Default Securing NM Cable 8 inches or 12 inches?

Is there a difference in method to secure NM cable depending on the type of outlet box is used? I thought there was a 12 inch rule but then I heard that if a non-conducting box is used that changes to 8 inches.
Attached Thumbnails
securing-non-metallic-cable-8-inches-12-inches-p1250747.jpg   securing-non-metallic-cable-8-inches-12-inches-p1250748.jpg  



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In

Last edited by gliebig; 3/25/11 at 1:14 PM.. Reason: Add Picture
Reply With Quote
Need a home inspection in Vermont? Check out InterNACHI's listing of Vermont certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 3/25/11, 10:50 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Securing NM Cable 8 inches or 12 inches?

I haven't heard that one Greg. I also follow the 12" rule.

I would be more concerned with the non-protected, incadescent lightbulb in a storage "closet".
Reply With Quote
  #3  
Old 3/25/11, 11:05 AM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Securing NM Cable 8 inches or 12 inches?

Hi Jeff, The "Closet" is actually an attic space with storage. I thought about that. There is no rule on protection of lights in attic spaces, but there is in "closets". This was in a knee wall storage area in a cape cod home. Had to crawl in for access. That's why I considered it as an attic.



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #4  
Old 3/25/11, 11:09 AM
Jeffrey R. Jonas's Avatar
Jeffrey R. Jonas Jeffrey R. Jonas is online now
InterNACHI Member
 
Join Date: Feb 2007
Location: Owatonna, MN
Posts: 12,195
Default Re: Securing NM Cable 8 inches or 12 inches?

Quote:
Originally Posted by gliebig View Post
Hi Jeff, The "Closet" is actually an attic space with storage. I thought about that. There is no rule on protection of lights in attic spaces, but there is in "closets". This was in a knee wall storage area in a cape cod home. Had to crawl in for access. That's why I considered it as an attic.
That is technically correct, but, we both know we can report based upon safety. I would consider that location more of a potential for hazard than a basic clothes closet. JMHO.

Hopefully someone has an answer to the 8"/12" question.
Reply With Quote
  #5  
Old 3/25/11, 12:14 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Securing NM Cable 8 inches or 12 inches?

Is this the exception you are referring to;

NEC 314.17(C) Exception: Where nonmetallic-sheathed cable or multiconductor Type UF cable is used with single gang boxes not larger than a nominal size 57 mm x 100 mm (2-1/4 in. x 4 in.) mounted in walls or ceilings, and where the cable is fastened within 200 mm (8 in.) of the box measured along the sheath and where the sheath extends through a cable knockout not less than 6 mm (1/4 in.), securing the cable to the box shall not be required. Multiple cable entries shall be permitted in a single cable knockout opening.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 3/25/11, 1:00 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Securing NM Cable 8 inches or 12 inches?

That must be it. So the way I interpret this applies to the way the cable is secured in the box which is something that we will not "see".

I am familiar with non-metallic boxes and most usually have a built-in "spring-type" clamping method that would prevent the cable from pulling loose anyway. So securing the cable(s) within 12 inches of the box is OK.

I have also seen non-metallic boxes that have a knock-out without any internal clamping method. In those cases, the cable needs to be secured within 8 inches of that style of non-metallic box.

I've attached some examples for help.
Attached Thumbnails
securing-non-metallic-cable-8-inches-12-inches-p1250807.jpg   securing-non-metallic-cable-8-inches-12-inches-p1250809.jpg   securing-non-metallic-cable-8-inches-12-inches-p1250810.jpg   securing-non-metallic-cable-8-inches-12-inches-p1250814.jpg   securing-non-metallic-cable-8-inches-12-inches-p1250748.jpg  




Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In

Last edited by gliebig; 3/25/11 at 1:12 PM..
Reply With Quote
  #7  
Old 3/25/11, 1:04 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Securing NM Cable 8 inches or 12 inches?

Good post Greg.



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #8  
Old 3/25/11, 2:51 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Securing NM Cable 8 inches or 12 inches?

Either way guys, the NM is not secured as required and the light will scorch teh OSB and may start a fire if left on too long IMHO.

Report it and move on.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #9  
Old 3/25/11, 3:57 PM
Gregory A. Liebig's Avatar
Gregory A. Liebig Gregory A. Liebig is offline
InterNACHI Member
 
Join Date: May 2006
Location: Sheboygan, WI
Posts: 687
Default Re: Securing NM Cable 8 inches or 12 inches?

Quote:
Originally Posted by mlarson View Post
Either way guys, the NM is not secured as required and the light will scorch teh OSB and may start a fire if left on too long IMHO.

Report it and move on.
Off Topic...but that's just another wonderful reason that 100 watt light bulbs are no longer being manufactured....



Greg Liebig, Owner
Sheboygan Wisconsin Home Inspector

4-Square Home Inspections, LLC
Where Knowledge will put your Mind at Ease ©
Sheboygan, WI 53081
(920) 451-4646

www.sheboyganhomeinspector.com
www.4squarehi.com
Like Us on Facebook
Follow Us on Linked-In
Reply With Quote
  #10  
Old 3/25/11, 4:25 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,343
Send a message via Yahoo to jfunderburk
Default Re: Securing NM Cable 8 inches or 12 inches?

I'm with Greg on the light. No code prohibits it and it's not a fire hazard. I'm an extremely thorough inspector, but when something's in question I often defer to the axiom "don't be a pinhead".



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Short circuit failures with 12/3 NM-B cable and NM clamp connectors pabernathy Electrical Inspections 10 4/17/11 1:43 PM
Commercial Electrical Inspections jtedesco1 Commercial Inspections 29 1/12/08 5:03 AM
Did you KNOW this about NM Cable? pabernathy Electrical Inspections 0 12/19/06 8:46 AM


All times are GMT -4. The time now is 9:29 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts