service drop comes in at a pole outside the home then underground... enters the home below ground... here is the part i am questioning... the wire once inside the home does not have the outer insulation covering, conduit.. nothing... it travels 20-25 feet along the outer rim joist before entering the panel as 4 independent wires. I could not get a good picture but here is what i have... thanks to all the sparkies in advance... jeff Jeff Campbell Campbell Property Inspections http://www.maineshomeinspector.com Pittston, Maine NACHI04013010 Last edited by jcampbell; 3/26/08 at 7:23 PM.. Reason: clarify |
|
#2
|
||||
|
||||
|
Jeff,
There should be a jacket on the 4 cables all the way up the the service panel. Are those branch wires stapled to within 12 inches of the panel? |
|
#3
|
||||
|
||||
|
that is what i was thinking david...
to within 12" of ? eachother? Jeff Campbell Campbell Property Inspections http://www.maineshomeinspector.com Pittston, Maine NACHI04013010 |
|
#4
|
||||
|
||||
|
Quote:
|
|
#5
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yeah, that's wrong as can be, and one of the most hazardous electrical pictures I've seen posed on the NACHI board in quite a while. Not only do individual conductors need to be contained in a raceway, but those conductors are called "URD" and aren't even an NEC conductor type approved for interior wiring. In short, even if you put those conductors in a raceway as they need to be, the conductors themselves are the wrong type. That whole feeder situation needs completely redone.
|
|
#6
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Marc, aren't these also the same insulation as USE? If so it is a smoke and flame issue. I also have problem with service conductors going any significant distance inside a home, no matter what the wiring method is.
I am on the side of the most strict intrepretation of 230.70(A)(1) Quote:
|
|
#7
|
||||
|
||||
|
thanks marc...
you know when you see something like this you just know it is wrong... jeff Jeff Campbell Campbell Property Inspections http://www.maineshomeinspector.com Pittston, Maine NACHI04013010 |
|
#8
|
||||
|
||||
|
I think we had an inexperience electrician working here... although the work was clean... there are issues...
in addition to this... NO GFCI in first floor bath... NO AFCI's in any bedrooms (2006-07 construction) multiple neutral and grounds entwined together under one lug Does anyone have any good verbage for lacking AFCI in a home... ? If so please post... thanks... going to search the BB now... Jeff Campbell Campbell Property Inspections http://www.maineshomeinspector.com Pittston, Maine NACHI04013010 |
|
#9
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
|
|
#10
|
||||
|
||||
|
Great Fact Sheet Joe... thanks...
Jeff Campbell Campbell Property Inspections http://www.maineshomeinspector.com Pittston, Maine NACHI04013010 |
|
#11
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The thing you can't emphasize enough is that there is no over current protection on service conductors and no practical way to disconnect them in a faulted condition. I would hit that harder on my report.
If you get a fault you will burn the insulation off that "20-25" feet of wire and if URD is like USE (direct burial service conductor wire) the products of combustion of this insulation are unsafe ... not to mention the fire itself. I am usually not the nervous Nelly here but 25' of unprotected service cable scares the hell out of me, particularly when it is not even a wiring method listed for use inside. The only real fix is an outside disconnect and replacing the wire inside. (4 wire SER, separate neutral and ground in the panel). The lack of AFCIs pales in comparison. IMHO |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| What do you think? Can this work for you? | jtedesco1 | Electrical | 13 | 2/9/09 11:58 PM |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical | 6 | 9/15/08 8:57 AM |
| Where is it written.... | bgromicko | General Inspection Discussion | 18 | 1/19/08 10:02 PM |
| Metal Rigid or PVC Rigid what is code | bpotts | Electrical | 5 | 12/4/06 3:40 PM |