Okay guys! This is the deal. This restaurant has a safety switch service entrance with two 200 amp fuses and a 125 amp fuse. There are four, count them four, sub-panels coming off this safety switch. Two 150 amp sub-panels and two 100 amp sub-panels. Question is: Is this safety switch entrance enough for the four sub-panels? Also, should I recommend a evaluation by a licensed electrical contractor? Here are some photos.
Last edited by hmcbride; 6/30/07 at 7:31 AM.. |
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
In a commercial occupancy, it is quite common to have lots of panels hanging off what might seem like a small service. They do this to simply get more "spaces". Without doing a demand load calc, there's no way to know if the service size is adequate. If the fuses don't blow in the disco, that's one half-shod way to know.
I'm a bit concerned that the old Penetrox has heated run down all over the fuse holder terminal wipers and hardened. This can present a problem for reliable refusing of the disconnect, should it become necessary in the future. If this is a 3 phase service, they likely only have one 3phase panel and 3 single phase panels. This is my best guess, based on the fusing arrangement. Either that, or they've fused the neutral. Hard to say at first blush. |
|
#3
|
||||
|
||||
|
Yes, Marc it is a 3 phase service. As you see in the fourth picture there are two sub-panels located near the safety switch. There are two additional 100 amp sub-panels. The fifth picture is the panel to the right of the safety switch. This panel looks like a mess. I didn't see any double taps and the wiring appeared to be sized properly but there are multiple wire splices and I can't determine were they are all going. Shouldn't I just defer to a licensed electrician to evaluate this whole system just to play it safe.
|
|
#4
|
||||
|
||||
|
Harry,
I am with Marc on this one....In the 5th picture I simply can't determine the location of the "Grounded" conductor through all that mess. While it is a REACH the cross section wire requirements seem to be a mess here.....I would venture to say they exceed the minimums. I would not be against having this looked at....I would LOVE to dig into it personally and see if the remote panels are done properly and even do a load calc on it myself..... Now as marc said if this was a 200A service with 3 phase....and they sized down the one to a 125A fuse...I would say either someone did not do a load calc or they just guessed....in the 4th picture the center conductor is quite small compared to the others....typically in a 3 phase setup they are equally sized unless they know something on the count we dont. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#5
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Marc, do you really think it heated up and dripped. It looks to me to just be a messy job of slathering noalox on the fuse holders.
The reason for the smaller fuse is possibly becasue this is a delta service with a high leg and the center phase is not getting nearly the load of the other two. Why the smaller fuse? Who knows??? There is no reason for it. Maybe that is all they had at one time to replace a 200? |
|
#6
|
||||
|
||||
|
To do a commercial inspection I would have a sparkie on retainer and on the job with me to do that portion of the job while I occupied myself with all the other pressing issues. It would be worth whatever his hourly rates are just to have him or her there.
|
|
#7
|
|||
|
|||
|
Please Note:
Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Check out the lugs that have been installed...nice
I would bet that the 200 amp fuses replaced two other bad 125 amp fuses...look at the size of the conductors. Did I mention the lugs.... |
|
#8
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
You know what I find strange. Look in the third pic. The service condcutors do seem to be large enough for 200 amps, 3/0cu, but does the center condcutor look smaller?
|
|
#9
|
||||
|
||||
|
Quote:
just an old strange setup I guess Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
|
#10
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
If the high leg has a lower ampacity that should be reflected in the fuse size.
I agree in 3p center delta it is common to have a lot higher load on the center tapped (120/240) winding. That will be a bigger transformer. The high leg will only serve the 3p loads. If this is only using 2 transformers it is important not to connect any L/N load to the high leg. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Home Inspection IS NOT ABOUT SAFETY | jcahill | General Inspection Discussion | 39 | 2/26/07 12:08 AM |
| Handbook for Electrical Safety | pabernathy | Electrical | 1 | 1/1/07 2:14 PM |
| Square D Electrocution Hazard Safety Switch Recall | jtedesco1 | Misc. Discussion | 5 | 12/16/06 1:09 AM |
| Home Safety | jbushart | General Inspection Discussion | 0 | 10/23/06 8:17 PM |
| Electrical Safety Information | jtedesco1 | Electrical | 0 | 2/19/06 2:48 AM |