#16
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hard to tell if the proper cable type or WP connector was used.
The PVC is acting as a sleeve either for protection or neatness or both. |
| Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#17
|
||||
|
||||
|
The NM must be rated for UV and damp/wet locations, or it's no good. Again, chances are slim to none that it is the proper type.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#18
|
||||
|
||||
|
Quote:
Is the fact that it's in a steel conduit an issue as well? 774 Manor Road Staten Island, NY 10314 718-514-3393 |
|
#19
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Steel conduit is permitted as a sleeve for NM cable.
|
|
#20
|
||||
|
||||
|
Robert, can you please clarify for me. I thought I saw that NM cannot be installed in a conduit. Thanks.
774 Manor Road Staten Island, NY 10314 718-514-3393 |
|
#21
|
||||
|
||||
|
Conduit can be used with NM for protection where it may be necessary, but as a general rule, NM should not be in conduit. However, as stated earlier, as long as the conduit-fill is not exceeded, it is not a prohibited practice.
IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#22
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
For conduit fill, NEC Chapter 9, Notes to the Tables #(9). This does not apply to short section of conduit used as a sleeve for protection of the cable. |
|
#23
|
||||
|
||||
|
Quote:
774 Manor Road Staten Island, NY 10314 718-514-3393 |
|
#24
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
There should have been a bushing or fitting on the end of the EMT to prevent abrasion of the cable sheath.
|
|
#25
|
||||
|
||||
|
Marcel Gratton, NACHI04011210, CMI On The Level Inspection Gatineau, Québec http://www.onthelevelinspection.com/ |
|
#26
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Good installation practices would require that, but you'd be hard pressed to find anything in any model code that requires that. If you called that out on an inspection report, I could make you look pretty foolish.
|
|
#27
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Marc, what about 300.15(C)?
|
|
#28
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
I agree with Jim, that applies to a peice of conduit used for physical protection of the cable. Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Is Romex in a crawl space a problem? | jtedesco1 | Electrical Inspections | 48 | 9/30/06 10:53 PM |
| Rule of Thumb A/C sizing question from Practice Exam | gliebig | Inspecting HVAC Systems | 9 | 5/25/06 1:38 AM |
| Answer to a common question about GFCI's | jtedesco1 | Electrical Inspections | 4 | 1/12/06 9:29 PM |