The service conductors were #2 copper, the main panel and main breaker were rated at 100 amps, and the meter was rated at 200 amps. I don't see very many of the smaller round meter bases, so I thought I would get some confirmation from the pros on this BB. I believe that is a 60 amp rated meter base, which makes the service capacity 60 amps. Upgrading the meter base would make the service capacity 100 amps. Is that right?
Attached Thumbnails
service-capacity-p1230234.jpg  
Reply With Quote
  #2  
Old 11/27/06, 12:07 AM
jschulte jschulte is offline
Active Poster
 
Join Date: Jul 2006
Location: Moberly, MO
Posts: 445
Please Note: jschulte is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Capacity

Be careful. According to one of our local (very knowledgable) electricians, there were quite a few 100 AMP round meter bases produced. There are no obvious markings on the exterior of the base, though.

If the panel is 100 AMPs, I state that it is likely 100 AMPs, but there is a possibility that it is only 60 AMPs, they need an electrician to determine which if it is a concern.
Reply With Quote
  #3  
Old 11/27/06, 2:31 AM
Darrell B. Hadler's Avatar
Darrell B. Hadler Darrell B. Hadler is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Medicine Hat, AB
Posts: 371
Default Re: Service Capacity

I'd call that a 100 amp service...BUT I never even dreamt of checking the actual meter BASE? I know they are old and watch for wire protection and height requirements as we usually see upgrades are necessary or will be on their next reno project involving electrical work.

Learn something new every day...WOW



Darrell Hadler CMI
Five Star Home Inspections
Medicine Hat, AB. Canada
NACHI# 04111082 Cell phone# (403)502-3593
Inspected once . . . inspected right!
Reply With Quote
  #4  
Old 11/27/06, 1:59 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service Capacity

Paul,

Many times they increase the size of the conductors but that ends up being where they stop. You have to understand while the conductors have a capacity of 200A the limiting factor on the system is the lowest rated in the setup.

In this case if the OCPD is 100A and the Panel's rating is 100A......do not rely on the round meter can...back in the DAY they even approved round models for 100A .....so better to use the factors you know and that would be the Service Enclosure and OCPD....as the size.....



Paul W. Abernathy
Reply With Quote
  #5  
Old 11/27/06, 4:32 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Capacity

My house in Md also had a 200a service using the small square meter can. You really can't prove much by what a PoCo will allow.
Reply With Quote
  #6  
Old 11/27/06, 4:37 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service Capacity

No doubt Greg...While in some cases it can be a piece to the puzzle....the use of the meter can should never be the determining factor. With experience it can aid in your process but in older homes it just can aid in getting the HI confused.



Paul W. Abernathy
Reply With Quote
  #7  
Old 11/28/06, 6:47 PM
pdickerson pdickerson is offline
InterNACHI Member
 
Join Date: May 2004
Location: Clinton, WA
Posts: 341
Default Re: Service Capacity

Great info. Thanks Paul and Greg.
Reply With Quote
  #8  
Old 11/28/06, 9:52 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Capacity

The real issue with meter bases is not volume, it is wire bending space. They make the bigger ones so you can enter at the bottom and have enough room to loop into the top lugs of the meter base. If it is 4/0 or less and you go straight into (45 degree bend or less) "lay in" lugs you only need 4".
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
New Washington Legislation Submitted gdomagala Legislation, Licensing & Legal Issues for Inspectors 294 2/10/08 1:20 AM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Help Determining Reportable Service Size cbarrows Electrical Inspections 8 7/19/06 7:12 PM
Electrical Inspection with Temp. Service? dandersen Electrical Inspections 16 6/27/06 10:41 PM


All times are GMT -4. The time now is 4:17 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts