Default Service amperage

Round meter base.
100 amp main breaker.
Appears to be #2 or #4 SEC Aluminum.

How would you report the service amps for this home? 60 or 100A.

I say the meter base is 60A
The SEC is 70A

I would report this as a 60 amp service.
Attached Thumbnails
service-amperage-106907-006-small-.jpg.jpg
Views:	30
Size:	33.3 KB
ID:	15171   service-amperage-106907-007-small-.jpg.jpg
Views:	31
Size:	34.4 KB
ID:	15172   service-amperage-106907-025-small-.jpg.jpg
Views:	53
Size:	65.0 KB
ID:	15173   service-amperage-106907-024-small-.jpg.jpg
Views:	43
Size:	63.3 KB
ID:	15174  
Reply With Quote
  #2  
Old 10/14/07, 3:05 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 383
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service amperage

First of all the SEC's are copper and most likely #4. I tend to call these: "upgraded 60 amp services ." Most likely, because it is #4 copper, the 100amp panel will be ok, but I advise my buyer they should anticipate upgrading the service.
Reply With Quote
  #3  
Old 10/14/07, 3:22 PM
David C. Macy's Avatar
David C. Macy David C. Macy is online now
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,466
Default Re: Service amperage

Quote:
Originally Posted by cbuell
First of all the SEC's are copper and most likely #4. I tend to call these: "upgraded 60 amp services ." Most likely, because it is #4 copper, the 100amp panel will be ok, but I advise my buyer they should anticipate upgrading the service.
Are the SEC tin coated copper?
Reply With Quote
  #4  
Old 10/14/07, 3:29 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 383
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service amperage

Given the age of the wire they would would have to be (my mind keeps wanting to find an exception )
Reply With Quote
  #5  
Old 10/14/07, 4:20 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service amperage

If...
Quote:
Originally Posted by dmacy
Appears to be #2 or #4 SEC Aluminum.
Then why......
Quote:
Originally Posted by dmacy
The SEC is 70A

I would report this as a 60 amp service.
If you are not sure of the size how can you call it anything????



If it is #2AL or #4CU then it is indeed a 100A service.





Quote:
Originally Posted by cbuell
Most likely, because it is #4 copper, the 100amp panel will be ok, but I advise my buyer they should anticipate upgrading the service.
THIS is a perfect way to report it.
Reply With Quote
  #6  
Old 10/14/07, 6:10 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service amperage

Would just like to add that Paul Abernathy has told us in the past that the meter base is just a guide rather than a limitation.
And the Gauge is a limitation as is the Main Breaker,taking smaller of the two as the limitation.
If the gauge is not rated for 100 amps or better I would call that a defect.
Speedy is right about needing accuracy.
Reply With Quote
  #7  
Old 10/15/07, 1:19 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service amperage

Without knowing more about this house I would never say 100a was too small. "Fossil" appliances could make 100a overkill.
Reply With Quote
  #8  
Old 10/15/07, 1:51 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service amperage

Hi Greg..I should have clarified better as I was refering to the specific situation above ,as the Breaker is rated at 100 amps.
Though fossil appliances use more juice than newer more energy efficient models.
Reply With Quote
  #9  
Old 10/15/07, 1:59 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service amperage

Quote:
Originally Posted by relliott
Hi Greg..I should have clarified better as I was refering to the specific situation above ,as the Breaker is rated at 100 amps.
Though fossil appliances use more juice than newer more energy efficient models.
I think Greg meant fossil fuel burning major appliances, rather than those that run on electricity.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues 293 2/10/08 2:20 AM
Rating Service Amperage scosta Electrical 3 9/25/07 11:50 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 6:58 PM
Service Entrance Amperage? jfunderburk Electrical 18 6/16/06 11:16 PM


All times are GMT -4. The time now is 3:46 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts