Default Re: Secondary Surge Arrester

Quote:
Originally Posted by dvalley
So in your case the lighting suppressor is only protecting the dryer circuit. And the suppressor itself should be mounted on the outside of the panel.
The device would be protecting more than just the dryer as it is across the bus when the breaker is in the on position.

Here is the Installation manual.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #17  
Old 2/19/08, 11:36 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: Secondary Surge Arrester

The vast majority of lightning arrestors and surge protectors I see installed in panelboards are connected to one of the 240 volt breakers. Rarely do I see them at the main lugs or main breaker. Either way will protect the panel, although I can't imagine anything protecting the system from a healthy lightning strike!



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #18  
Old 2/19/08, 3:50 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 586
Default Re: Secondary Surge Arrester

Quote:
Originally Posted by bwiley
The vast majority of lightning arrestors and surge protectors I see installed in panelboards are connected to one of the 240 volt breakers. Rarely do I see them at the main lugs or main breaker. Either way will protect the panel, although I can't imagine anything protecting the system from a healthy lightning strike!
So...going back to my conversation with the electric supply house person...

The entire panel is protection by connecting to any one (240) breaker? Not just the circuit it is wired to?

Also, I read the directions that Mike provided (thanks - I found brochures, but no instructions) and it says "connections to a branch circuit breaker that has terminals suitable for use with #14AWG wire..."

So, is it possible to have this wired in the lugs of an unused breaker and still operate properly?

Thanks
Bruce



Bruce Thompson
Professional Inspector, Lic. #9199
Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area.
www.TylerHomeInspector.com
NACHI 06081394
Reply With Quote
  #19  
Old 2/19/08, 4:26 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Secondary Surge Arrester

This is interesting.....From UL
Many people assume that surge suppressors can protect their home from lightning damage. Surge suppressors are not lightning protection devices - they cannot protect your home or your home's internal electrical wiring from a direct strike. Surge suppressors can, however, protect your equipment from voltage surges caused by unexpected occurrences such as a utility pole downed by a storm.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #20  
Old 2/19/08, 4:33 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Secondary Surge Arrester

AC Residential Surge Arrester
125/250Vac, single phase, 3-wire




Features

* Locknut and bushing furnished for simple mounting.
* Extra long 36" #12 THHN leads for ease of installation.
* Will pass a large number of high-energy surges and half-cycle spikes prior to failing.
* Always fails "clear" to permit continued use of power system.
* Non-conductive base to prevent a blown arrester from being a shock hazard.
* Will not produce carbon dust upon failing like some other arresters, preventing
damage to other equipment
* 4-1/4" high, 2-1/4" diameter
* PVC weatherproof case
* Locknut and washer furnished
* UL Recognized

Simple to install on outside of load center panel, or inside.








Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!

Last edited by ccurrins; 2/19/08 at 4:36 PM..
Reply With Quote
  #21  
Old 2/19/08, 5:56 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Secondary Surge Arrester

Quote:
Originally Posted by ccurrins

AC Residential Surge Arrester
125/250Vac, single phase, 3-wire




Features

* Locknut and bushing furnished for simple mounting.
* Extra long 36" #12 THHN leads for ease of installation.
* Will pass a large number of high-energy surges and half-cycle spikes prior to failing.
* Always fails "clear" to permit continued use of power system.
* Non-conductive base to prevent a blown arrester from being a shock hazard.
* Will not produce carbon dust upon failing like some other arresters, preventing
damage to other equipment
* 4-1/4" high, 2-1/4" diameter
* PVC weatherproof case
* Locknut and washer furnished
* UL Recognized

Simple to install on outside of load center panel, or inside.








Looks double tapped to me.
Reply With Quote
  #22  
Old 2/19/08, 5:57 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: Secondary Surge Arrester

Quote:
Originally Posted by bwiley
The vast majority of lightning arrestors and surge protectors I see installed in panelboards are connected to one of the 240 volt breakers. Rarely do I see them at the main lugs or main breaker. Either way will protect the panel, although I can't imagine anything protecting the system from a healthy lightning strike!
Must be a geographic thing. I've never seen them anywhere but the main...
Reply With Quote
  #23  
Old 2/19/08, 7:11 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 586
Default Re: Secondary Surge Arrester

Quote:
Originally Posted by ccurrins
Features

* Locknut and bushing furnished for simple mounting.
* Extra long 36" #12 THHN leads for ease of installation.
* Will pass a large number of high-energy surges and half-cycle spikes prior to failing.
* Always fails "clear" to permit continued use of power system.
* Non-conductive base to prevent a blown arrester from being a shock hazard.
* Will not produce carbon dust upon failing like some other arresters, preventing
damage to other equipment
* 4-1/4" high, 2-1/4" diameter
* PVC weatherproof case
* Locknut and washer furnished
* UL Recognized

Simple to install on outside of load center panel, or inside


Interesting...the Square D installation instructions say the wires should be short.

WHERE'S PAUL?? WHERE'S MARC SHUNK? HELP!!!



Bruce Thompson
Professional Inspector, Lic. #9199
Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area.
www.TylerHomeInspector.com
NACHI 06081394
Reply With Quote
  #24  
Old 2/19/08, 8:51 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Secondary Surge Arrester

They should be short to reduce inductive resistance.

tom
Reply With Quote
  #25  
Old 2/20/08, 1:41 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Secondary Surge Arrester

The ones I have installed say they must be on the load side of a 240v breaker.
My main concern with the double tap is the size and type of the lead. I doubt the SqD and CH breakers are listed for a #10 solid and trhe smaller stranded you get on the protector. I had the slots so I put mine on a separate 20a double pole.
Reply With Quote
  #26  
Old 2/20/08, 1:55 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 586
Default Re: Secondary Surge Arrester

Quote:
Originally Posted by Greg Fretwell
The ones I have installed say they must be on the load side of a 240v breaker.
My main concern with the double tap is the size and type of the lead. I doubt the SqD and CH breakers are listed for a #10 solid and trhe smaller stranded you get on the protector. I had the slots so I put mine on a separate 20a double pole.
Which answers my earlier question...

You apparently CAN put this on an unused breaker by itself. Do I understand that correctly?

Thanks,
Bruce



Bruce Thompson
Professional Inspector, Lic. #9199
Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area.
www.TylerHomeInspector.com
NACHI 06081394
Reply With Quote
  #27  
Old 2/20/08, 2:00 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Secondary Surge Arrester

Quote:
Originally Posted by bthompson1
Which answers my earlier question...

You apparently CAN put this on an unused breaker by itself. Do I understand that correctly?

Thanks,
Bruce
It would have to be a two pole breaker to be effective for both "hi" sides.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #28  
Old 2/20/08, 2:03 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 586
Default Re: Secondary Surge Arrester

Quote:
Originally Posted by mlarson
It would have to be a two pole breaker to be effective for both "hi" sides.
Right, sorry. Shoulda clarified.



Bruce Thompson
Professional Inspector, Lic. #9199
Serving Tyler, Lindale, Bullard, Whitehouse, Mineola and the surrounding East Texas area.
www.TylerHomeInspector.com
NACHI 06081394
Reply With Quote
  #29  
Old 2/20/08, 9:23 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Secondary Surge Arrester

Here's a site with various installation arrangements:

http://www.deltala.com/installa.htm
Reply With Quote
  #30  
Old 2/21/08, 11:07 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Secondary Surge Arrester

From a purely engineering protection point-of-view it really doesn't matter where it is connected as long as the wires are kept relatively short (because of industance as mentioned above) and the device is connected to both busses (i.e. via the SE lugs or 2 pole breaker). Note that curling the long wires into a coil to keep them "short" would about the worst thing to do.

The main reason that the usual recommendation is to connect thorough a breaker is because often, when a surge arrestor does its job (or tries to), it typically fails at the same time and will need to be replaced. Most of the time I would expect it to fail "clear", thus the need to be able to see the light. If the failure mode is really severe, it will trip that breaker. A connection at the SE lugs would mean having to de-energize the entire panel, often with the assistance of the local utility.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Secondary condensate ports bking Inspecting HVAC Systems 16 9/14/06 6:29 PM
Lighting surge lagudo Electrical Inspections 5 8/30/06 11:49 PM
Washer Secondary Drain roconnor Plumbing Inspections 7 4/2/06 1:02 PM


All times are GMT -4. The time now is 9:29 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts