Default Satellite Bond question

The local satellite dish company bonded its coaxial to a copper spigot on a house that is plumbed with CPVC. hmmmm

My question is, does this coaxial have to be bonded (it would be about a 30 ft run to the exterior panel/meter) or can it be grounded using a ground rod?
Attached Thumbnails
satellite-bond-question-picture-015-small-.jpg.jpg
Views:	45
Size:	45.2 KB
ID:	12502  



**************************************
Shawn Rowe, CMI
HomeFirst Inspection Services, LLC
- InfraRed Specialist (Level 1 & Building Science certified)
- Code Certified Residential Building Inspector
- Certified Master Inspector
-- Serving NE Florida, St. Johns, Duval, Flagler, Putnam counties --
Reply With Quote
  #2  
Old 6/21/07, 2:36 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 20,741
Default Re: Satellite Bond question

According to my son-in-law who installs Dish Network equipment, they are not allowed to mount the dish unless it can be bonded to the grounding system.
Reply With Quote
  #3  
Old 6/21/07, 2:36 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,431
Default Re: Satellite Bond question

It should be bonded and grounded. Proper bonding will create proper grounding as well (assuming the service is already properly grounded).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #4  
Old 6/21/07, 2:41 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,987
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Satellite Bond question

Why not remve the bonding wire from the spigot and run it to the panel and bond it there?
Reply With Quote
  #5  
Old 6/21/07, 3:28 PM
Shawn Rowe's Avatar
Shawn Rowe Shawn Rowe is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: St. Augustine, FL
Posts: 265
Default Re: Satellite Bond question

Quote:
Originally Posted by rwand1
Why not remve the bonding wire from the spigot and run it to the panel and bond it there?
They could, but it is about 30 ft away, they wanted some options beside burying the line or running it through the attic. .... you know, not too much work and gotta look pretty.

There is a gas line which isn't as far.



**************************************
Shawn Rowe, CMI
HomeFirst Inspection Services, LLC
- InfraRed Specialist (Level 1 & Building Science certified)
- Code Certified Residential Building Inspector
- Certified Master Inspector
-- Serving NE Florida, St. Johns, Duval, Flagler, Putnam counties --
Reply With Quote
  #6  
Old 6/21/07, 3:31 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,431
Default Re: Satellite Bond question

Quote:
Originally Posted by srowe
There is a gas line which isn't as far.
You can't use a gas line for grounding. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #7  
Old 6/21/07, 4:10 PM
Shawn Rowe's Avatar
Shawn Rowe Shawn Rowe is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: St. Augustine, FL
Posts: 265
Default Re: Satellite Bond question

The gas line is bonded to house grounding system. Can you not bond the coaxial to the bonded gas line?



**************************************
Shawn Rowe, CMI
HomeFirst Inspection Services, LLC
- InfraRed Specialist (Level 1 & Building Science certified)
- Code Certified Residential Building Inspector
- Certified Master Inspector
-- Serving NE Florida, St. Johns, Duval, Flagler, Putnam counties --
Reply With Quote
  #8  
Old 6/21/07, 4:11 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 476
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Satellite Bond question

810.21F) Electrode. The grounding conductor shall be connected as follows:
(1) To the nearest accessible location on the following:
a. The building or structure grounding electrode system as covered in 250.50
b. The grounded interior metal water piping systems, within 1.52 m (5 ft) from its point of entrance to the building, as covered in 250.52
c. The power service accessible means external to the building, as covered in 250.94
d. The metallic power service raceway
e. The service equipment enclosure, or
f. The grounding electrode conductor or the grounding electrode conductor metal enclosures; or
(2) If the building or structure served has no grounding means, as described in 810.21(F)(1), to any one of the individual electrodes described in 250.52; or
(3) If the building or structure served has no grounding means, as described in 810.21(F)(1) or (F)(2), to an effectively grounded metal structure or to any of the individual electrodes described in 250.52
Reply With Quote
  #9  
Old 6/21/07, 4:41 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,431
Default Re: Satellite Bond question

Quote:
Originally Posted by srowe
The gas line is bonded to house grounding system. Can you not bond the coaxial to the bonded gas line?
Nope.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #10  
Old 6/25/07, 12:41 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 4,389
Send a message via Yahoo to jfunderburk
Default Re: Satellite Bond question

Never look at them. My Agreement says this: "The following are specifically excluded from this inspection: Sewer lines and/or onsite waste disposal systems; water softeners; shower pans, over-flow drains, low voltage electrical systems; data and communications systems or other ancillary wiring that is not part of the primary electrical distribution system..."



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #11  
Old 7/2/07, 10:01 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,688
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Satellite Bond question

Just remember guys the main reason for this BOND is to decrease the potential from the electrical systems wiring to the dish setup system in case of a lightning strike or surge onto the system.

By creating a equal potential between the systems you decrease the lightnings DESIRE to arc horizontal to unequal potentials.

Thus the main reason we BOND these systems in accordance with Mike's post.



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
  #12  
Old 7/2/07, 12:11 PM
Michael D. Thomas Michael D. Thomas is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 642
Default Re: Satellite Bond question

Shawn,

See:

http://mikeholt.com/mojonewsarchive/...s~20020303.htm
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Interesting Question? jmckenna1 Misc. Discussion 9 11/25/07 1:13 PM
E&O vs. Performance Bond in PA byocum Misc. Discussion 3 5/30/06 10:39 PM


All times are GMT -4. The time now is 2:17 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts