Am I correct that this service drop is too close to the house roof? (I realize that the pictures aren't showing this very well).
The service drop comes in over an addition and at the closest point, clears the roof by about 10". It continues over the addition, approximately 12' in length, until it gets to the mast. At that point it is clearing the roof by about 24". Mark MD HI Lic # 30090 BPI Certified Building Analyst PA DEP Radon Cert # 2457 Certified Home Energy Tune-uP Inspector
|
|
#2
|
|||
|
|||
|
230.24 Clearances. Service-drop conductors shall not be readily accessible and shall comply with 230.24(A) through (D) for services not over 600 volts, nominal. (A) Above Roofs. Conductors shall have a vertical clearance of not less than 2.5 m (8 ft) above the roof surface. The vertical clearance above the roof level shall be maintained for a distance of not less than 900 mm (3 ft) in all directions from the edge of the roof. Exception No. 1: The area above a roof surface subject to pedestrian or vehicular traff ýc shall have a vertical clearance from the roof surface in accordance with the clearance requirements of 230.24(B). Exception No. 2: Where the voltage between conductors does not exceed 300 and the roof has a slope of 100 mm (4 in.) in 300 mm (12 in.), or greater, a reduction in clearance to 900 mm (3 ft) shall be permitted. Exception No. 3: Where the voltage between conductors does not exceed 300, a reduction in clearance above only the overhanging portion of the roof to not less than 450 mm (18 in.) shall be permitted if (1) not more than 1.8 m (6 ft) of service-drop conductors, 1.2 m (4 ft) horizontally, pass above the roof overhang, and (2) they are terminated at a through-the-roof raceway or approved support. FPN: See 230.28 for mast supports. Exception No. 4: The requirement for maintaining the vertical clearance 900 mm (3 ft) from the edge of the roof shall not apply to the final conductor span where the service drop is attached to the side of a building. Paul W. Abernathy |
|
#3
|
||||
|
||||
|
Thanks Paul! So if I understand you correctly, what you are saying is that I should quit being such a lazy dumb--s and read the damn book myself!
Mark MD HI Lic # 30090 BPI Certified Building Analyst PA DEP Radon Cert # 2457 Certified Home Energy Tune-uP Inspector
|
|
#4
|
|||
|
|||
|
Nope...I am saying......since it is easier to understand the NEC than my garbled messages...I would just post the code and the answer is within.
The vertical clearance above the roof level shall be maintained for a distance of not less than 900 mm (3 ft) in all directions from the edge of the roof. Exception No. 4: The requirement for maintaining the vertical
clearance 900 mm (3 ft) from the edge of the roof shall not apply to the final conductor span where the service drop is attached to the side of a building. Paul W. Abernathy |
|
#5
|
|||
|
|||
|
If the clearance is over the house portion and the pitch is less than 4/12...AND if we are not talking about an overhang....meaning the service drop you are speaking of runs right across an open roof.....it is wrong.
If we are talking about it just going over a small corner of it and the roof has a pitch that is as steep as a 4/12 or more.....It can be reduced.....likely no one would get near it to be involved with it. Ok....How close is your MAST from he edge of the house Mark? Would THIS apply to your example...I really can't tell from the images Exception No. 3: Where the voltage between conductors does not exceed 300, a reduction in clearance above only the overhanging portion of the roof to not less than 450 mm (18 in.) shall be permitted if (1) not more than 1.8 m (6 ft) of service-drop conductors, 1.2 m (4 ft) horizontally, pass above the roof overhang, and (2) they are terminated at a through-the-roof raceway or approved support. Paul W. Abernathy Last edited by pabernathy; 12/18/06 at 9:32 PM.. |
|
#6
|
|||
|
|||
|
Please Note:
Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Service drop conductors over roof, roof overhangs and separate structures on the same property seem to be "missed" during inspection processes. This is not just an NEC code, but also an NESC (utility) code as well. I have taken many photos of just what you have and many others as well.
|
|
#7
|
||||
|
||||
|
Quote:
I'm also hypothesizing that perhaps the utility installed the service drop before the new addition was actually built and the contractor/homeowner built the addition under the service drop. It still should have been picked up though on a final inspection for the addition, if there was a final. Anyway, I've noted it as wrong and in need of further evaluation and correction. Thanks Paul! Mark MD HI Lic # 30090 BPI Certified Building Analyst PA DEP Radon Cert # 2457 Certified Home Energy Tune-uP Inspector
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Service Drop over the Roof | jhagarty | Electrical Inspections | 8 | 11/24/07 7:22 PM |
| Chimney flashing photo's needed: brick and stone done correctly | kshepard | Exterior Inspections | 6 | 10/13/07 8:10 AM |
| service drop clearance | belliott | Electrical Inspections | 28 | 6/1/07 1:23 PM |
| Service Drop Q | alarsen1 | Electrical Inspections | 11 | 2/25/07 9:45 AM |
| Roof Repair? Maybe NO | jhagarty | Exterior Inspections | 9 | 2/15/07 1:19 AM |