Default SE Cable length??

What is the allowed maximum lenght of the SE cable after it enters the meter? I inspected a home where it came out of the meter and then wrapped around to the opposite side of the house before entering the home. At what point, if any, would it be required to be in metal conduit? Thanks.



Patrick Coulter
Cross County Inspection Services, LLC
(443) 266-7544
Reply With Quote
Find an InterNACHI certified Montana Home Inspector (and anywhere else in North America)
  #2  
Old 6/19/09, 3:53 PM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: SE Cable length??

The Code requires the cable inside to be "as short as practical". The length outside is unlimited.

Protection would only be required if it were deemed subject to physical damage.
Reply With Quote
  #3  
Old 6/19/09, 10:25 PM
Patrick Coulter Patrick Coulter is offline
InterNACHI Member
 
Join Date: Jun 2007
Location: Clarksville, MD
Posts: 180
Default Re: SE Cable length??

Thanks, Jim. Appreciate the info!!



Patrick Coulter
Cross County Inspection Services, LLC
(443) 266-7544
Reply With Quote
  #4  
Old 6/20/09, 10:53 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: SE Cable length??

Lets also remember that "SER" is also SE Cable and if you have a service disconnection means in compliance with NEC 230.70(A)(1) then the SER being run within the dwelling has no real limit either. In your case, examine the cable for nicks, physical damage and poor securing and supporting and not as such on your report. Other than that it has been covered well by others.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Commercial Electrical Inspections jtedesco1 Commercial 29 1/12/08 6:03 AM
Short circuit failures with 12/3 NM-B cable and NM clamp connectors pabernathy Electrical 5 2/16/07 1:19 PM
Did you KNOW this about NM Cable? pabernathy Electrical 0 12/19/06 9:46 AM
Hey Joe Tedesco pbolliger Electrical 7 4/11/06 1:17 AM
Ceilings falling with wires in it. jsmith3 Interior 8 3/16/06 8:24 PM


All times are GMT -4. The time now is 8:05 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts