  #1  
Old 3/26/10, 7:49 PM
Robert A. Jack Robert A. Jack is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Guilford, VT
Posts: 63
Default SE ot THHN?

Found this on a home yesterday. This was the SE from the meter to the service panel. Looks like THHN to me, not SE cable. any ideas? The wire gauge was 2gaw attached to a Murry 200 amp panel.
Attached Thumbnails
se-ot-thhn-p1180853r.jpg   se-ot-thhn-p1180854r.jpg   se-ot-thhn-p1180856r.jpg  
Reply With Quote
Need a home inspection in District Of Columbia? Check out InterNACHI's listing of District Of Columbia certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/26/10, 8:37 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: SE ot THHN?

From the middle photo it appears to be SE cable but I cannot make out the writing on the cable jacket. Do you have another photo showing the cable itself?
Reply With Quote
  #3  
Old 3/26/10, 8:59 PM
Robert A. Jack Robert A. Jack is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Guilford, VT
Posts: 63
Default Re: SE ot THHN?

The photo shows everything I could see. I was always lead to beleive SE cable should be wrapped with the ground conductor. In this cable the ground is just another conductor. This doesn't provide any contact protection for the primary voltage carring conductors.
Reply With Quote
  #4  
Old 3/26/10, 10:35 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: SE ot THHN?

So the EGC was bare in this cable? That would mean that the cable is likely NM cable (Romex) which comes in sizes up to #2 AWG. Is this cable coming straight from the meter enclosure? If so then there is probably a long list of NEC violations.
Reply With Quote
  #5  
Old 3/26/10, 11:06 PM
Robert A. Jack Robert A. Jack is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Guilford, VT
Posts: 63
Default Re: SE ot THHN?

The home was remodled and the meter was relocated. So, yes, the cable is run to the service meter.
Reply With Quote
  #6  
Old 3/27/10, 8:13 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,252
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: SE ot THHN?

Quote:
Originally Posted by rjack1 View Post
The home was remodled and the meter was relocated. So, yes, the cable is run to the service meter.
So if the cable is indeed NM cable you would have an NEC problem with #2 AWG NM only being rated for 95 amps (@60° C) and these two code sections:

Quote:
334.12 Uses Not Permitted.
(A) Types NM, NMC, and NMS. Types NM, NMC, and NMS cables shall not be permitted as follows:
(1) In any dwelling or structure not specifically permitted in 334.10(1), (2), and (3)
Exception: Type NM, NMC, and NMS cable shall be permitted in Type I and II construction when installed within raceways permitted to be installed in Type I and II construction.
(2) Exposed in dropped or suspended ceilings in other than one- and two-family and multifamily dwellings
(3) As service-entrance cable
Quote:
230.70 General.
Means shall be provided to disconnect all conductors in a building or other structure from the service-entrance conductors.
(A) Location. The service disconnecting means shall be installed in accordance with 230.70(A)(1), (A)(2), and (A)(3).
(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
How many #12 THHN allowed in 3/4" conduit jmerritt1 Electrical Inspections 13 3/2/09 4:50 PM