Default Romex question

1) Can romex be directly attached to a disposer?
2) Can romex be attached to a plug (is there an approved plug)?

Having trouble finding the answers via Google.

Thanks
Reply With Quote
  #2  
Old 7/5/07, 8:44 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Romex question

Answers :

1.) Question # 1 - Depends on who you ask. If the romex is subject to physical damage and not run with the contours of the building then it should be sleeved and protected ( whips have some exceptions as well ). Personally if it is run with the contour of the plumbing and is not hanging down I would probably not harp on it too much....but thats me ( I see gray sometimes )

If they want to be safer...sleeve it in some liquidtight for a little added protection.

2.) No, Romex should not be connected to an attachment plug for the intent you are speaking about. It is not considered cord or flexible cord ( ie: SO and SJ cord for example )

Attachment Plug (Plug Cap) (Plug).
A device that, by insertion in a receptacle,
establishes a connection between the conductors of the attached flexible cord and the
conductors connected permanently to the receptacle.


Best thing for them to do is take that Romex into a BOX mounted on the surface and buy a 4' listed and approved Disposal Cord and Plug set and use that...then plug it into the newly mounted receptacle.



Paul W. Abernathy

Last edited by pabernathy; 7/5/07 at 9:01 PM..
Reply With Quote
  #3  
Old 7/5/07, 10:31 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: Romex question

I call it out as "sub standard" installation. Romex is not designed or intended to be a flexable cord. Upgrades recommended by a qualified trades person.

What, why and how.



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #4  
Old 7/5/07, 10:34 PM
John Cahill John Cahill is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Plano, TX
Posts: 826
Default Re: Romex question

Thanks for the info,

I sometimes see romex run straight to a disposer. I write it up but never really knew a source to back me up.

I write up a plug on romex however I saw one today that really looked like it was intended for the romex. A nicely done connection. I wrote it up as usual but still wondered.

I know the disposer manufacturers allow direct connections and they are made up in a j box. The switch is considered the disconnecting means.
Reply With Quote
  #5  
Old 7/6/07, 7:01 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Romex question

Quote:
Originally Posted by jcahill
The switch is considered the disconnecting means.
Yep.....except if they try to use a decora "ROCKER" switch which has no On/Off actually on the switch.



Paul W. Abernathy
Reply With Quote
  #6  
Old 7/6/07, 9:08 AM
John Cahill John Cahill is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Plano, TX
Posts: 826
Default Re: Romex question

Faster to carry a magic marker than write it up.

Last edited by jcahill; 7/6/07 at 2:48 PM..
Reply With Quote
  #7  
Old 7/6/07, 12:21 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex question

Interesting point Paul. Personally I still like the idea of cord and plug connected disposals and dishwashers. If you order them that way it is only a couple bucks more, cheaper than buying a plug and 3 feet of romex. Legal too.
Reply With Quote
  #8  
Old 7/6/07, 12:26 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Romex question

Greg,

I am with you fella, I install all mine with a cord and plug on it and place a receptacle under the sink for each of these items. Both of which get a single plug ( 20A ) and just makes for a nice and neat install.

And you are so correct.....a legal one to boot...



Paul W. Abernathy
Reply With Quote
  #9  
Old 7/6/07, 6:25 PM
John Cahill John Cahill is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Plano, TX
Posts: 826
Default Re: Romex question

May I clarify. I am still a bit in the dark.

Is attaching the romex directly to a dishwasher allowed?
Is attaching the romex directly to a disposer allowed?

I understand the preferred method of a cord and receptacle. I also know there are regional variations.
Reply With Quote
  #10  
Old 7/6/07, 6:44 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Romex question

Quote:
Originally Posted by jcahill
May I clarify. I am still a bit in the dark.

Is attaching the romex directly to a dishwasher allowed?
Is attaching the romex directly to a disposer allowed?

I understand the preferred method of a cord and receptacle. I also know there are regional variations.
Romex direct to disposal or dishwasher can be okay if not subjected to physical damage but don't connect an attachment plug to romex in order to plug it into a receptacle.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #11  
Old 7/6/07, 7:17 PM
John Cahill John Cahill is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Plano, TX
Posts: 826
Default Re: Romex question

Thanks. . . . I think I have it now.
Reply With Quote
  #12  
Old 7/6/07, 7:38 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Romex question

Quote:
Originally Posted by lkage
Romex direct to disposal or dishwasher can be okay if not subjected to physical damage but don't connect an attachment plug to romex in order to plug it into a receptacle.
Here that translates to: exposed in the house anywhere, lower than 7' high in a shed or on the patio, exposed to direct sunlight.

Your reccomended serving suggestions may depend on your regional tastes, please consult your personal physican before adjusting your milage
Reply With Quote
  #13  
Old 7/6/07, 9:04 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex question

This has always been a grey area. A strict reading of the code says you can't run exposed Romex unless it closely follows the building surface. Flying arcoss under a sink base can hardly fit that description but is a handy place to hang the windex sprayer.
In that regard, coming out the drain bezel in the drywall and tywrapped to the pipe is probably more code compliant than anything else I can think of.
Reply With Quote
  #14  
Old 7/6/07, 9:10 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Romex question

Quote:
Originally Posted by bkelly2
Here that translates to: exposed in the house anywhere, lower than 7' high in a shed or on the patio, exposed to direct sunlight.

Good point...I'll try to stay with "around here".



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #15  
Old 7/6/07, 9:16 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Romex question

Quote:
Originally Posted by Greg Fretwell
This has always been a grey area. A strict reading of the code says you can't run exposed Romex unless it closely follows the building surface. Flying arcoss under a sink base can hardly fit that description but is a handy place to hang the windex sprayer.
In that regard, coming out the drain bezel in the drywall and tywrapped to the pipe is probably more code compliant than anything else I can think of.
Like this Greg? http://www.nachi.org/forum/f11/plumbing-electricial-18356/
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Safety Foundation International Links jtedesco1 Electrical Inspections 5 12/8/07 3:10 PM
WA State Legislative update hmiller Legislation, Licensing & Legal Issues for Inspectors 153 5/4/07 11:55 PM
Romex Wire Through Stucco Wall Tab M. Wilcox Electrical Inspections 12 5/11/06 1:33 AM
Romex wire connected to standard male plug. ghawley Electrical Inspections 2 3/2/06 1:35 PM