The size of the main disconnect is 50 amps on the outside. There is a panel on the inside that appears to be 60 amps. Is this a problem for a 1800 sq ft house built in 1969 that has Central AC and Heat (Gas), water heater ( gas), electric stove and the occupant is only one person?
Thanks in advance for any replies and be nice. |
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
The smallest link in the chain... you havn't said much with regard to wire gauges and such, so with the information given so far it would be 50 amps.
|
|
#3
|
|||
|
|||
|
Please Note:
Harvey W. Kelly is a non-member guest and is in no way affiliated with InterNACHI or its members.
Sorry if I didn't make myself clear. What I was trying to get at is with the service amps today ranging from 100 to 200 amp in a modern home. Does older homes that still have the amperage rating at 50 amps, a concern that should be mentioned ?
|
|
#4
|
||||
|
||||
|
Quote:
James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 |
|
#5
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
About 7-8 years ago, I inspected a small house of 550-600 or so sq ft with a 15-20 year old 60 amp service and panel. I did a load calculation and found 60 amps met the code. I told the buyer that this may be an issue for insurance reasons.....the vendor had an an electrical inspector check it out......no problems......but 3 months later the house finally sold with a new 100 amp entrance. Check with insurers. Do any have a policy similar to those in Canada? If so, warn the purchaser.....it's outside of any SOP but still may be a fact of life and the customer deserves to know as much as possible. |
|
#6
|
||||
|
||||
|
"The service entrance amperage is estimated to be XX amps. Generally speaking, 100 amps is the minimum amperage necessary for today's modern homes. You should confirm the amperage prior to close of escrow and consult with a licensed electrician about the limitations of this size service."
“The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#7
|
||||
|
||||
|
Joe is exactly right! It should be mentioned...
"Be Proud of Your Home, Go With Pride!" 'Not just a Home Inspection, but an Education' Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties. |
|
#8
|
||||
|
||||
|
Seeing as the air-conditioner will likely use up to as much as 80% of the total capacity of the service, I would venture to say its undersized.
"Recommend the client sit in the dark and not watch television while the air-conditioning is running"! |
|
#9
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Don't get me wrong, just trying to help you CYA. |
|
#10
|
||||
|
||||
|
Quote:
Quote:
Although way beyond the scope of an inspection, that service may very well be overloaded on paper. Just for discussion ... taking 5,400 VA for general lighting/receptacles (3 VA/sf), 1,500 VA for general laundry, 3,000 VA for the kitchen (excluding stove), 8,000 VA for the stove (up to 12 kW stove), and say 6,000 VA to 7,000 VA for the central AC ... would add to around a 75A to 80A service load (even using the lower alt method for existing houses). If there was no central AC and a gas stove it might be a different story. JMO & 2-nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#11
|
||||
|
||||
|
I had an inspection the other day with a similar problem.
When you looked at the old snake skin service entrance cable, it appeared to look 60 amp. when I poped the cover the aluminum wire appeared to look like 100 amps. Confused, Any tips? A -MARK HOME INSPECTIONS, INC. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Difficult Chimneys | thance | Inspecting HVAC Systems | 2 | 1/29/08 8:16 PM |
| PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. | gromicko | Miscellaneous Discussion for Inspectors | 53 | 8/30/06 5:58 PM |
| Help Determining Reportable Service Size | cbarrows | Electrical Inspections | 8 | 7/19/06 7:12 PM |
| Electrical Inspection with Temp. Service? | dandersen | Electrical Inspections | 16 | 6/27/06 10:41 PM |