Default Service Cable?

Is there anyway this is acceptable?

Last edited by ccurrins; 4/20/09 at 1:47 AM..
Reply With Quote
  #2  
Old 1/10/09, 6:16 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Cable?

Quote:
Originally Posted by ccurrins View Post
Is there anyway this is acceptable?
What do you see wrong?

Deck ? to close? Not sure that is a problem.

It is not the feeder.

I go by this

1 If your electric meter will be
under it, the deck must be at
least 7 feet high.
2 There must be 36 inches of
unobstructed space in front of
the meter.
3 There must be a 36-inch
wide unobstructed travel path in
front of the meter.
4 There must be at least
2 inches of space on both sides
of the meter.
5 No structure may be built
around the meter, except for
approved meter rooms.
6 Doors or windows cannot be
within one foot of the meter.
7 Meters located inside fenced
areas must have gate access.
Reply With Quote
  #3  
Old 1/10/09, 6:16 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Cable?

Yes, or course. Why wouldn't it be? That looks identical to hundreds of thousands of services done in SE cable in the northeast.
Reply With Quote
  #4  
Old 1/10/09, 6:55 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Service Cable?

looks fine to me.....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 1/10/09, 6:58 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Cable?

Quote:
Originally Posted by relliott View Post
I go by this

1 If your electric meter will be
under it, the deck must be at
least 7 feet high.

2 There must be 36 inches of
unobstructed space in front of
the meter.

3 There must be a 36-inch
wide unobstructed travel path in
front of the meter.
4 There must be at least
2 inches of space on both sides
of the meter.

5 No structure may be built
around the meter, except for
approved meter rooms.
6 Doors or windows cannot be
within one foot of the meter.

7 Meters located inside fenced
areas must have gate access.
Curious where these requirements come from? Sounds like something off a cheat sheet.
Reply With Quote
  #6  
Old 1/10/09, 7:00 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Service Cable?

Agreed...I see alot of "MUST" terms in that check list. Robert is this derived from your local POCO ( as we in Virginia call the "Blue Book" ) or from some HI checklist?



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 1/10/09, 7:03 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Cable?

Quote:
Originally Posted by pabernathy View Post
Agreed...I see alot of "MUST" terms in that check list. Robert is this derived from your local POCO ( as we in Virginia call the "Blue Book" ) or from some HI checklist?
Not sure where I got it from.
Source is missing from my clips.

To answer Marc that may be related to cable enclosures and so forth.

At least we agree.
Reply With Quote
  #8  
Old 1/10/09, 7:06 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Cable?

The reason I asked is because only #3 (pretty much the same as #2) and #5 echo similar code requirements, I agree with #7 just because it's a good idea. The rest are just silly, which do nothing to enhance the safety of the installation.
Reply With Quote
  #9  
Old 1/10/09, 7:07 PM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: Service Cable?

Quote:
Originally Posted by pabernathy View Post
Agreed...I see alot of "MUST" terms in that check list.
and it's on this MB so it "MUST" be true



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good
Reply With Quote
  #10  
Old 1/10/09, 7:08 PM
David A. Andersen's Avatar
David A. Andersen David A. Andersen is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Woodlawn, TN
Posts: 3,703
Default Re: Service Cable?

Looks like the house I grew up in!

You guys have go to get over that every darn house you inspect does not need to comply with today's code.

It doesn't matter if you "don't like the looks of it"!

If you don't have an adverse condition associated with it, it's not in your hands...

Read your State HI law, or the SOP you prescribe to.

I have just made a report template that actually "IS" the HI law in print.
This is the basis to start the report, more is added depending on issues addressed by the state.

You can see this template at: http://www.midtninspections.com/TN_home_insp_report.htm



David A. Andersen & Associates
Clarksville - Nashville Home Inspector Lic#40
http://www.midtninspections.com
ITC Certified Level II Thermographer Cert#1958
Building Science Thermographer Cert#33784
http://www.thermalimagingscan.com
HVAC Certification EPA Cert#2046620

Link to my Website at: http://www.midtninspections.com/link-submission
Reply With Quote
  #11  
Old 1/10/09, 7:08 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Service Cable?

Quote:
Originally Posted by badair View Post
and it's on this MB so it "MUST" be true
lol....Oh yes...Indeed



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 1/10/09, 11:00 PM
ccurrins's Avatar
ccurrins ccurrins is offline
Active Poster
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 3,234
Please Note: ccurrins is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Cable?

Thanks for verifying what I already new regarding the SE cable, even though around here it is very rare. There was a "friend" with the agent that said it was "home owner rigged" and that all service entrance must be in conduit. I didn't feel like arguing at the time and it's great to know I have you guys to back me up.
Reply With Quote
  #13  
Old 1/11/09, 11:41 AM
Jim Port Jim Port is online now
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Cable?

Quote:
Originally Posted by ccurrins View Post
There was a "friend" with the agent that said it was "home owner rigged" and that all service entrance must be in conduit. .
The prohibition might be a local amendment or a POCO rule. As has been said it is in compliance with the NEC as a wiring method.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Service Cable -What should I use Ernest Harbaugh Electrical 6 11/8/08 1:09 PM
Commercial Electrical Inspections jtedesco1 Commercial 29 1/12/08 6:03 AM
Short circuit failures with 12/3 NM-B cable and NM clamp connectors pabernathy Electrical 5 2/16/07 1:19 PM
Did you KNOW this about NM Cable? pabernathy Electrical 0 12/19/06 9:46 AM


All times are GMT -4. The time now is 1:25 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts