Default Service Drop & SEC Clearance Requirements

Is there a requirement for clearance over stairs and doorway landing? (I know about the 10ft requirement for balcony/decks and yards, but I can not find any for stairs and doorway landing.

Peter
Attached Thumbnails
service-drop-and-sec-clearance-requirements-100_4304-small-.jpg.JPG
Views:	150
Size:	35.0 KB
ID:	28079  
Reply With Quote
Find an InterNACHI certified New Jersey Home Inspector (and anywhere else in North America)
  #2  
Old 4/19/09, 10:53 AM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Service Drop & SEC Clearance Requirements

Someone can reach up and grab it which makes it a safety hazard. A walkway/balcony needs 10' clearance...my thoughts.



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #3  
Old 4/19/09, 10:55 AM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 546
Default Re: Service Drop & SEC Clearance Requirements

That's my opinion too.
Peter
Reply With Quote
  #4  
Old 4/19/09, 11:25 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Service Drop & SEC Clearance Requirements

(B) Vertical Clearance.
The vertical clearance of final
spans above, or within 900 mm (3 ft) measured horizontally
of, platforms, projections, or surfaces from which they
might be reached shall be maintained in accordance with
230.24(B).

230.9 Clearances on Buildings.
Service conductors and
final spans shall comply with 230.9(A), (B), and (C).

(A) Clearances.
Service conductors installed as open conductors
or multiconductor cable without an overall outer
jacket shall have a clearance of not less than 900 mm (3 ft)
from windows that are designed to be opened, doors,
porches, balconies, ladders, stairs, fire escapes, or similar
locations.

Exception: Conductors run above the top level of a window
shall be permitted to be less than the 900-mm (3-ft)
requirement.



Paul W. Abernathy
Reply With Quote
  #5  
Old 4/19/09, 6:28 PM
Peter W. Bennett Peter W. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Little Silver, NJ
Posts: 546
Default Re: Service Drop & SEC Clearance Requirements

Thanks Paul, just what I needed.
Peter
Reply With Quote
  #6  
Old 4/20/09, 6:48 PM
Humberto Carvajal's Avatar
Humberto Carvajal Humberto Carvajal is offline
InterNACHI Member
 
Join Date: May 2005
Location: Homestead, FL
Posts: 819
Default Re: Service Drop & SEC Clearance Requirements

Although Paul answered it very eloquently, here is an attached PDF file to keep handy.

Regards,
Attached Files
File Type: pdf Service Drop Clearances.pdf (72.6 KB, 173 views)





Humberto Carvajal Jr.
Florida State Property Inspections, LLC
Florida Home Inspector License# HI884
LEEDŽ Accredited Professional
Member USGBC South Florida Chapter

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Florida Licensing Bill - Action Soon jburkeson1 Legislation, Licensing & Legal Issues for Inspectors 250 7/1/10 4:50 PM
Service ground requirements? kcabral Electrical Inspections 2 1/22/09 8:14 PM
Larger wires at service drop mtimpani Electrical Inspections 33 1/19/09 8:35 AM
Service Drop Q alarsen1 Electrical Inspections 11 2/25/07 9:45 AM
Service Drop and SEC jpope Electrical Inspections 11 1/14/06 11:15 PM


All times are GMT -4. The time now is 8:24 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts