Here is the Installation manual. You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#17
|
|||
|
|||
|
The vast majority of lightning arrestors and surge protectors I see installed in panelboards are connected to one of the 240 volt breakers. Rarely do I see them at the main lugs or main breaker. Either way will protect the panel, although I can't imagine anything protecting the system from a healthy lightning strike!
Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties. Abraham Lincoln www.qualityhomeinspectionsfl.com |
|
#18
|
||||
|
||||
|
Quote:
The entire panel is protection by connecting to any one (240) breaker? Not just the circuit it is wired to? Also, I read the directions that Mike provided (thanks - I found brochures, but no instructions) and it says "connections to a branch circuit breaker that has terminals suitable for use with #14AWG wire..." So, is it possible to have this wired in the lugs of an unused breaker and still operate properly? Thanks Bruce Bruce Thompson Professional Inspector, Lic. #9199 Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area. www.TylerHomeInspector.com NACHI 06081394 |
|
#19
|
||||
|
||||
|
This is interesting.....From UL
Many people assume that surge suppressors can protect their home from lightning damage. Surge suppressors are not lightning protection devices - they cannot protect your home or your home's internal electrical wiring from a direct strike. Surge suppressors can, however, protect your equipment from voltage surges caused by unexpected occurrences such as a utility pole downed by a storm. Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#20
|
||||
|
||||
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Last edited by ccurrins; 2/19/08 at 4:36 PM.. |
|
#21
|
||||
|
||||
|
Quote:
|
|
#22
|
||||
|
||||
|
Quote:
|
|
#23
|
||||
|
||||
|
Quote:
WHERE'S PAUL?? WHERE'S MARC SHUNK? HELP!!! Bruce Thompson Professional Inspector, Lic. #9199 Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area. www.TylerHomeInspector.com NACHI 06081394 |
|
#24
|
||||
|
||||
|
They should be short to reduce inductive resistance.
tom |
|
#25
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The ones I have installed say they must be on the load side of a 240v breaker.
My main concern with the double tap is the size and type of the lead. I doubt the SqD and CH breakers are listed for a #10 solid and trhe smaller stranded you get on the protector. I had the slots so I put mine on a separate 20a double pole. |
|
#26
|
||||
|
||||
|
Quote:
You apparently CAN put this on an unused breaker by itself. Do I understand that correctly? Thanks, Bruce Bruce Thompson Professional Inspector, Lic. #9199 Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area. www.TylerHomeInspector.com NACHI 06081394 |
|
#27
|
||||
|
||||
|
Quote:
You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell |
|
#28
|
||||
|
||||
|
Quote:
Bruce Thompson Professional Inspector, Lic. #9199 Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area. www.TylerHomeInspector.com NACHI 06081394 |
|
#29
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
|
|
#30
|
|||
|
|||
|
From a purely engineering protection point-of-view it really doesn't matter where it is connected as long as the wires are kept relatively short (because of industance as mentioned above) and the device is connected to both busses (i.e. via the SE lugs or 2 pole breaker). Note that curling the long wires into a coil to keep them "short" would about the worst thing to do.
The main reason that the usual recommendation is to connect thorough a breaker is because often, when a surge arrestor does its job (or tries to), it typically fails at the same time and will need to be replaced. Most of the time I would expect it to fail "clear", thus the need to be able to see the light. If the failure mode is really severe, it will trip that breaker. A connection at the SE lugs would mean having to de-energize the entire panel, often with the assistance of the local utility. Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Secondary condensate ports | bking | Inspecting HVAC Systems | 16 | 9/14/06 6:29 PM |
| Lighting surge | lagudo | Electrical Inspections | 5 | 8/30/06 11:49 PM |
| Washer Secondary Drain | roconnor | Plumbing Inspections | 7 | 4/2/06 1:02 PM |