #11  
Old 2/6/06, 12:57 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: Is Romex in a crawl space a problem?

So Greg,

What are your thoughts on the initial comments regarding romex in a crawlspace?

Admittedly, I'm no sparky. I have lots of friends who are not only licensed for some time, but who are extremely competent.

We cannot find the reference anywhere, and believe that the application is acceptable.

Last edited by jfarsetta; 2/6/06 at 1:02 AM..
Reply With Quote
  #12  
Old 2/6/06, 4:26 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is Romex in a crawl space a problem?

Quote:
Originally Posted by pabernathy
lol..who is this NEW kid...lol.......do we know him Joe...?

I do have some opinions on the romax in crawl spaces if anyone wants MY opinion on it from a everyday practicle use opinion...
Paul, I knew you would catch on and if you can give your opinion on this subject we can take it a bit furthur.
Reply With Quote
  #13  
Old 2/6/06, 8:24 AM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 4,107
Default Re: Is Romex in a crawl space a problem?

Okay, guys...

What's up here?
Reply With Quote
  #14  
Old 2/6/06, 9:39 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is Romex in a crawl space a problem?

Yoo Dude want my opinion? I think that the comments about the area are important, I have seen some areas in crawl spaces and basements that show signs of, and deteriorated cables and any metallic wiring method with total rust and no longer of any use at all.

I am a friend of "The Nail" so let get this to an agreement.

Yoo Paul where are you?

Last edited by jtedesco1; 3/4/06 at 9:28 PM..
Reply With Quote
  #15  
Old 2/6/06, 11:32 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Is Romex in a crawl space a problem?

Joe,

Is that image the latest picture of you at the convention...thehehe..nice suit.

Actually when it comes to this issue I have to tell you it is seriously not enforced in this area and in most areas I see unless their is evidence of serious moisture issues.

I wont start quoting code here because I think we know what code says....but I have to tell you...in all the houses my company wire and the dozens of companies in the area and many have a crawl space.....their is plenty of romax running through the crawl.

In many electrical thoughts the easiest way to run the wires lets say on a first floor is down and up....keeping the possibly issues of a over inspired drywaller who is using the wrong length screws from poking the wire.....and in some cases is just goes faster than drilling every stud.....

Either way......here is MY opinion and it just happens to the opinion of the local AHJ's that I run into as well....

I do not see a problem with romax entering down into the crawl space and coming back up at the correct location.....moisture and damp is one thing but if you reduce the odds of it coming in contact with the issues the less of an issue it becomes.

While the NEC clearly states where Romax can be located....what is does not do is define exactly where damp locations exist without using good judgement and in my opinion it really depends on the individual crawl space.....We see plenty of them that are dry as a bone....and because they are constructed correctly will stay that way.....so it really depends on the space.....honestly if we said every wire entering a crawl has to be of a nature that is allowed in damp locations.....we would NEVER get a house wired and make a profit......

Their is a huge difference in a damp crawl space and a dry crawl space.....and while we can't predict the future of that space I personally do not in my own opinion...beyond the NEC....and what the local AHJ's are supporting as a real damp location that could have effect on the romax that is (1) most likely above the insulation and (2) not in direct contact with the damp or moist surface or so on.....I just dont see it as a huge problem and again with all the homes done in virginia alone...the AHJ's will not create a issue that is not a issue.

Probably not what you wanted to hear....but again I have been doing this for 18 years....and I am not going to stop running romax down into the crawl and back up if needed......in my eyes perfectly fine.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Return air from crawl space WHI Inspecting HVAC Systems 11 1/9/12 8:43 PM
Crawl space in under house dnasser Structural Inspections 15 2/27/07 8:12 PM
No Crawl Space Ventilation dmccormick Structural Inspections 11 2/5/07 11:34 AM
Manufactured home crawl space sstanczyk Structural Inspections 2 2/19/06 5:23 PM


All times are GMT -4. The time now is 8:14 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts