What is the allowed maximum lenght of the SE cable after it enters the meter? I inspected a home where it came out of the meter and then wrapped around to the opposite side of the house before entering the home. At what point, if any, would it be required to be in metal conduit? Thanks.
Patrick Coulter Cross County Inspection Services, LLC (443) 266-7544
|
| Find an InterNACHI certified Montana Home Inspector (and anywhere else in North America) |
|
#2
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
The Code requires the cable inside to be "as short as practical". The length outside is unlimited.
Protection would only be required if it were deemed subject to physical damage. |
|
#3
|
|||
|
|||
|
Thanks, Jim. Appreciate the info!!
Patrick Coulter Cross County Inspection Services, LLC (443) 266-7544
|
|
#4
|
||||
|
||||
|
Lets also remember that "SER" is also SE Cable and if you have a service disconnection means in compliance with NEC 230.70(A)(1) then the SER being run within the dwelling has no real limit either. In your case, examine the cable for nicks, physical damage and poor securing and supporting and not as such on your report. Other than that it has been covered well by others.
Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Commercial Electrical Inspections | jtedesco1 | Commercial | 29 | 1/12/08 6:03 AM |
| Short circuit failures with 12/3 NM-B cable and NM clamp connectors | pabernathy | Electrical | 5 | 2/16/07 1:19 PM |
| Did you KNOW this about NM Cable? | pabernathy | Electrical | 0 | 12/19/06 9:46 AM |
| Hey Joe Tedesco | pbolliger | Electrical | 7 | 4/11/06 1:17 AM |
| Ceilings falling with wires in it. | jsmith3 | Interior | 8 | 3/16/06 8:24 PM |