Default Is this scorching an issue?

Inside of this very neatly organized panel today, I found a scorch mark. It appears that something arched between the bus bar (is that the right term) and the back of the panel. There is a small nick in the copper bar. Is this enough of an issue to refer an electrician to review, or just document and move on?

Any thoughts?
Attached Thumbnails
scorching-issue-img_3779a.jpg   scorching-issue-img_3778a.jpg  
Reply With Quote
  #2  
Old 2/6/07, 8:53 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,515
Default Re: Is this scorching an issue?

Quote:
Originally Posted by jschulte
Inside of this very neatly organized panel today, I found a scorch mark. It appears that something arched between the bus bar (is that the right term) and the back of the panel. There is a small nick in the copper bar. Is this enough of an issue to refer an electrician to review, or just document and move on?

Any thoughts?
Was there an outline of a body on the floor in front of the panel?
Reply With Quote
  #3  
Old 2/6/07, 8:55 PM
jschulte jschulte is offline
Active Poster
 
Join Date: Jul 2006
Location: Moberly, MO
Posts: 445
Please Note: jschulte is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this scorching an issue?

Quote:
Originally Posted by rnewland
Was there an outline of a body on the floor in front of the panel?
No. It was a high end home, though, they would have cleaned that up.
Reply With Quote
  #4  
Old 2/6/07, 9:06 PM
Russell J. Hensel Russell J. Hensel is offline
New User
 
Join Date: Sep 2004
Posts: 16
Please Note: Russell J. Hensel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this scorching an issue?

I would call it out. Anytime something like this is present I refer them to a licensed tradesman. What caused the arching? You don't know, but you can make a GUESS....let someone else GUESS....I like to tell people lets get clarification about this from an electrician, this way when you go to sell the house we will have all the facts for the next home inspector.

High end does not mean quality........just means price!
Reply With Quote
  #5  
Old 2/6/07, 9:41 PM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,090
Default Re: Is this scorching an issue?

Looks like someone with a screwdriver got a little careless.
Reply With Quote
  #6  
Old 2/6/07, 9:46 PM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,620
Default Re: Is this scorching an issue?

Been there done that and no I would not call it out .
Roy Cooke



Need help on inspection call my cell 613-827-2011

I like email Roycooke@hotmail.com

Never wrestle with a pig (however titled) as you just get dirty and the pig has all the fun.



Reply With Quote
  #7  
Old 2/6/07, 9:52 PM
Ted Allen Ted Allen is offline
InterNACHI Member
 
Join Date: Oct 2003
Posts: 3,090
Default Re: Is this scorching an issue?

Quote:
Originally Posted by rcooke
Been there done that and no I would not call it out .
Roy Cooke
I have screwdrivers that are now awls.
Reply With Quote
  #8  
Old 2/6/07, 9:53 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: Is this scorching an issue?

I wouldn't worry about it too much either.

I've left a few "signatures" like that in my time--how else would anyone know it was my work??



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #9  
Old 2/6/07, 10:05 PM
jschulte jschulte is offline
Active Poster
 
Join Date: Jul 2006
Location: Moberly, MO
Posts: 445
Please Note: jschulte is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this scorching an issue?

Quote:
Originally Posted by jwilliams4
I've left a few "signatures" like that in my time--how else would anyone know it was my work??
Is it like a prison tatoo, then?

Last edited by jschulte; 2/6/07 at 10:09 PM..
Reply With Quote
  #10  
Old 2/6/07, 10:07 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this scorching an issue?

I agree with the latter others. That was an unfortunate mistake for the installer and NO, that nic will NOT affect the buss bar.
Reply With Quote
  #11  
Old 2/6/07, 11:04 PM
apolillo's Avatar
apolillo apolillo is offline
Active Poster
 
Join Date: Nov 2004
Location: Baltimore, Md
Posts: 191
Please Note: apolillo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this scorching an issue?

I would write up the neutrals and grounds sharing termination screws.

anatol
Reply With Quote
  #12  
Old 2/6/07, 11:05 PM
jschulte jschulte is offline
Active Poster
 
Join Date: Jul 2006
Location: Moberly, MO
Posts: 445
Please Note: jschulte is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this scorching an issue?

Quote:
Originally Posted by apolillo
I would write up the neutrals and grounds sharing termination screws.

anatol
Thats how the electricians in the area do it.
Reply With Quote
  #13  
Old 2/6/07, 11:32 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Is this scorching an issue?

Pretty crummy looking weld
Reply With Quote
  #14  
Old 2/6/07, 11:48 PM
wsiegel wsiegel is online now
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this scorching an issue?

Are all those exposed wires on either side of the box. If they are, they need to be protected.
Reply With Quote
  #15  
Old 2/7/07, 8:07 AM
tneumann's Avatar
tneumann tneumann is offline
Active Poster
 
Join Date: Jan 2006
Location: Woodland Park, co
Posts: 2,060
Please Note: tneumann is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Is this scorching an issue?

Nice looking closeup photograph...care to share the settings on your camera and what type of camera that was?

TY
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Cutler-Hammer CH breaker issue Marc D. Shunk Electrical Inspections 4 5/27/07 2:04 PM
Robust views on issue of home inspectors wblakey Canadian Inspectors 0 11/24/06 5:49 PM


All times are GMT -4. The time now is 9:28 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts