  #1  
Old 4/25/11, 2:54 PM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Romex under patio eave...Question

This is for exterior lights connected to eaves....
Should the wire runs be in conduit?

Reply With Quote
Need a home inspection in Rhode Island? Check out InterNACHI's listing of Rhode Island certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 4/25/11, 3:11 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Romex under patio eave...Question

"Romex" (NM) does not belong in conduit, and it is not allowed for use in damp/wet locations.

So the answer to your question is "no," but this wiring method is improper for exterior lighting.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 4/25/11, 3:20 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Romex under patio eave...Question

What Jeff said as you should never double insulate conductors.
Reply With Quote
  #4  
Old 4/25/11, 4:12 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex under patio eave...Question

I agree that standard NM cable is not permitted in wet or damp locations. NM cable is permitted to be pulled into a raceway providing that the allowable raceway fill is followed.
Reply With Quote
  #5  
Old 4/25/11, 4:14 PM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: Romex under patio eave...Question

Quote:
Originally Posted by jpope View Post
"Romex" (NM) does not belong in conduit, and it is not allowed for use in damp/wet locations.

So the answer to your question is "no," but this wiring method is improper for exterior lighting.
I have seen Romex rated for exterior use.




774 Manor Road
Staten Island, NY 10314
718-514-3393
Reply With Quote
  #6  
Old 4/25/11, 4:21 PM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: Romex under patio eave...Question

Quote:
Originally Posted by jpope View Post
"Romex" (NM) does not belong in conduit, and it is not allowed for use in damp/wet locations.

So the answer to your question is "no," but this wiring method is improper for exterior lighting.
Thanks Jeff...Im will use this statement...

( wiring method is improper for exterior lighting. )
Reply With Quote
  #7  
Old 4/25/11, 4:31 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex under patio eave...Question

Quote:
Originally Posted by jgromkoski View Post
I have seen Romex rated for exterior use.

You're correct, there is a cable, NMC that is listed for damp and wet locations but it's a pretty rare cable type .

Quote:
II. Installation
334.10 Uses Permitted.
Type NM, Type NMC, and Type NMS cables shall be permitted to be used in the following:
(1) One- and two-family dwellings.
(2) Multifamily dwellings permitted to be of Types III, IV, and V construction except as prohibited in 334.12.
(3) Other structures permitted to be of Types III, IV, and V construction except as prohibited in 334.12. Cables shall be concealed within walls, floors, or ceilings that provide a thermal barrier of material that has at least a 15-minute finish rating as identified in listings of fire-rated assemblies.
FPN No. 1: Types of building construction and occupancy classifications are defined in NFPA 220-2006, Standard on Types of Building Construction, or the applicable building code, or both.
FPN No. 2: See Annex E for determination of building types [NFPA 220, Table 3-1].
(4) Cable trays in structures permitted to be Types III, IV, or V where the cables are identified for the use.
FPN: See 310.10 for temperature limitation of conductors.
(A) Type NM. Type NM cable shall be permitted as follows:
(1) For both exposed and concealed work in normally dry locations except as prohibited in 334.10(3)
(2) To be installed or fished in air voids in masonry block or tile walls
(B) Type NMC. Type NMC cable shall be permitted as follows:
(1) For both exposed and concealed work in dry, moist, damp, or corrosive locations, except as prohibited by 334.10(3)
(2) In outside and inside walls of masonry block or tile
(3) In a shallow chase in masonry, concrete, or adobe protected against nails or screws by a steel plate at least 1.59 mm ( in.) thick and covered with plaster, adobe, or similar finish
Reply With Quote
  #8  
Old 4/25/11, 4:39 PM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Romex under patio eave...Question

Quote:
Originally Posted by jgromkoski View Post
I have seen Romex rated for exterior use.
http://www.paigeelectric.com/specs/P7295D.pdf
Reply With Quote
  #9  
Old 4/25/11, 5:46 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Romex under patio eave...Question

Quote:
Originally Posted by jgromkoski View Post
I have seen Romex rated for exterior use.
As have I, but chances are slim to none that the right type is in use here.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 4/25/11, 8:50 PM
Tim Spargo's Avatar
Tim Spargo Tim Spargo is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Lancaster, CA
Posts: 2,407
Default Re: Romex under patio eave...Question

I gotta agree... just about anytime we see NM on the exterior, or in a garage or a host of other places... it's likely wrong in some way shape or form.

What you think about a CA checklist for NM and/or visible wiring practices Jeff? Pics of correct/incorrect EMT fittings and so on.. just the basics/common stuff. Most places we see sched 40 should be RMC and so on.

Just an idea.



Home Inspections in Palmdale Lancaster California

Tim Spargo
Spec Rite Inspections
Commercial and Residential Inspections
Palmdale Lancaster Santa Clarita CA
661-317-5770








Reply With Quote
  #11  
Old 4/25/11, 9:43 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Romex under patio eave...Question

What are you waiting for Tim? Get it started and I'll be happy to contribute



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 4/26/11, 5:10 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Romex under patio eave...Question

Our electricians here (as well as the courts) don't mind if it's unprotected as long as it's seven feet or above. If it's lower than that, they want it protected, usually in a raceway.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #13  
Old 4/26/11, 7:02 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex under patio eave...Question

Quote:
Originally Posted by rray View Post
Our electricians here (as well as the courts) don't mind if it's unprotected as long as it's seven feet or above. If it's lower than that, they want it protected, usually in a raceway.

What do the courts have to do with it?
Reply With Quote
Need a home inspection in Rhode Island? Check out InterNACHI's listing of Rhode Island certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 4/26/11, 10:50 AM
Russel Ray's Avatar
Russel Ray Russel Ray is offline
InterNACHI Member
 
Join Date: Mar 2003
Location: La Mesa, CA
Posts: 16,629
Default Re: Romex under patio eave...Question

Lawsuit that actually went to court rather than being settled out of court.



NACHI 2005 U.S. Member of the Year
Reply With Quote
  #15  
Old 4/26/11, 4:01 PM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: Romex under patio eave...Question

How about this arrangement?
Attached Thumbnails
romex-under-patio-eave-question-img_7894.jpg  




774 Manor Road
Staten Island, NY 10314
718-514-3393
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Is Romex in a crawl space a problem? jtedesco1 Electrical Inspections 48 9/30/06 10:53 PM
Rule of Thumb A/C sizing question from Practice Exam gliebig Inspecting HVAC Systems 9 5/25/06 1:38 AM
Answer to a common question about GFCI's jtedesco1 Electrical Inspections 4 1/12/06 9:29 PM


All times are GMT -4. The time now is 9:27 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts