Default Re: Romex under patio eave...Question

Hard to tell if the proper cable type or WP connector was used.

The PVC is acting as a sleeve either for protection or neatness or both.
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #17  
Old 4/26/11, 4:20 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Romex under patio eave...Question

The NM must be rated for UV and damp/wet locations, or it's no good. Again, chances are slim to none that it is the proper type.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #18  
Old 4/26/11, 4:32 PM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: Romex under patio eave...Question

Quote:
Originally Posted by Jim Port View Post
Hard to tell if the proper cable type or WP connector was used.

The PVC is acting as a sleeve either for protection or neatness or both.
Its a steel conduit, not PVC.
Is the fact that it's in a steel conduit an issue as well?




774 Manor Road
Staten Island, NY 10314
718-514-3393
Reply With Quote
  #19  
Old 4/26/11, 4:39 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex under patio eave...Question

Quote:
Originally Posted by jgromkoski View Post
Its a steel conduit, not PVC.
Is the fact that it's in a steel conduit an issue as well?
Steel conduit is permitted as a sleeve for NM cable.
Reply With Quote
  #20  
Old 4/26/11, 5:02 PM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: Romex under patio eave...Question

Quote:
Originally Posted by Robert Meier View Post
Steel conduit is permitted as a sleeve for NM cable.
Robert, can you please clarify for me. I thought I saw that NM cannot be installed in a conduit. Thanks.




774 Manor Road
Staten Island, NY 10314
718-514-3393
Reply With Quote
  #21  
Old 4/26/11, 5:19 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Romex under patio eave...Question

Conduit can be used with NM for protection where it may be necessary, but as a general rule, NM should not be in conduit. However, as stated earlier, as long as the conduit-fill is not exceeded, it is not a prohibited practice.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #22  
Old 4/26/11, 5:56 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex under patio eave...Question

Quote:
Originally Posted by jgromkoski View Post
Robert, can you please clarify for me. I thought I saw that NM cannot be installed in a conduit. Thanks.
Actually it's required to be protected by conduit or other means when subject to physical damage. 334.15(B).

For conduit fill, NEC Chapter 9, Notes to the Tables #(9). This does not apply to short section of conduit used as a sleeve for protection of the cable.
Reply With Quote
  #23  
Old 4/26/11, 5:58 PM
John Gromkoski's Avatar
John Gromkoski John Gromkoski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Staten Island, NY
Posts: 608
Default Re: Romex under patio eave...Question

Quote:
Originally Posted by Robert Meier View Post
Actually it's required to be protected by conduit or other means when subject to physical damage. 334.15(B).

For conduit fill, NEC Chapter 9, Notes to the Tables #(9). This does not apply to short section of conduit used as a sleeve for protection of the cable.
Makes sense. Thanks.




774 Manor Road
Staten Island, NY 10314
718-514-3393
Reply With Quote
  #24  
Old 4/26/11, 6:18 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex under patio eave...Question

There should have been a bushing or fitting on the end of the EMT to prevent abrasion of the cable sheath.
Reply With Quote
  #25  
Old 4/26/11, 6:35 PM
Marcel Gratton's Avatar
Marcel Gratton Marcel Gratton is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Gatineau, QC
Posts: 1,778
Default Re: Romex under patio eave...Question

Good info at link below.

http://www.faqs.org/faqs/electrical-...section-5.html



Marcel Gratton, NACHI04011210, CMI
On The Level Inspection
Gatineau, Québec
http://www.onthelevelinspection.com/
Reply With Quote
  #26  
Old 4/28/11, 1:05 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex under patio eave...Question

Quote:
Originally Posted by Jim Port View Post
There should have been a bushing or fitting on the end of the EMT to prevent abrasion of the cable sheath.
Good installation practices would require that, but you'd be hard pressed to find anything in any model code that requires that. If you called that out on an inspection report, I could make you look pretty foolish.
Reply With Quote
  #27  
Old 4/28/11, 8:30 AM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex under patio eave...Question

Marc, what about 300.15(C)?
Reply With Quote
  #28  
Old 4/28/11, 8:55 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Romex under patio eave...Question

Quote:
Originally Posted by Jim Port View Post
Marc, what about 300.15(C)?

I agree with Jim, that applies to a peice of conduit used for physical protection of the cable.

Quote:
300.15 Boxes, Conduit Bodies, or Fittings — Where Required.
A box shall be installed at each outlet and switch point for concealed knob-and-tube wiring.
Fittings and connectors shall be used only with the specific wiring methods for which they are designed and listed.
Where the wiring method is conduit, tubing, Type AC cable, Type MC cable, Type MI cable, nonmetallic-sheathed cable, or other cables, a box or conduit body shall be installed at each conductor splice point, outlet point, switch point, junction point, termination point, or pull point, unless otherwise permitted in 300.15(A) through (M).
(A) Wiring Methods with Interior Access. A box or conduit body shall not be required for each splice, junction, switch, pull, termination, or outlet points in wiring methods with removable covers, such as wireways, multioutlet assemblies, auxiliary gutters, and surface raceways. The covers shall be accessible after installation.
(B) Equipment. An integral junction box or wiring compartment as part of approved equipment shall be permitted in lieu of a box.
(C) Protection. A box or conduit body shall not be required where cables enter or exit from conduit or tubing that is used to provide cable support or protection against physical damage. A fitting shall be provided on the end(s) of the conduit or tubing to protect the cable from abrasion.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Is Romex in a crawl space a problem? jtedesco1 Electrical Inspections 48 9/30/06 10:53 PM
Rule of Thumb A/C sizing question from Practice Exam gliebig Inspecting HVAC Systems 9 5/25/06 1:38 AM
Answer to a common question about GFCI's jtedesco1 Electrical Inspections 4 1/12/06 9:29 PM


All times are GMT -4. The time now is 9:27 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts