Default Safety Switch for Restaurant

Okay guys! This is the deal. This restaurant has a safety switch service entrance with two 200 amp fuses and a 125 amp fuse. There are four, count them four, sub-panels coming off this safety switch. Two 150 amp sub-panels and two 100 amp sub-panels. Question is: Is this safety switch entrance enough for the four sub-panels? Also, should I recommend a evaluation by a licensed electrical contractor? Here are some photos.

Last edited by hmcbride; 6/30/07 at 7:31 AM..
Reply With Quote
  #2  
Old 3/18/07, 2:26 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Safety Switch for Restaurant

In a commercial occupancy, it is quite common to have lots of panels hanging off what might seem like a small service. They do this to simply get more "spaces". Without doing a demand load calc, there's no way to know if the service size is adequate. If the fuses don't blow in the disco, that's one half-shod way to know.

I'm a bit concerned that the old Penetrox has heated run down all over the fuse holder terminal wipers and hardened. This can present a problem for reliable refusing of the disconnect, should it become necessary in the future.


If this is a 3 phase service, they likely only have one 3phase panel and 3 single phase panels. This is my best guess, based on the fusing arrangement. Either that, or they've fused the neutral. Hard to say at first blush.
Reply With Quote
  #3  
Old 3/18/07, 2:44 PM
Harry V. McBride, III's Avatar
Harry V. McBride, III Harry V. McBride, III is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Alachua, FL
Posts: 145
Default Re: Safety Switch for Restaurant

Yes, Marc it is a 3 phase service. As you see in the fourth picture there are two sub-panels located near the safety switch. There are two additional 100 amp sub-panels. The fifth picture is the panel to the right of the safety switch. This panel looks like a mess. I didn't see any double taps and the wiring appeared to be sized properly but there are multiple wire splices and I can't determine were they are all going. Shouldn't I just defer to a licensed electrician to evaluate this whole system just to play it safe.
Reply With Quote
  #4  
Old 3/18/07, 6:11 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Safety Switch for Restaurant

Harry,

I am with Marc on this one....In the 5th picture I simply can't determine the location of the "Grounded" conductor through all that mess. While it is a REACH the cross section wire requirements seem to be a mess here.....I would venture to say they exceed the minimums.

I would not be against having this looked at....I would LOVE to dig into it personally and see if the remote panels are done properly and even do a load calc on it myself.....

Now as marc said if this was a 200A service with 3 phase....and they sized down the one to a 125A fuse...I would say either someone did not do a load calc or they just guessed....in the 4th picture the center conductor is quite small compared to the others....typically in a 3 phase setup they are equally sized unless they know something on the count we dont.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 3/18/07, 7:25 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Safety Switch for Restaurant

Marc, do you really think it heated up and dripped. It looks to me to just be a messy job of slathering noalox on the fuse holders.

The reason for the smaller fuse is possibly becasue this is a delta service with a high leg and the center phase is not getting nearly the load of the other two.
Why the smaller fuse? Who knows??? There is no reason for it.
Maybe that is all they had at one time to replace a 200?
Reply With Quote
  #6  
Old 3/18/07, 10:06 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,516
Default Re: Safety Switch for Restaurant

To do a commercial inspection I would have a sparkie on retainer and on the job with me to do that portion of the job while I occupied myself with all the other pressing issues. It would be worth whatever his hourly rates are just to have him or her there.
Reply With Quote
  #7  
Old 3/18/07, 11:21 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Safety Switch for Restaurant

Check out the lugs that have been installed...nice

I would bet that the 200 amp fuses replaced two other bad 125 amp fuses...look at the size of the conductors.

Did I mention the lugs....
Reply With Quote
  #8  
Old 3/18/07, 11:52 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Safety Switch for Restaurant

You know what I find strange. Look in the third pic. The service condcutors do seem to be large enough for 200 amps, 3/0cu, but does the center condcutor look smaller?
Reply With Quote
  #9  
Old 3/19/07, 10:03 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Safety Switch for Restaurant

Quote:
Originally Posted by Speedy Petey
You know what I find strange. Look in the third pic. The service condcutors do seem to be large enough for 200 amps, 3/0cu, but does the center condcutor look smaller?
yeah....thats what i was talking about....unless they know something on the CALC side we don't it is usually strange even in a delta config to do this as you notice that most of the panels being used as 120/240 panels ....now we know that quite possibly the center could be the high leg and well...they are just not using it.........at all thus the smaller size......

just an old strange setup I guess



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 3/19/07, 1:04 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Safety Switch for Restaurant

If the high leg has a lower ampacity that should be reflected in the fuse size.
I agree in 3p center delta it is common to have a lot higher load on the center tapped (120/240) winding. That will be a bigger transformer. The high leg will only serve the 3p loads. If this is only using 2 transformers it is important not to connect any L/N load to the high leg.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Home Inspection IS NOT ABOUT SAFETY jcahill General Inspection Discussion 39 2/26/07 12:08 AM
Handbook for Electrical Safety pabernathy Electrical 1 1/1/07 2:14 PM
Square D Electrocution Hazard Safety Switch Recall jtedesco1 Misc. Discussion 5 12/16/06 1:09 AM
Home Safety jbushart General Inspection Discussion 0 10/23/06 8:17 PM
Electrical Safety Information jtedesco1 Electrical 0 2/19/06 2:48 AM


All times are GMT -4. The time now is 12:28 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts