Give this image a look and see if YOU can find the problems in this image that is online.
http://www.nachi.org/gallery/thumbs/...-piping-3d.jpg Paul W. Abernathy |
| Need a home inspection in Massachusetts? Check out InterNACHI's listing of Massachusetts certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
No gas shut-off valve
No water shut-off valve Water heater not 18" off ground and gas line right in front of electric service Kisers Home Inspections http://www.inspectorpages.com/jkiser http://activerain.com/jimekiser http://www.kisershomeinspections.com |
|
#3
|
||||
|
||||
|
Might be worth mentioning that the term "gas pipe grounding" is dangerously wrong, although gas pipe bonding is required under most codes
Regards Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#4
|
|||
|
|||
|
No flue
|
|
#5
|
||||
|
||||
|
Correct Ed I was just going to edit my post to reflect that but you beat me to it
Gerry "To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future." (Mark B Adams) Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida. NACHI cell 484-429-5466 NACHI02121106 |
|
#6
|
||||
|
||||
|
Panel mounted to the gas pipe is funny
|
|
#7
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Looks like foreign systems in the workspace requirements of Article 110.
|
|
#8
|
|||
|
|||
|
Well...First the heading of the graphic is "Frightening" and "Incorrect"
You do not GROUND the gas line....You may Bond to it in accordance with NEC 250.104...but it has not been used for any grounding purposes since the 1965 NEC. The gas line is not actually running to the electrical panel, but it is indeed running in front of it which presents an issue with working space clearance as well and does create a safety concern...big time. Anyone see some others... Paul W. Abernathy |
|
#9
|
||||
|
||||
|
Paul... for the sake of discussion and education... would it be an issue if the gas line wasbehind the electrical panel?
Jeffrey R. Jonas Critical Eye Property Inspections JRJ Consultants Owatonna, Minnesota Chapter President InterNachi Awards Portal: http://co.nachi.org/inachiawards/
|
|
#10
|
||||
|
||||
|
Hot & cold water pipes are not bonded across the water heater
Chuck Evans (TREC #7657) Level III Infraspection Institute Certified Infrared Thermographer (#8402) HomeCert Houston Home Inspections & Thermal Inspections Find us on Facebook Houston Thermal Inspections & Infrared Imaging Find us on Facebook Houston Home Inspector Houston, TX |
|
#11
|
|||
|
|||
|
Sure...I always love me some education time....
well I still have a problem with the title of this graphic so i can't work my way around that bad taste. ( P.S. All graphics should be REVIEWED for accurancy before making them available to members..saves issues ) If the working space no longer becomes an issue and lets say it is not a dedicated equipment space issue then I fall back to NEC 250.104 and ask myself..."Self....is that gas line likely to become energized" and I would answer my self and say " Self...based on THIS image I would say it could on the premise of the location itself. So with that said NEC 250.104 kicks in....now lets look at NEC 250.104(B)...Now look at the code refence below and tell me does the connections shown ( assuming no electric ignition to the water heater with an EGC is provided since it is not shown ).....does it STILL comply if behind the panel? (B) Other Metal Piping. Where installed in or attached to a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or the one or more grounding electrodes used. The bonding jumper(s) shall be sized in accordance with 250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible. Paul W. Abernathy |
|
#12
|
|||
|
|||
|
Ok....let me be clear. I did not post this to RAG on images. I used it to present condition to which the title itself was incorrect and in doing so allow YOU the student ( myself included in that YOU ) to learn from the image. For all i know that was the actual intent of the image...
Paul W. Abernathy |
|
#13
|
||||
|
||||
|
Hi, Everyone --
Kate the Editor here... Thanks for all your input about this graphic. Our goal with all our courses and publications is to present accurate information (obviously), so please contact me or Nick directly via email (I'm at kate@internachi.org) if you find any problems so that we can address and rectify these issues as soon as possible. Nick & Crew have been out of town all week at the ICC Convention, and I just happened to check out this Forum discussion, which is something I actually rarely do because of my workload. We are in the process of re-printing our HVAC book in which this graphic appears, so the timing was great, but we almost didn't find out about it! We appreciate everyone's eagle eye and expertise -- that's the great thing about our members! -- and we encourage you to communicate with us directly about any inaccurate information you find anywhere on our site, especially in our online courses, or in our publications, in addition to using the Forum. Thanks! Kate |
| Need a home inspection in Massachusetts? Check out InterNACHI's listing of Massachusetts certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
|||
|
|||
|
Also the water line runs over the panel
|
|
#15
|
|||
|
|||
|
You cant tell that ed in an image like this..that would be assuming.
Kate.....You know me, I am always using something as an example to educate be it right or wrong. Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Am I doing something wrong here? | gmelien | Miscellaneous Discussion for Inspectors | 11 | 12/21/09 5:35 PM |
| Free Books And Articles For Electrical | jtedesco1 | Electrical Inspections | 14 | 1/6/08 6:45 PM |