Default service drop clearance

Sorry for the poor photo but I was wondering about any clearance issues involving this drop attachment which is clearly within reach of the back upper deck area.
Is it still the 3 foot rule as relates to windows or something else.?service-drop-clearance-servicedropattachment.jpg
Reply With Quote
  #2  
Old 5/30/07, 7:08 PM
Scott Schultz Scott Schultz is offline
Active Poster
 
Join Date: Sep 2006
Location: Surprise, AZ
Posts: 216
Please Note: Scott Schultz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: service drop clearance

a child, or anyone for that matter, can just reach through or over the railing and grab those wires. No way is that good. At least that's how I am interpreting that from the pic. What was that setup like? Why would they run the service wires along the side of the house? I assume the deck was put there afterwards but still wondering why the wires weren't ran over the roof?
Reply With Quote
  #3  
Old 5/30/07, 7:14 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: service drop clearance

IMO that would fall under 225.19(D)(2) which states the same clearance must be met in 225.18. They treat that deck the same as ground level.

This would be 10' from that platform.
Reply With Quote
  #4  
Old 5/30/07, 7:15 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: service drop clearance

Also, the porcelain spool is missing from the point of attachment.
Reply With Quote
  #5  
Old 5/30/07, 7:26 PM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: service drop clearance

Thanks ..this is a new back porch ,with know way to meet 10 foot clearance requirements,however I have noticed other buildings in the area do protect by blocking the questioned area.Remember this is the city where we jam everything together.It is only a condo inspection but will include this.
Reply With Quote
  #6  
Old 5/30/07, 7:31 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: service drop clearance

Quote:
Originally Posted by Speedy Petey
Also, the porcelain spool is missing from the point of attachment.
Indeed. That particular attachment insulator is often called either a "fork bolt" or a "one-point rack". This is how they're supposed to look:

Reply With Quote
  #7  
Old 5/31/07, 12:09 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: service drop clearance

If this is below the deck it is 3' from the edge of the deck.
Reply With Quote
  #8  
Old 5/31/07, 1:42 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,567
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: service drop clearance

I would say that cable attachment is 6 inches from the top of the handrail.
Not 3 feet as you may be seeing the photo wrong.
Reply With Quote
  #9  
Old 5/31/07, 10:59 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: service drop clearance

I think what Greg is saying Robert is it "HAS" to be 3' from the edge of the deck and it is not....so he is just bringing attention to that fact is all.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #10  
Old 5/31/07, 11:09 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: service drop clearance

3' horizontal(if they can't go out, then up requires 10 feet up[from even top of rail I believe, have to check again]). Or made such that unreachable. I've seen permanent lattice walls installed to meet requirements.

The older houses I help refurbish, originally allowed for row houses to get service feeds across other peoples properties. This meant houses could be feed on an angle. Today, only your property can be crossed, so we've 'walled' sides of patios to 'fix' things.

tom
Reply With Quote
  #11  
Old 5/31/07, 11:20 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,684
Default Re: service drop clearance

Robert,

That installation is a definite RED FLAG.

If I can touch it, it gets written up...Period

If you're looking for minimum clearances of the SE, it's 3-feet.

"Click to Enlarge"
Attachment 11959
Attachment 11960

Last edited by dvalley; 10/7/07 at 5:40 PM..
Reply With Quote
  #12  
Old 5/31/07, 11:26 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: service drop clearance

David,

Interesting you should bring that up because I have been preaching in semianars for some time now that use this example...

If the Service Drop is over the window...above it then the NEC is ok with it....However in my opinion if the top portion of the window opens or swings down then it indeed becomes a situation where it could be reached....

So while the minimum safety standards of the NEC apply in most all cases, in this case it is a more enhanced safety situation to call out a service entrance drop that lets say is above a window...and allowed by the NEC ....BUT could be reached by the consumer if the top portion of the window is down....now if the top is fixed...no worries...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #13  
Old 5/31/07, 2:33 PM
jkogel jkogel is offline
Active Poster
 
Join Date: Jan 2007
Location: Sooke, BC
Posts: 699
Please Note: jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: service drop clearance

[quote=Marc D. Shunk]Indeed. That particular attachment insulator is often called either a "fork bolt" or a "one-point rack". This is how they're supposed to look:


"Emily knobs".
Reply With Quote
  #14  
Old 5/31/07, 4:09 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: service drop clearance

Emily's what?!
Reply With Quote
  #15  
Old 5/31/07, 7:41 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: service drop clearance

ok..lets not gripe about Emily now....Emily can do who she wishes...



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Service Drop Dropped While at Inspection!! mlong Electrical Inspections 9 10/20/07 7:20 AM
Service Drop Q alarsen1 Electrical Inspections 11 2/25/07 10:45 AM
Service Drop Clearance Over Roof mlong Electrical Inspections 6 12/19/06 8:39 AM
Service panel clearance wwarner Electrical Inspections 13 8/12/06 1:07 PM
Service Drop Run Over Balcony? jtedesco1 Electrical Inspections 0 5/31/06 6:23 AM


All times are GMT -4. The time now is 1:40 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts