Default Romex in the garage...need advice

Does romex always have to be enclosed in conduit or behind
the wall below 7ft. in a residential garage?

This romex starts about 3ft. high.






An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
Need a home inspection in Utah? Check out InterNACHI's listing of Utah certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 10/4/11, 8:09 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex in the garage...need advice

There is no minimum height mentioned in the NEC. However, there is a prohibition against using NM where subject to physical damage. Physical damage is not defined in the NEC and is subject to individual definition. Acceptable methods of protection are listed in Article 334.

Side note, raceways are prohibited from providing support like is shown with the NM ty-rapped to the conduit.
Reply With Quote
  #3  
Old 10/4/11, 8:25 AM
Gary D. Rowden Gary D. Rowden is offline
InterNACHI Member
 
Join Date: Sep 2008
Location: Hemet, CA
Posts: 146
Default Re: Romex in the garage...need advice

Anytime I see exposed romex wiring in a garage that is lower than 7’ I call it out, even though when structure was constructed it may have passed inspection.
“There is exposed romex wiring inside garage that is low enough to be subject to physical damage and could cause a danger, this is a safety concern. Recommend further review and corrections from a qualified electrician contractor.”
Reply With Quote
  #4  
Old 10/4/11, 9:11 AM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: Romex in the garage...need advice

Quote:
Originally Posted by growden View Post
Anytime I see exposed romex wiring in a garage that is lower than 7’ I call it out, even though when structure was constructed it may have passed inspection.
“There is exposed romex wiring inside garage that is low enough to be subject to physical damage and could cause a danger, this is a safety concern. Recommend further review and corrections from a qualified electrician contractor.”
thanks for this verbiage....

David



An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
  #5  
Old 10/4/11, 9:12 AM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: Romex in the garage...need advice

Quote:
Originally Posted by Jim Port View Post
There is no minimum height mentioned in the NEC. However, there is a prohibition against using NM where subject to physical damage. Physical damage is not defined in the NEC and is subject to individual definition. Acceptable methods of protection are listed in Article 334.

Side note, raceways are prohibited from providing support like is shown with the NM ty-rapped to the conduit.

Thanks for the feedback...

David



An Ounce of prevention is better
than a pound of cure :}
Reply With Quote
  #6  
Old 10/4/11, 10:57 PM
Dan Bowers, CMI Dan Bowers, CMI is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Shawnee Mission, KS
Posts: 3,893
Default Re: Romex in the garage...need advice

David - Use your head / FORGET when it was built or NOT built.

PART was in conduit / part was outside conduit in same location ... This is NOT rocket science. Its handyman crap. Write it needs repair...Period.
Reply With Quote
  #7  
Old 10/4/11, 10:59 PM
Paul Pendley Paul Pendley is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: CA
Posts: 1,274
Default Re: Romex in the garage...need advice

Lets not forget the black taped extension cord from the outlet!!



Paul Pendley
Premier Property Inspections
866-458-8516
Reply With Quote
  #8  
Old 10/5/11, 4:22 PM
Pete Campbell's Avatar
Pete Campbell Pete Campbell is offline
InterNACHI Member
 
Join Date: Apr 2011
Location: Fort Pierce, FL
Posts: 591
Default Re: Romex in the garage...need advice

always in the wall or in conduit under 7' A.F.F.





Pete Campbell

pete4545@comcast.net
http://www.PortStLucieInspections.com
http://www.ChooseGI.com
http://ifwemissitwewillfixit.com


Inspecting Fort Pierce, St. Lucie Village, Lakewood Park, Vero Beach, Indian River Shores, Sebastian, Fellsmere, Fort Drum, Okeechobee, Jensen Beach, Stuart, Palm City, Hobe Sound and Indiantown, Florida.
Reply With Quote
  #9  
Old 10/5/11, 5:52 PM
Eric C. Van De Ven's Avatar
Eric C. Van De Ven Eric C. Van De Ven is online now
InterNACHI Member
 
Join Date: Mar 2003
Location: South Florida
Posts: 2,322
Default Re: Romex in the garage...need advice

Must be protected. for those of you afraid of the code, it is a safety issue.
Guy finishes trimming his trees with one of those pole saws and lays it down on the Romex.....
Ask me how I know!
Reply With Quote
  #10  
Old 10/5/11, 9:26 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex in the garage...need advice

Where does the 7' come from?
Reply With Quote
  #11  
Old 10/5/11, 11:14 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex in the garage...need advice

Quote:
Originally Posted by pcampbell View Post
always in the wall or in conduit under 7' A.F.F.
Not according to the NEC.

Quote:
Originally Posted by dbowers View Post
David - Use your head / FORGET when it was built or NOT built.

PART was in conduit / part was outside conduit in same location ... This is NOT rocket science. Its handyman crap. Write it needs repair...Period.
There is a possibility that the conduit was not needed in the first place. While it should not have been secured to the conduit, NM can be run on the surface. Again the subject to damage is subjective.

Last edited by Jim Port; 10/5/11 at 11:18 PM..
Reply With Quote
  #12  
Old 10/6/11, 12:01 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: Romex in the garage...need advice

Does everyone get on their knees and look under garage steps?
I found some wiring completely eaten through under a one foot tall landing with bare copper up against the wood. This was the only romex visible in the entire garage.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Attached Garage Fire Containment. Please proof this new inspection article. gromicko General Inspection Discussion 38 8/12/09 6:55 PM
Garage door inspection procedure bgromicko General Inspection Discussion 5 8/7/09 12:47 PM
Garage / Apt separation Carol Jones Structural Inspections 1 6/14/09 7:56 AM


All times are GMT -4. The time now is 9:27 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts