Default Service box ground

Here is a picture of a neutral service entrance and earth grounding conductor bond at the service box/panel. What are the two big screws for on the neutral bus connector? Is there a bonding screw in this picture? The grounding equipment conductors are all attached to the back of the service panel.
Attached Thumbnails
service-box-ground-dsc01856.jpg   service-box-ground-dsc01857.jpg  
Reply With Quote
  #2  
Old 5/4/08, 8:42 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service box ground

I am not at all familiar with those panels, but it does seem the bond screw is missing. Maybe it goes in that empty hole right above the larger copper wire terminatedon the neutral bar?
Reply With Quote
  #3  
Old 5/5/08, 12:40 AM
Bruce Erny Bruce Erny is offline
New User
 
Join Date: Apr 2008
Location: SW Florida
Posts: 18
Please Note: Bruce Erny is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service box ground

The two large screws are holding the long neutral bar in place and attaching it to the neutral conductor just below them. The bonding screw should be just under the bar in the empty hole. If this is a sub panel, the screw should not be there. If it is a main breaker panel than somebody forgot to install the bonding screw (main bonding jumper)
Reply With Quote
  #4  
Old 5/5/08, 12:43 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Service box ground

Quote:
Originally Posted by Speedy Petey
I am not at all familiar with those panels,
That's because they manufacture FPE in the USA anymore. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 5/5/08, 1:42 AM
mnicholet's Avatar
mnicholet mnicholet is offline
Active Poster
 
Join Date: Mar 2008
Location: Vancouver Island, BC
Posts: 543
Please Note: mnicholet is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service box ground

Thanks for the information. This is a main service box/panel combo. With no bonding screw. Essentially, the grounding equipment conductors are an open circuit. Is the bonding screw typically located under the neutral bus connector bar?
Reply With Quote
  #6  
Old 5/5/08, 6:40 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service box ground

Quote:
Originally Posted by jpope
That's because they manufacture FPE in the USA anymore. . .
Yeah, I knew it was FPE (Canada). I just never saw one with the ground screws right in the back of the box like that. Interesting setup.
Reply With Quote
  #7  
Old 5/5/08, 9:04 AM
Bruce Erny Bruce Erny is offline
New User
 
Join Date: Apr 2008
Location: SW Florida
Posts: 18
Please Note: Bruce Erny is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service box ground

Quote:
Originally Posted by mnicholet
Thanks for the information. This is a main service box/panel combo. With no bonding screw. Essentially, the grounding equipment conductors are an open circuit. Is the bonding screw typically located under the neutral bus connector bar?
usually a screw thru the bar to the can or a strap from the bar to the can. If main panel it must be there.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Service panel bonding to ground abolt Electrical Inspections 22 12/18/07 2:47 PM
Looking for comments on this service ground wire connection cbuell Electrical Inspections 6 2/8/07 6:27 PM


All times are GMT -4. The time now is 9:30 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts