Default Service Drop and Federal Electric Panel

I'm going to go ahead and post this again, even though I can't seem to figure out how to load my images. (Must be dumb as mud!)

First issue. The service drop lines attach near the corner of a house on the left side. Then they wrap around the corner over to the right side where they make the splice to the service entrance conductor. The drop lines are in contact with the corner of the house. My inclination is that this makes them susceptable to wear from any movement from wind? Agreed?

Second issue. Same house has a Federal Electric Products service panel, from Newark. New Jersey. Label doesn't say Federal Pacific, but after looking at pictures of Federal Pacific panels on line, this panel looks very similar, but not identical to any I've seen. It very old, and may predate Federal Pacific. Other than being old and crowded, didn't discern any specific issues with it. Does anybody have any info about Federal Electric or any other thoughts about this?



Mark
MD HI Lic # 30090
PA DEP Radon Cert # 2457
Certified Home Energy Tune-uP Inspector

Last edited by mlong; 1/28/06 at 10:37 AM.. Reason: Can't load my images. I'll get back tomorrow.
Reply With Quote
  #2  
Old 1/27/06, 9:09 PM
Mark R. Long Mark R. Long is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Thurmont, MD
Posts: 320
Default Re: Service Drop and Panel Questions

Cancel



Mark
MD HI Lic # 30090
PA DEP Radon Cert # 2457
Certified Home Energy Tune-uP Inspector

Last edited by mlong; 1/27/06 at 9:18 PM..
Reply With Quote
  #3  
Old 1/28/06, 8:15 AM
lewens's Avatar
lewens lewens is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Brantford, On
Posts: 778
Send a message via AIM to lewens
Default Re: Service Drop and Panel Questions

Bump



Larry Ewens
1578 Colborne St
Brantford On
Nachi ID #05022485
Just my usual 12.5 cents


http://acissbrant.blogspot.com/

Reply With Quote
  #4  
Old 1/28/06, 8:56 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 6,350
Default Re: Service Drop and Panel Questions

Quote:
Originally Posted by lewens
Bump
Reply With Quote
  #5  
Old 1/28/06, 10:42 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,441
Default Re: Service Drop and Panel Questions

http://www.inspect-ny.com/fpe/fpepanel.htm



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #6  
Old 1/28/06, 1:09 PM
Mark R. Long Mark R. Long is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Thurmont, MD
Posts: 320
Default Re: Service Drop and Panel Questions

Thanks, Jeff. I have in fact looked at that link. My quandary is that my panel does look very similar to the pictures on that site, but not exactly. There's nothing that I can see that matches my panel. My panel for the most part looks older than the samples shown, plus my panel reads Federal Electric Products, not Federal Pacific Electric.

I may just recommend further evaluation and possible upgrade just because of the age. I'm also thinking of taking another look at this panel, just to make sure I didn't miss anything.



Mark
MD HI Lic # 30090
PA DEP Radon Cert # 2457
Certified Home Energy Tune-uP Inspector
Reply With Quote
  #7  
Old 1/28/06, 2:37 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,441
Default Re: Service Drop and Panel Questions

If you like, you can email me the pictures and I'll upload them for you.

Don't worry about size, I have a T-1 connection.

InspectorJeff@sbcglobal.net



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #8  
Old 1/28/06, 2:37 PM
jmichalski's Avatar
jmichalski jmichalski is offline
Active Poster
 
Join Date: Aug 2004
Location: Souderton, PA
Posts: 2,572
Please Note: jmichalski is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Service Drop and Panel Questions

They are one and the same....

See:
http://www.codecheck.com/pdf/electri...%20Nov2003.pdf
Reply With Quote
  #9  
Old 1/28/06, 5:20 PM
Mark R. Long Mark R. Long is offline
InterNACHI Member
 
Join Date: Mar 2004
Location: Thurmont, MD
Posts: 320
Default Re: Service Drop and Panel Questions

Thanks Joe. This confirmed my assumption that Federal Electric was the company's name before Federal Pacific. I'm going to use my standard verbage for Federal Pacific panels.

Also, I went back to look at this panel without the realtor and client talking in my ear, and took more time. This panel was so packed with wires, that I actually missed some loose non-terminated wires, plus a double tap. Not good on my part. Need to take a deep breath and focus sometimes. But my suspicions were aroused after I was looking at my photos back at my office. At least I don't mind biting the bullet and re-checking myself, just don't want to make a habit of it.

Thanks for the offer Jeff of uploading the pictures, but I think that I have it under control now.



Mark
MD HI Lic # 30090
PA DEP Radon Cert # 2457
Certified Home Energy Tune-uP Inspector
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical Safety Foundation International Links jtedesco1 Electrical 5 12/8/07 3:10 PM
Electricians Check List pabernathy Electrical 74 12/5/07 6:39 PM
Parallel 200 amp panel questions ccarrington Electrical 4 9/22/07 4:38 PM
Panel Inspection Safety roconnor Electrical 10 9/24/06 9:02 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Misc. Discussion 53 8/30/06 5:58 PM


All times are GMT -4. The time now is 5:39 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts